Question about Sta Rite Sr200lp Max E Therm Pool & Spa Heater Dual Electronic Ignition Lo Nox 200,000 Btu Propane Gas
Can turn it on, but it turns itself off after a couple of min.
The motor is running. it displays the current water temp. have to press the up arrow really hard to get heater to turn on. sudden whoosh of air is heard. good cycling sound. air rushing out at exhaust on pack of heater. however, after 1-2 min. the heater shuts off. the current temp. of the pool water continues to be displayed and even shows a slightly higher temp as the afternoon sun warms it naturally. so I know at least the thermostat seems to be working.
    Top Expert:
  • Sta Rite Master
  • 7,905 Answers
Check gas pressure if ok check manual bypass in header
Posted on Dec 05, 2017
  • 61 Answers
SOURCE: Heater turns on runs for short time display reads
It is probably your thermistor. It is screwed into the header (the place where the pipes come out). To know for sure you would have ohm it out (I am not sure of the ohms of this particular model). If it ohms out ok then it could be the control board.
Posted on Apr 07, 2009
  • 83 Answers
SOURCE: When Heater is turned on display shows 125, doesn't ignite/fire.
I am not sure if you have solved this issue, or not, but here is one idea. When you turn on the heater, it is reading the temp at 125/126 correct? IF this is what the heater is reading, then the problem is the Thermistor,or temp sensor, and is very easy to replace.
If you have an Owner's Manual, there are part numbers and instructions on how to replace the Thermistor. If you do not have one, follow the link below and it will take you to one online:
http://www.pentairpool.com/pdfs/MaxEThermOM.pdf
Posted on Jul 01, 2009
  • 83 Answers
SOURCE: Sta-rite heater error code 126
The 126 is not an error code, but it maybe the temp of the water that the heater is reading. If the heater thinks the water is 126 degrees, it will not start at all.
If the heater is reading the wrong water temp, the problem is the Thermister, which is the sensor that is suppose to read the water temp. You will need to replace this sensor in order to correct the problem with the heater. It is really easy to do!
If you have a manual for the heater, if you go to the Replacement Parts Listing for the Electrical System, page 53 in the online version, the Thermistor is Item #9. It goes into the left side of the manifold in the to place, between the first two manifold bolts.
Posted on Jul 10, 2009
  • 83 Answers
SOURCE: Sta Rite Sr333na Max E Therm Pool & Spa Heater gauge stuck?
Anytime the heater is reading the water temp to be above what it actually is, especially 126, the problem is the Thermistor, or Temp Sensor, for the heater. This is a very easy part to replace. The Thermistor is located on the manifold, on the left side, between the top two bolts.
Sorry this is a late response! Hope that it helps!
  • 83 Answers
SOURCE: Sta Rite SR400 NG heater with code r=5
You can find an Owner's Manual online at the following site:
http://www.inyopools.com/owners_manual/sta-rite_heaters_max-e-therm.pdf
IF you have tried to restart the heater and received the same outcome, the r5, or S, is a badk control board. Sorry about that one!
What you may want to try is resetting the heater. You will need to put the SunTouch in the maintenance mode. Then turn off the heater, turn off the Circuit Breaker for the heater, wait about 15 to 20 minutes, then reverse the order. Circuit breaker, then heater, then try and start the heater without the SunTouch first. If it works, then try with the SunTouch.
Posted on Jul 14, 2009
Fridge & freezer lights and the water display light beep and flash 10-12 times every few hours. Simultaneously a fan motor starts and stops. Any one know what needs to be done to remedy this?
Fridge keeps beeping or buzzing: The following is for Frigidaire models but others can be addressed similarly.
Several Frigidaire refrigerator models have an electronic control panel on the freezer door the owner can use to adjust the internal temperature, dispense ice and water and receive notification about issues such as the need to replace a water filter. The refrigerators also emit a beep for various actions and as an occasional alarm. Determining what causes the beeps necessitates some troubleshooting.
Temperature Controls ·A Frigidaire refrigerator's display panel blinks when the control panel is touched to set temperature controls. After pressing "Freezer Temp" or "Refrigerator Temp" on the keypad, press the arrow buttons within five seconds to increase or decrease the desired temperature. If you do not press the arrow buttons within five seconds after pressing "Freezer Temp" or "Refrigerator Temp" on the keypad, the refrigerator beeps to indicate the current setting will stay in place.
Door Open ·When you leave the refrigerator or freezer door open, the refrigerator beeps. Also, the "Door Ajar" indicator illuminates on the appliance's display panel. Shutting the door and pressing "Alarm Reset" stops the beeping and turns off the "Door Ajar" indicator light.
