Compressor overheating split ac
Pel siver line 1 ton a.c which caplari used
  • 21 Answers
SOURCE: could I use wire size 14 for 1 1/2 ton air window
No sir,14 gauge,three conductor will carry only up to 15 amps,which is usually wired for lighting circuits.Look on the electrical requirement plate on the unit,usually located under the front panel cover.It will tell you how many amps are drawn when unit is operating.Using a three conductor cable;wire accordingly:#14--15amps----#12--20amps---#10--30amps----#8--50amps.These are the wire sizes and the current(amps)they will carry.Be safe! Gregg
Posted on Jun 12, 2009
2coolrick
  • 560 Answers
SOURCE: my LG intelloair 1.5 ton split a/c's compressor not working.
check the compressor's start/run capacitor. if it is swelled at the top, where the connectors are, replace it.
Posted on Apr 04, 2010
  • 51 Answers
SOURCE: yonan ac split mini 1.5 ton error codes E1
CHECK ROLLOUT SWITCH AND CHECK FOR A POSSIBLE
GROUND FAULT..OR FUSE..
Posted on Apr 13, 2010
heatman101
  • 43501 Answers
SOURCE: Wiring standard for Split AC 1.5 Ton
The factor that you have not included here is the distance from the power panel to the unit...if it is too far then you need to up gauge the wire to compensate for that... that could be why the electrician wanted to go to the 720 ga. wire.
heatman101
Posted on Apr 16, 2010
  • 3 Answers
SOURCE: My 5 ton Goodman Heat Pump won't go into heat or a...
Easy: Turn the "fan" switch to on at the thermostat and see if the blower starts. If no start, check breaker at breaker box. Check service disconnect at or near the air handler. With the breaker and/or service disconnect OFF check the 3 or 5 amp fuse inside the top cover in the air handler.
Not so easy: (You must know what you are doing for this part or let an HVAC Tech do it for you) Open thermostat and firmly jump the Y and R terminals to see if you get the compressor to start for no more than 30 seconds. (don't do it more than once.) Jump the G and R terminals to see if you get the blower to start. If so, u have a bad thermostat. If not, check the transformer inside the same cover in air handler for proper voltage. (24V. Make sure you also get 220 on the opposite side of the transformer)
If the blower comes on, but the heat pump doesnt start, open the side cover of the heat pump, with the thermostat on cool, and the temp. setting as low as possible for at least 10 minutes see if the contactor is pulled in. If so, check the capacitor and see if it's blown out. Be super careful these systems operate with 220v and the amperes are enough to kill you if you make a simple mistake.
Posted on Aug 28, 2010
How may capacitors are there in LG split ac 1.5 ton unit
At least 3. 1 on the inside unit fan, 1 on the outside unit fan and 1 on the compressor. The outside unit may have both in a single chassis.
Aug 15, 2016 | LG Electronic Window Air Conditioner
I have samsung split ac 1.5 ton 2.5 years old when am switch on the ac the indoor unit is working when it tires to on the out door unit after 3 minute delay suddenly the ac is restarting but the out d
Make sure all of the pressure switches are closed on the low voltage control circuit on the outdoor unit. If any are stuck open, the compressor will not kick on. Or just push the compressor contactor in with an insulated screwdriver to ensure the compressor does actually work.
Dec 28, 2014 | Samsung Heating & Cooling
Any body tell me what is the problem with my 1.5 Dawlance split ac It gives perfect cooling in night and morning but in afternoon its compressor turn on and off every after 15 minutes. And due to this my...
when the heat ambient temps go up . the start capacitor gets hot to turn on fan and heat sensor for the compressor senses it and turns off . check the run/start cap first
May 25, 2014 | Haier 18000 Btu Air Conditioner Heat Pump...
Dawlance split ac
My guess is compressor motor overtemp cutout. So why is the motor overheating? Possibles: Needs bearing oil, bad bearings, compressor too much pressure, overfull with freon, mechanical friction, cooling fan not turning.
Suggest set thermostat to demand less cooling, see if compressor stays on longer.
--Gil
When we start the ac it take 6amp curent but as the ac run the amp. contineous grow $ it reach at 14amp. we also changed its filter $ caplari pipe
salaams ,
check the capacitors(running) and also fan capacitors. or in the last check the compressor may be overheated.
Sep 06, 2011 | LG Heating & Cooling
My 1.5 ton,LG split AC shuts off rather
Hello
First the foam insulation is not just for looks,you will have some loss of cooling on the unit,the larger cooper line needs to be insulated,the small one does not.The large line is the suction line,the small one the liquid line.
Voltage,168 is low,sounds like a 208 volt unit or 220 volt.running at 168 or 198 ac volts is going to raise the amperage causing the compressor to run hot and work harder and soon burn up,And cause it to trip the breaker or shut itsself down on high heat.Your going to need to get that voltage fixed.I dont know why it needs a stabilizer if the unit was sized correctly it shouldnt need one.
Hope this helps.
Apr 14, 2010 | LG LS-K2430HL Heat Cool Mini Split Air...
Best split ac 1.5 ton
I think you just have a faulty unit. Most of the mid wall split units have similar components and there are only cosmetic differences. Lg is strangely enough a good aircon. Personally i like Samsung .(Spares are easily available). You should concider who the best after sales service supplier is and go that way. (As stated, most units are similar in my oppinion.)
Sep 21, 2009 | LG Heating & Cooling
Samsung 1.5 ton slpit AC.the out door unit is very noisy
Check to see if the noise is coming from the fan, could be bad bearings. Replace the fan motor if that is the case. If the noise is coming from the compressor, the only other place besides the fan, then your compressor has some issues and will probably stop working soon, maybe line up for a replacement before you are left with a hot house.
Jun 11, 2009 | Fujitsu 24C1 Air Conditioner