I wired the generator to a two pole breaker box for two 120 volt circuits. I get 116 volt on each side at the box from the generator. Installed breakers and the first one register 116 volt (no wiring connected yet. Turn the second breaker on and voltage on the first drops to about 105 and the other one register about 135 volts (again no wiring attached. Have no clue where to go. All connections are good an tight. Help111
    Top Expert:
  • 78,267 Answers
Sorry we do not have this.
Posted on Jul 10, 2017
3 Suggested Answers
  • 39 Answers
SOURCE: tried replacing a 2 pole
You are correct. Try replacing the single pole breakers with thinner space saver breakers to get more space in the pannel.
Posted on Oct 18, 2010
  • 3289 Answers
SOURCE: one half of a 240
The breaker must engage TWO bus bars in the panel, in addition to the a neutral connection. If the breaker is aligned to engage only one of the bus bars, only one of the terminals will be powered at the breaker terminal screw (most likely the top).
Some electrical panels have covers that have numbers and spaces stamped for circuit breakers at the bottom; when in reality, there is no bus bar to connect. Make sure you are not attempting to install into a space that lacks both bus bars.
If unable to get 240 volts out of the breaker without the load wires connected, there may be an issue internally with it. If after connecting the load wires, one side fails again, it may be detecting a ground fault or an over current situation but due to an internal failure is unable to trip both poles of the breaker. This breaker should be replaced.
Posted on Jun 02, 2011
What do i have to do to plug my 110 air conditioner into where my 220 window unit
You need a step down transformer, to convert 220V to 110V. You can't just plug the 110V A/C unit in directly unless it is clearly marked as being suitable for multi-voltage supply (110V - 220V input).
Such a transformer has to be of sufficient capacity to handle the current, or wattage, that will be required. The Frigidaire unit in your question is a 3.5 kW cooling capacity, so the transformer would need to be about the same, ie for a 10A supply at least. They are quite big boxes, about $120.
http://welectronics.com/TRANSFORMERS/step-up-down.JPG
You would put this in the roof or in a cupboard.
Apr 25, 2015 | Frigidaire FAC126P1 wall/window Air...
3 Pole light switch won't turn on
Verify your wiring on the switch to make sure that you stripped them to the correct length and that they are fully inserted and tightened down. Also check that you put the correct wire in the correct terminal. The terminal marked HOT will have the either the 120 volt power coming from the breaker or the 120 volt switch leg going to the light fixture, depending on which of your 3-way switches is fed from the breaker. The terminals marked 1-pole and 3-way should have your traveler wires connected to them. Check the switch that you did not replace to see which two wires were used as the travelers, they will be the ones on the screws of the same color. The odd colored screw is the hot or switch leg, depending on which end of the circuit it is on (on the breaker side, it is the hot wire, on the light fixture side of the circuit, it is the switch leg.)
Apr 16, 2014 | Electrical Supplies
I have 110 volts n each leg but not 220 across both why??
In a traditional North American residential electrical panel (120/240 volt, single phase), installing a single width or single pole circuit breaker, you would expect to read 120 volts from the breaker terminal screw to either ground or neutral. A double width or double pole breaker would provide 120 volts from either of the breaker terminal screws to ground or neutral AND it will provide 240 volts BETWEEN the TWO breaker terminals.
A single-width circuit breaker case that contains two handles is NOT a two pole circuit breaker (these are called "tandem" or "1/2 size" breakers). This is because a single width breaker engages only one "line" in the panel. A double width breaker will engage 2 "lines" as a triple width breaker would engage 3 "lines" of a 3 phase panel. A single wide breaker can not physically engage more than 1 "line" so it will never be able to pass 240 volts.
You must install a double width / double pole breaker to safely supply a 240 volt circuit / device.
Mar 15, 2014 | GE 20 Amp 1 In Double Pole Circuit Breaker...
5000 watt inverter schematics circuit
If you have (90) 50w lamps = 4500 watts total. Assuming a 120/240 panel, if you put 1/2 on one "side" of the panel and the other 1/2 on the other "side" of the panel, that would be 2250 watts on each half. The generator should be rated *at least* 125% of the load; 4500w x 1.25 = 5625W. Using a 4500W generator on this load will cause it to overheat and shorten its life as it is running at 100% of capacity all the time..
One half of the panel is 120V to neutral, and the other is 120V to neutral - or 240V between both circuit breaker terminals. Ohms law for DC circuits and purely resistive AC circuits says Volts x Amps = Watts; or Watts / Volts = Amps. So, 2250W / 120V = 18.75A on each pole of a 2 pole circuit breaker that feeds the sub panel. A #12 copper wire is rated for 20 amps; but as per National Electrical Code - must be de-rated to 80% of rating which means it is good up to 16 amps maximum. A #10 copper wire is rated for 30 amps, but it too must be derated to 80%, making it good for 24 amps maximum. So, if you are going to feed a sub panel supplying (90) 50watt lamps, you will need to run a #10/3 copper cable from a two pole 30 amp circuit breaker at the generator to a 120/240 volt "main lug only" sub panel rated for at least 30 amps.
Divide your load evenly across the sub panel - (4) 15 amps circuits via (2) two pole 15 amp circuit breakers on each "side" of the panel if you run (2) 14/3 cables out to the lights - or (4) single pole 15 amp circuit breakers if you run (4) 14/2 cables out to the lights. No circuit breaker terminal should have more than 23 lamps that means you have (2) w/ 22 lamps and (2) with 23 lamps. The circuit w/ 23 lamps will draw 23 lamps x 50w = 1150W. 1150W / 120V = 9.6A. The 22 lamp load will be 22 x 50w = 1100W. 110W / 120V = 9.2A. Which is well within the 12A maximum allowed (after derating as required by code) by a #14 copper wire rated for 15A.
Mar 10, 2014 | Electrical Supplies
I purchased a 7000W Westinghouse Portable Generator to back feed my circuit breaker box. The cable is rated to 30amps. Do I use a 30 amp or a 40 amp circuit breaker? Thanks, Mike
1) Match wire and breaker:
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/See-inside-main-breaker-box.html
2) 7000 watts divided by 240 volts = 29.1 amps.
30 amp breaker x 80% safe maximum = 24 amps.
This means you should use 8 gauge wire and 40 amp double pole breaker for 240volt
3) 7000 watts divided by 120 volt = 58.3 amps.
60 amp breaker x 80% safe maximum = 48 amps.
So use 70 amp breaker and #4 wire.
Jan 30, 2013 | Electrical Supplies
How do I wire a Woods 59402 timer 240v input running two 120v outlets
Woods 59402 timer wires identical to Intermatic GM40, with same ratings and dip-switch settings.
http://waterheatertimer.org/How-to-wire-GM40-timer.html
Here is specific wiring diagram per your request, showing 240Volt input controlling two 120Volt outlets.
http://waterheatertimer.org/images/GM40-wiring-240v-120-volt-5.jpg
Keep in mind that with 240Volt, both hot wires coming from breaker box carry 120Volt each, with 240Volt potential across both hot leads.
Each 120Volt Hot from breaker box, also carries 120Volt potential to Neutral or ground wire.
So the 240Volt wires from breaker box can supply the Hot for a 240Volt circuit, but the circuit must also have a neutral wire to complete 120Volt circuit.
Be mindful that timer is not 2-channel, so both outlets are controlled by same timing schedule.
If you want two different schedules for the outlets, then buy a 2-channel timer like Intermatic ET1125. Wiring for ET series remains similar to illustration link above.
Dec 01, 2012 | Coleman Cable Woods 59402 40Amp Timer for...
Dryer and electric cookstove
First make sure that the circuit breakers are compatible with the installed circuit breaker panel. If you have to force it or jerry rig it, replace with the correct one. Then make sure that you tightened down the terminals and that you are using the correct wire size - 6 awg for the 50 amp and 10 awg for the 30. Then verify that you connected the wire correctly to the new outlets you installed.