·The Frigidaire refrigerator has a control lock feature that prevents use of its control panel or dispensers when the unit is locked. When the control lock is active, a beep sounds when a keypad or dispenser is pressed. Release the control lock by pressing the "Control Lock" icon for three seconds. A beep will sound, and the icon's light will go out.
Power Reset ·A power reset is occasionally necessary if the Frigidaire refrigerator's control panel does not work normally or a reset function on the keypad does not work. A power reset involves disconnecting power to the refrigerator by unplugging its power cord from the electrical outlet, waiting 30 seconds and plugging the power cord back into the electrical outlet. When the control panel resets, a beep sounds. If the refrigerator beeps even after a power reset and the beeps' source is not known, contact Frigidaire.
Read more :http://www.ehow.com/info_12148688_cause-beeping-noise-frigidaire-refrigerator.html
Cause of Beeping Noise in Frigidaire Refrigerator eHow
Apr 25, 2015 | Refrigerators
I would like to know which buttons to push on my 2008 Chevy cobalts clock to set the time
Without Date Display
AM/FM Base Radio with a Single CD Player
This type of radio has a button for setting the time. You can set the time by following these steps:
Turn the ignition key to ACC/ACCESSORY or ON/RUN. Press the knob, located in the center of the radio, to turn the radio on.
Press the button until the hour begins flashing on the display. Press the button a second time and the minute begins flashing on the display.
While either the hour or the minute numbers are flashing, turn the knob, located on the upper right side of the radio, clockwise or counterclockwise to increase or decrease the time.
Press the button again until the clock display stops flashing to set the currently displayed time; otherwise, the flashing stops after five seconds and the current time displayed is automatically set.
To change the time default setting from 12 hour to 24 hour, press the button and then the pushbutton located under the forward arrow label. Once the time 12H and 24H are displayed, press the pushbutton located under the desired option to select the default. Press the button again to apply the selected default, or let the screen time out.
With Date Display
Single CD (MP3) Player
This type of radio has a button for setting the time and date.
To set the time and date, follow these instructions:
Press the button and the HR, MIN, MM, DD, YYYY (hour, minute, month, day, and year) displays.
Press the pushbutton located under any one of the labels that you want to change. Every time the pushbutton is pressed again, the time or the date if selected, increases by one.
• Another way to increase the time or date, is to press the right SEEK arrow or FWD button.
• To decrease the time or date, press the left SEEK arrow or REV button, or turn the knob, located on the upper right side of the radio.
The date does not automatically display. To see the date press the button while the radio is on. The date with display times out after a few seconds and goes back to the normal radio and time display.
Hope this helps ! hope you had a very Merry Christmas an have Happy New Year
Dec 27, 2014 | 2008 Chevrolet Cobalt
How do you program this heater
temp setting
1. press the temp/timer button untill the temp icon blinks
2 use up and down arrows to set temp.3 the temperture icon will stop blinking and the current room temperture will appear after desired temp. is set.
4 the heat will turn off shortly after the desiredtemp. is reached and the temp. ndisplay will blink.
5 the heater will turn back on when room temperture drops below the set temp.
timer : auto -off press the temp/time button untill timer icon blinks. the hour display will apear. the auto off icon will also appear.
2. use up and down arrow buttons to set the heater operation time between 1 and 10 hours. this function will activate once the timer icon stops blinking.
3. the heater will automaticly turn off when time runs out.
set temperture first so heater will cycle on and off till shut down time reached
Feb 02, 2011 | Comfort Zone CZ9009 Oil Filled Electric...
The treadmill will turn off while in the middle of a run. After a couple of min. it will turn back on.
hi, please check when machine turn off display is gone or not ,IF display is gone pls check power point, IF display is not gone check the current rating with load ,
Dec 09, 2010 | Spirit Esprit ET-8 Foldable Treadmill
How do you change the clock on a 2009 Chevy cobalt.
Setting the Clock Without Date Display AM/FM Base Radio with a Single CD Player
To set the time:
  1. Turn the ignition key to ACC/ACCESSORY or ON/RUN. Press to turn the radio on.
  2. Press until the hour begins flashing on the display. Press a second time and the minute begins flashing on the display.
  3. While either the hour or the minute numbers are flashing, turn to increase or decrease the time.
  4. Press again until the clock display stops flashing to set the currently displayed time; otherwise, the flashing stops after five seconds and the current time displayed is automatically set.
To change the time default setting from 12 hour to 24 hour, press the button until 12H or 24H is displayed. Once 12H or 24H is displayed, turn the knob to the desired option to select the setting. Press the button again to apply the setting, or let the screen time out.
