Try disconencting the remote start wires between the transfer switch and the generator, if ot still does it you have a bad control board. If it stops, then check the transfer switch for correct wiring of utility and generator power wires, also check with an ohm meter if the run contacts in the transfer switch are closed, that would indicate loss of sensing, or bad board
Posted on Dec 01, 2013
I have a Kohler 12 RES home standby generator. Once in a while when the power goes out the generator will start and then immediately shut down with no fault codes. When I flip the control in the unit
Check the inlet fuel pressure, on exervise there is no load, when power is out it is loaded and demands more fuel. Also check for bugs blocking gas regulators vents etc
Nov 12, 2012 | Kohler Generator. 12 kW and 14 kW Home...
I have and old model #10RY6Z 10 KW Kohler Generator used for back up on a solr system that over speeds when we try to run it without to solar panels hooked up. What is
Your problem is mag pick up, or possibly the solar panels are reverse powering the generator, if the home consumes less than solar output
Oct 29, 2012 | Kohler Electrical Supplies
Under voltage
Check rotor slip rings,brushes then rotor and stator for shorts
Aug 08, 2012 | Kohler 17 kW Emergency Power System -...
Generator starts for no reason
You have a short in the remote start wiring, incorrect wiring terminations, or a defective control sensing in the transfer switch
May 31, 2012 | Kohler 20RES 20 kW L.P./N.G. Genset
If I lose street power momentarily and my generator immediately starts than quits because the street power comes back on, the weekly 20 minute generator excercise does not work.I have to reset the transfer...
Although A bit inconvienent this does seem to be the norm for some Kohler units. Actually a small price to pay rather than having a technician come out to replace the ATS control board. There are time delays that could be set longer to keep the unit running longer and may prevent this from happenng
Jan 03, 2011 | Kohler 18RESL 18 kW Emergency Power...
Kohler 12res AC breaker flipping with no error listed
wat size c/breaker
6600 divide 240 = amp
rule of thumb
Aug 16, 2009 | Kohler 12 kW Emergency Power System -...
My Kohler 17RES has stopped doing it's scheduled weekly exercise. How can I get it exercising again?
On your Automatic Transfer Switch ( the little gray box you see on the right in the picture above) you have two blue buttons. One is a Manual test switch. The other has a clock on it and this is your exercise set button. Hold it down for a FULL 3 seconds if you want it to excercise without a load (not powering your home) Hold it down for a FULL 6 seconds if you want it to exercise with a load every week. Your generator will start and run for 20 minutes, and then shut down. Now every week your generator will exercise at the time and day that you pushed the set button.
Aug 08, 2009 | Kohler 12 kW Emergency Power System -...
Kohler lp shuts down
What you need to know is there enough fuel going to the regulator. It should be 7 to 11 inches Water Column. If not your problem may be not enough fuel. That includes when the heater in your house kicks on and what ever gas appliance you may have. Once you verify that you need to figure out if you have the proper pressure coming out of the regular on the inside of the generator. Next I would look at compression of the cylinders. It may need new piston rings.