The voltage between the Hot lead at 7 o'clock and W 120-volt, Hot lead and G 120-volt, W and G 0-volt1_1_2012_4_17_30_pm.jpg
The voltage between Y and X should be 240-Volt, X and W 120-Volt, Y and W 120-Volt, X and G 120-volt, Y and G 120-volt, W and G 0-Volt
Hope this helps! Hal aka ImJustAvg
Jan 01, 2012 | Dryers
I have a electric dryer Model WED5810SW0 THAT I WAS TOLD I COULD CONVERT TO 120V from 240v is this true and if so how do i do this?
If you consider doing this the first thing is SHUT THE MAIN BREAKER OFF. Use an auxiliary light source to see when working in a dead panel. Always keep in mind an ARC FLASH ACROSS HOT MAINS HAS ENOUGH HEAT TO PEAL THE SKIN OFF OF YOU. Before an explanation of how to do it you should keep in mind that this is for a single receptacle only. If any other receptacles are on the same circuit they will also be changed to 240 volt receptacles and if you plug any 120 volt device into them, the 120 volt device will be destroyed. That said OK, any 120 volt outlet can be changed to 240 volt by removing the 120 volt circuits neutral, re identifying the white wire with red or black phase tape and connecting it to a new 2 pole 15 amp breaker. The maximum that this circuit will now load up to is, on #14 wire at 80% = 12 amps at 240 volts. The 120V receptacle must be changed to a 15A - 240V receptacle so that 120 volt devices can not be plugged into it. Never use 2 single pole breakers together because code requires that on a fault trip both legs of the 240V circuit must be disconnected simultaneously. OR USED A Quick 220 Voltage Converting Power Supply
Voltage converter buying guide. Voltage Transformer Buying guide.Voltage converters also known as voltage transformers are devices that convert foreign electricity to power devices from different parts of the world. A step down voltage converter is a 220 to 110 volts converter. A step up converter is a 110 volts to 220 volts converter. Our 2-way converters are voltage transformers that convert power from both 220 to 110 volts and 110 to 220 volts. They also work with 100 volts, 110 volts, 120 volts, 220 volts and 240 volts. This model is a 2 way voltage converter / voltage transformer available in many different sizes including 100 watts, 200 watts, 300 watts, 500 watts, 750 watts, 1000 watts, 1500 watts, 2000 watts, 3000 watts and 5000 watts.
Sep 07, 2011 | Whirlpool Dryers
I'm confused about how to properly hook the wiring to the product below. Specifically where does the "neutral" wire attach. I have it all hooked up, but I'm not getting the full 220...
Your 240V wiring is not described clearly, and it sounds like you are confused about 240Volt circuits.
You posted under T104R indoor-outdoor 240volt timer:
http://waterheatertimer.org/images/T-104-control-240V-Load4-35.jpg
Typically a 240Volt cable is 2-wire with ground, and does not have a 'neutral'
A neutral is not necessary to complete 240V circuit.
If your 240Volt cable is a 3-wire with ground, then the neutral connects to terminal A on timer.
Open following links for specific T104 wiring diagrams plus illustration of 2-wire and 3-wire cables, and illustrations and explanation of difference between 120V and 240V circuits:
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html
http://waterheatertimer.org/images/wire-ga-250.jpg
http://waterheatertimer.org/B220C.html
If you have 240Volt cable, then do not move clock motor wires.
The clock motor wires connect to terminals 1 and 3.
240V power from circuit breaker connects to same terminals.
Load wires connect to terminals 2 and 4.
If you are not getting 240V across terminals 1 and 3, then check circuit breaker.
240Volt circuit breaker can be tripped off on one leg, or bad on one side so you get 120V on one leg at timer, and then clock motor does not rotate dial.
http://waterheatertimer.org/How-to-troubleshoot-Intermatic-timer.html
Jul 03, 2011 | Intermatic T104R 208-277Volt 40-amp Timer...
One half of a 240 volt gfi breaker does not supply the 120 volts and the other half does. when I did a continuity test, both sides of the breaker show or indicate good circuits. position of breaker in...