With Date Display Radio with CD (MP3) and USB Port, and Radio with Single CD (MP3) Player
To set the time and date:
  2. Press and the HR, MIN, MM, DD, YYYY (hour, minute, month, day, and year) displays.
  3. Press the softkey located below any one of the tabs that you want to change.
  4. To increase the time or date do one of the following: • Press the softkey located below the selected tab. • Press SEEK, or FWD. • Turn clockwise.
  5. To decrease the time or date do one of the following: • Press SEEK or REV. • Turn counterclockwise.
The date does not automatically display. To see the date press while the radio is on. The date with display times out after a few seconds and goes back to the normal radio and time display.
To change the time default setting from 12 hour to 24 hour or to change the date default setting from month/day/year to day/month/year:
  1. Press and then the softkey located below the forward arrow label. Once the time 12H and 24H, and the date MM/DD/YYYY (month, day, and year) and DD/MM/YYYY (day, month, and year) displays.
  2. Press the softkey located below the desired option.
  3. Press again to apply the selected default, or let the screen time out.
Nov 21, 2010 | 2009 Chevrolet Cobalt
How do i set timer
How to program Raindrip R673CT
Download R673CT manual at raindrip
Other models
R683CP
R672CT
Raindrip drip water guide
R673CT
Install 2 AAA batteries to power display
Set current time:
Press TIME and hour digit flashes > Use up-down arrows to set 24 hour clock
Press SET to confirm hour
Use up-down arrows to set minute
Press SET to confirm minute
Use up-down arrows to set day of week
Press SET to confirm day
Program review
Timer can set 16 watering schedules
When programming, look at display:
Notice: PROG for programming mode, #1, start time, run time, SU MO WE for days
Press PROG and display appear just like image above
Use arrows to select 1, 2, 3, 4 through 16 different watering schedules
Programming
Start time hour will flash
Once hour flashes, use arrows to select hour
Minutes will flash
Use arrows to select minute
Press SET to confirm minutes
Run time hours will flash
Use arrows to set run time hours duration (0 to 9 hours)
Run time minutes will flash
Use arrows to set run time minutes
Press Set to confirm
Now #2 shows on display this is about which days the timer will water
Decide 1) every other day, 2) every third day, or 3) watering at will
1) To water every other day:
While 2nd is flashing, press SET and SU TU WE FR will appear in display
2) To water every third day:
While 2nd is flashing, press down-arrow
3rd will start flashing and TU WE SA will display
3) To water at will:
While 2nd is flashing, press down-arrow twice
SU will flash
Press down-arrow to go to MO TU WE etc
Press SET when day you want appear on display
To set another watering program
Scroll back up to "programming" on this page
Press arrows to select programming 1 thru 16
Repeat programming sequence
After programming is set, press clock button and current time will show
Oct 07, 2010 | Raindrip R673CT Digital Water Timer
Need trouble shooting proceedure to enter self diagnostics for maytag neptune
From the service manual there is more to it but that was all I could put here.
Accessing Service/Diagnostic Mode:
Pressing down the damp dry and time (-) keys
for 5 seconds places the machine in the
diagnostic mode.
SPECIAL TESTS
The following table lists the various tests
available while in the Service Mode, which
can be accessed by pressing the following
keys:
Press Keys Special Test/ Function
wrinkle
release Diagnostic Codes
dryer
temp(^ )
Sequences up the
help/diagnostic code list
dryer temp(v) Sequences down the
time (-) Displays Software Revision
Number
very dry(< ) View current cycle
temperature (Co)
start/pause
Start or pause cycle running
but remain in Diagnostic
mode
Accessing Diagnostic Codes
After the machine is in the diagnostic mode,
a ‘d’ will display and let the technician know
they are in the diagnostic mode. Pressing the
wrinkle release key will access the diagnostic
codes.The diagnostic codes can be viewed by
using the temperature (^) & (v) keys.
The down arrow key will sequence down the
list one each time it is pushed with no wrap.
The first time the down arrow key is pushed
the display will sequence to the next code
logged. The last code being displayed being
the oldest code. The up arrow will sequence
up the list one code each time it is pushed
until it reaches the top code. If there are no
diagnostic codes available, ‘00‘ will be
displayed for the diagnostic code.
There will be no multiple occurrences of
either a diagnostic code or help code generated
in the same cycle reported on the list.
But if the same code occurs in repeated
cycles, it will be registered.
To clear the diagnostic code list press
wrinkle prevent and very dry (>) for 5
seconds while viewing the list.
System Check Mode
While in diagnostic mode, pressing the damp
dry
and signal (+) keys for 2 seconds, will
put the dryer into the system check mode.
"SC" will display.
This mode will allow the various inputs and
outputs to be controlled and viewed by the
technician by pressing individual keys. If no
activity is seen for 5 minutes after a key is
depressed, the control will reset back to the
normal mode. If no further activity is seen
after an additional 5 minutes the washer will
turn off. The following table lists the various
functions based upon on keys being depressed.
Membrane Pad Check
While in system check mode, pressing the
damp dry and sensor dry keys for 5 seconds,
will start a membrane pad switch test.
The membrane check involves turning all the
embedded LED on the membrane pad on.
All the LED’s can be toggled off by pressing
the key associated with the LED. To exit the
test at any point, press the damp dry (>) &
sensor dry keys again for 5 seconds or press
the off key to exit diagnostic mode.
Key Pressed: Function Performed
sensor dry
Enable sensor dry circuit.
(sense dry LED) When short
circuit is detected across the
sensor bars the normal dry
LED will turn on.
start/ pause
Cycles the motor relay
on/off. When the motor is
running the start/pause LED
is on.
dry temp(^ )
If motor is running, cycles
the heater/gas valve on/off.
When the heater is regular
temp LED is on.
temperature (Co)
www.appliancehelponline.com
Mar 26, 2010 | Maytag Neptune MDG5500AW Gas Dryer
Setting the time on car stereo/cd player
Changing the general settings
(PSM)
You can change the items listed on the next page
by using the PSM (Preferred Setting Mode) control.
• The PSM items are grouped into five
categories—“Disp (display),” “Clock,” “Tuner,”
“Color,” and “Audio.”
Basic Procedure
1 Press and hold SEL (select) for more
than 2 seconds so that one of the PSM
items appears on the display.
(See page 23.)
The currently selected
category is shown on the
left side of the display.
2 Press 5 (up) or ∞ (down) repeatedly
until your desired PSM category
appears on the left side of the
display.
3 Select the PSM item you want to
adjust.
4 Adjust the PSM item selected.
5 Repeat steps 2 to 4 to adjust the other
PSM items if necessary.
6 Finish the setting.
To set clock—Clock Hr, Clock Min
You can set the clock using the PSM control.
1 Press and hold SEL (select) for more than 2
seconds so that one of the PSM items appears
on the display.
2 Press 5 or ∞ repeatedly until “Clock” is selected
as the PSM category (it is shown on the left side
of the display).
3 Press ¢ or 4 to select “Clock Hr
(hour).”
4 Turn the control dial to adjust the hour.
5 Press ¢ or 4 to select “Clock Min
(minute).”
6 Turn the control dial to adjust the minute.
Nov 04, 2008 | JVC KD-G720 CD Player
Honeywell HZ-705.....HELP!!!!
Should have oil in it. I don't think you can refill it. If it has leaked out, it's probably no good. Anyway, here are the instructions.
Press the *power button* once to start the heater on high power, continuous run. If left at this setting, the unit will run continuously on high power (1500 watts, 12.5 amps) and will not shut off until the unit is manually turned off.
Press the *power button* again, to change to low power, continuous run, (900 watts, 7.5 amps) and will not shut off until the unit is manually turned off.
Set temperature:
Press the temp/timer button until the temperature icon blinks. Use the up and down arrows to set the desired temperature.
The temperature icon will stop blinking and the current room temperature will reappear after the desired temperature is set.
The heater will turn off and on to achieve the desired temperature.
Set timer: (auto off)
Press the timer/timer button until the timer icon blinks. The hour display will appear. The auto off icon will also appear.
Use the up and down arrow buttons to set the heater operation time between 1 and 10 hours. This function will activate once the timer icon stops blinking. The heater will automatically turn off whn the times runs out.
Set timer: (auto on)
Press the temp/timer button until the timer icon blinks. The hour display will appear. The auto on icon will also appear.
Use the up and down arrow buttons to set the heater start time between 1 and 10 hours. This function will activate once the timer icon stops blinking.
The heater will automatically turn on when time expires.
Hope this helps!
Aug 17, 2008 | Heating & Cooling
Honeywell oil radiator
Set temperature:
Hope this helps!
Sep 24, 2007 | Honeywell /KAZ HOME ENVIRONME HZ-705 7Fin...
Sta Rite Sr200lp Max E Therm Pool & Spa Heater Dual Electronic Ignition Lo Nox 200,000 Btu Propane Gas Logo
24 people viewed this question
Top Sta Rite Pool & Spa Experts
Jay Finke
Jay Finke
Oloyede Monsuru
john h
Are you a Sta Rite Pool and Spa Expert? Answer questions, earn points and help others