Honeywell rth6350 the air handler shuts off before the compressor. it meets set point and turns on and off as it crosses the set point.
  • 499 Answers
honeywell rth6350 - b37e45c0-977c-4c80-a840-4ff38e44c97f.jpgYou need to test from Green to Common on the thermostats sub based or air handler low voltage terminal board to see if the stats the culprit or the board/relay etc.
Posted on Aug 27, 2013
Honeywell thermostatTemp set at 73 turning off and back on the 'cool on'flashes. After about five minutes it stays solid. the temperature drops from 84 to 81shuts down and the cool on flashing again.
Possibly have a backed up drain that is draining very slowly. Machine runs, produces enough water to trip the float switch, then turns off. Drain drains slowly, enough to clear the float switch, process starts all over. Check PVC at air handler for a piece with 2 wires connected. Remove the top and see if there is any signs of water. NEVER LEAVE SWITCH OUT. You must clear the drain. If no water, turn system to off and fan to on. Let machine run like this for a while and see if any "shut downs." If still a problem you either have a loose wiring connection or bad stat. If no problems with fan only, problem likely outside. Good Luck!!
Mar 23, 2017 | Honeywell Heating & Cooling
Installed a rth6350 now no power
The RTH6350 is a battery-powered thermostat. Did you correctly install the AA batteries? Press down and pull the battery holder away from the thermostat on the right hand side. Try new batteries. Did you remember to secure the C wire with a wire nut and push it back into the wall. It should not be connected to the thermostat.
If you connected the C wire, you may have damaged the thermostat by providing too much current. Honeywell has the documentation for the RTH6350 on the product page: http://yourhome.honeywell.com/home/Products/Thermostats/5-2-Day-Programmable/RTH6350D.htm . The installation guide is here: https://customer.honeywell.com/request.cfm?form=69-2416ES . See page 23 and subsequent pages for the wiring diagrams.
I hope this helps.
Oct 11, 2014 | Honeywell RTH6350 5-2 Programmable...
JUST REPLACED NEW COMPRESSOR AND NOW MY AIR HANDLER WONT SHUT OFF WHEN TSTAT SHOWA OFF
it is either miswired or the fan control switch on the thermostat is in the on position instead of auto position. hopefully its that simple
Sep 07, 2012 | Heating & Cooling
Outdoor AC unit runs for about 2 minutes after air handler shuts off
Hello, it is possible that the new thermostat has some type of time delay built in it. But typically this would shut of the outdoor unit first and then the air handler.
Jul 25, 2012 | Heating & Cooling
Honeywell Thermostat RTH6350 makes heat run in AC mode after AC runs
Well, if it wasn't doing that before then you more than likely know its in your wiring. Cools down then heats back up sounds like the auto change over is on, and the heat setting is higher than the cool setting?
Mar 02, 2017 | Heating & Cooling
I replaced an old mercury T-stat (York with model number 2TH11704024) installed a new T-stat (RTH6350). The wires that I I have are O (orange), G (green), Y (yellow), T (gray but not used in new T-stat),...
Did you shut the power off to the air handler/furnace...... before you installed the new thermostat??? You may have shorted out the transformer or blown the transformer fuse...... If you try to put the Fan switch on the stat to Fan ON does the fan come on ..... if it does the transformer is OK.. On the new thermostat did you program it to tell it that you had a heat pump system ???? Looks like you had it wired right. Here is a pdf manual for a RTH6350 http://customer.honeywell.com/techlit/pdf/PackedLit/69-2416ES.pdf
Its on page 13 Advance setup for tell the new stat that you have a heat pump....There is also a Honey well Hot line on page 2 Hope this helps.
May 01, 2011 | Heating & Cooling
Trying to hook up Honeywell RTH6350 thermostat. When turned on cool out air blows out. We only have a green, red, yellow and white wire from the old unit. Are we missing some wires? we have a heat pump.
Your Thermostat should wire as Red to Rc/Rh (if Rc/Rh are not connected you need to put a jumper between them; White to W; Green to G; and Yellow to Y on your thermostat. These will be the only wire connections that you need to connect from the unit to the thermostat. However, if your thermostat is not battery operated and is programmable then you will have to run on wire form the transformer in the units C to the Bl on your thermostat.
Thank you for choosing FIxYa.com
Justin
Apr 02, 2011 | Heating & Cooling
My thermostat when prgrammed and set on "auto" mode kicks on heat when temp drops below set temperature. The problem is that after warming up to that temperature...it does not shut the fan off. ...
I have a honeywell TH8320U thermostat and American standard Air handler with heating unit put in. THE thermostat works fine with the ac and follows the programs I have set. However the heat is a different story. The thermo clicks on to follow program but the unit does not run. (auto settings) If I place the thermo in heat and turn it to on I get heat?
Dec 08, 2010 | Honeywell Programmable Thermostat Heater
Upgrade Baystat 239 to a Honeywell RTH7600D controller
For Trane sytems, B is your "Common" wire. O is your reversing valve relay, G is your fan, Y is your compressor contactor, R is Hot, Brown will not be used on your electronic tstat. X2 is your backup electric heaters. Without knowing what terminals are on your new tstat, I cannot offer more information than this. The installation manual may indicate what each terminal is controlling. I strongly suggest to write down ALL of the terminals and colors from your old t-stat and be sure to turn off the power to your air handler. Put the fan switch on your tstat to ON before turning off the power. Make sure the fan is running. Then turn the power off to your Air Handler. If your fan stops running, you have turned the power off to your tstat and are ready to start replacing it with your new tstat. I hope you find this helpful. Good Luck!!!
Feb 06, 2010 | Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen