Have a AC unit working for two years great all of a sudden outdoor unit stops push the contactor in and outdoor fan and compressor come on but will not stay on have 24 volts and fuses are fine any ideas
  • 31 Answers
Most likely you have either a low or high pressure cutout switch that has shut the unit down. One will be located on the suction line (larger tube) the other on the high pressure line (small tube). If you have both high & low shitches they are tied together in series and in order to bypass them you need to trace them back to the contactor . Pull cutout switch by the unit to disconnect power. Do NOTHING inside the box with power on. You will see they tie together somewhere and each one has one end attached to the contactor. Mark which wire goes where and remove these. This will put those sensors out of the loop. If only one sensor then both wires will go the contactor, one on each side. Turn unit back on and see it the compressor starts up. If so then you need a tech to re-charge or diagnose problem. If not, make sure temp inside is set low enough for compressor to turn on. Still noting, then it most likley your thermostat. Need volt meter to check this and better to not mess with the wires as this can really mess things up. At some point you will most likely need to call a tech anyway as you need to be licensed to buy freon and will be required if low charge is indicated.
Posted on Apr 23, 2013
  • 3 Answers
SOURCE: The fan in the outdoor unit does not work while the AC is on.
these motors are famous for the inyernal fuse blowing in the fan motor. check continuity between the red and blac wires. if there is non the fuse is gone. These motors are fairly easy to take apart and change the fuse . hope this helps
Posted on Sep 01, 2008
  • 252 Answers
SOURCE: Carrier AC Compressor Fan will not turn on.
Bad contactor - replace
Posted on May 07, 2009
SOURCE: Compressor will not come on. Fan runs great.
I fixed it. I had a dirty connection on the starter relay for the compressor. Thanks again for the help.
Posted on May 18, 2009
  • 534 Answers
SOURCE: Contactor not engaging to start condenser unit
I would replace the contactor if you are getting 24 volts to the contactor and it isn't engaging therefore the magneto on the contactor is out and the contactor will need replacement. If you don't have 24 volts at the contactor then the transformer that sends the 24 volts is bad and will need replacing
Dave
Posted on Mar 11, 2010
roniecon
  • 6927 Answers
SOURCE: My contactor switch will not remain engaged. I
Something,is drawing too many amps,most likely the compressor.
Posted on Jul 08, 2010
I have samsung split ac 1.5 ton 2.5 years old when am switch on the ac the indoor unit is working when it tires to on the out door unit after 3 minute delay suddenly the ac is restarting but the out d
Make sure all of the pressure switches are closed on the low voltage control circuit on the outdoor unit. If any are stuck open, the compressor will not kick on. Or just push the compressor contactor in with an insulated screwdriver to ensure the compressor does actually work.
Dec 28, 2014 | Samsung Heating & Cooling
How to troubleshoot thermostat wiring?
I'm not sure if the thermostat is wired correctly. First, the thermostat is wired directly to the outdoor unit (compressor/condenser unit). It is NOT directly connected to the indoor unit. It connects to a low voltage control panel in the outdoor unit that sends a signal to your indoor fan/evaporator. This wire is called the fan relay switch and physically runs between the low voltage controls of the indoor and outdoor units. If the fan relay is bad it's possible that the unit runs continuously. To prevent destroying your outdoor unit there is a safety feature that prevents the indoor fan from shutting down while the outdoor unit is running. If the indoor fan did shut down while the outdoor unit was running than you would slug your compressor. That is, your compressor normally sees refrigerant gas but is instead seeing refrigerant liquid. That would not be good since this scenario would destroy your compressor. It sounds like a faulty fan relay. The actual contactor portion of the relay is in the outdoor unit.
Aug 22, 2014 | Honeywell Electronic Programmable...
A/c won't stop running and no cool air
There seems to be a problem with the wiring of the thermostat. Apparently the thermostat is calling for cool (if wired properly), but is not being satisfied. The thermostat is just a switch. When there's a call for cool, the thermostat sends 24-28 volts to the contactor (inside the condensing unit to start the compressor and outdoor fan). The indoor fan is energized through the fan relay (inside the air handler). When the temperature in the conditioned space reaches the set temperature,then the thermostat cuts the power to the contactor and it stops the compressor and outdoor fan. Check that the compressor is actually running, if not, check for 24-28 volts on the wires feeding the contactor, if there is, and the contactor isn't closing then the contactor is defective. If the contactor closes and the compressor doesn't come on, check the capacitor. If the capacitor is good then check your compressor motor. I suspect you have an improperly wired thermostat
Aug 26, 2013 | Honeywell PRO 4000 5-2 Day Programmable...
Intertherm Air Conditioner S3BA-042KA compressor and fan not working (has power)
It sounds like that unit is connected to a "power saving load controller" device from the power company. The power company can turn your unit on & off with a radio signal. If you manually activated contactor and unit ran. I would bet that the power company's device or the wiring connecting it is where the problem lies. Call the power company and have them check their device. If they tell you that the device has been tested remotely and is working fine. Explain to them that you can activate your unit manually and it works fine. They should not charge you to come out. Those "load controller devices" have a pretty good longevity record.
Jul 11, 2012 | Intertherm Heating & Cooling
The outdoor unit doesnt work for ac panasonic cs c9mkp,i have following the instruction on manual book.
After switching the indoor unit to cool, the indoor fan starts and the light flashes, lower the temperature setting to 16 degree centigrade. When the light stops flashing the outdoor fan and the compressor start, if not check the wiring connection going to the compressor contactor. Check if there is power supplying the holding coil of the contactor. If the contactor works, check the power on both contact points by using a volt meter. If the outdoor fan only works, you need to check line working pressure. If the standing pressure is low, compressor will not start.
Sep 02, 2011 | Panasonic Heating & Cooling
All of the sudden tonight it was getting hot went to adjust thermostat and it was blank. No air and no fan. Bought new thermostat (above). checked circuit breakers. thermostat shows it is on but wont kick...
At the thermostat you have several colored wires. Touch the green and red wire together and see if the indoor fan comes on. If you know what wire goes to the coil on your AC contactor touch the red wire to that wire. If it starts the outdoor fan and your compressor the thermostat is not wired correctly. All you are doing by my suggestion is bypassing the thermostat to eliminate it as the possible problem.
The outdoor AC contactor coil wire is usually yellow or blue, but you must make sure not to short the red wire to the other side of your transformer as that will cause you to have to buy a new transformer. Your unit wire diagram should show the wire to the AC contactor coil. You need to determine which wire feeds the AC coil which closes the contactor to the compressor and outdoor fan motor.
If this helps please rate me at fixya.com
Aug 03, 2011 | Heating & Cooling
AC compressor wiil not turn on
You will have to find the contactor which is located in the outside unit. And check the voltage at the contactor, 26 v as this is the thermostat calling for the compressor to come on. You can also push in the contactor and see if the fan and compressor start. There should be an outside fuse box close to your condensing unit. Good luck
Jul 23, 2010 | Samsung AW1203B Air Conditioner
Air conditioner just conked out;only 3 yrs old
Is the indoor unit operating? If no turn the fan from auto to on at thermostat. If the fan comes on, that is a sign that you have 24volts
present on thermostat side.
Turn AC unit off outside,turn the thermostat as low as it will go. Open the electrical panel to the outdoor unit. There is a contactor located in the unit, push the plastic bar in the middle of contactor. If it pushes
in, you have low voltage wiring problem from the outdoor unit to the
indoor unit.
If you are skilled or know somebody that is with electrical, turn the power back on to the outdoor unit take a non conductive object and
push the contactor in, the unit may start. If it doesnt start,check the
breaker for the ac unit to make sure it is not tripped.
If the breaker is not tripped and the condensor fan comes on and the
compressor does not come on and the breaker does not trip, then it
is very possible that you will need a new capacitor and while you are
at it put in a hard start kit.
This unit according to you, still should have 2 years left on the compressor warranty.
Jun 18, 2010 | Goodman CLQ36AR49 Air Conditioner
Indoor unit freezing up
THE OUTDOOR UNIT HAS A CONTACTOR WITH THE CONTACTS WELDED TOGETHER THE CONTACTOR CONNECTS TO THE COMPRESSOR AS IT TYPICALLY PULLS A SURGE OF 20 -30 AMPS OR MORE..WITH THE INDOOR UNIT IN FAN ONLY THE COMPRESSOR SHOULD NOT BE RUNNING. THE CONTROL WIRES GOING TO THE UNIT HAVE 24 VOLTS TO THE CONTACTOR TO PULL IN THE CONTACTS TO SUPPLY 220 TO COMPRESSOR.
Mar 09, 2010 | Heating & Cooling
AC Unit is not working
if you got high volt to the outdoor machine....make sure the thermostrat is in fact on.open the control box cover to the a/c.a round or oval soda pop lookin can thing should be visually noticeable.is it blown up.thecan top will be bulged.if it is the capacitor is defective.duel capacitors control phase shift for both motors...the outdoor fan and the compressor.a big black relay with the wires comming from the outdoor fuse box should be noticeable.this is the high volt contactor, is the contactor pulled in?beets the **** out of you???grab a screw driver by the insulated handle, not the metal part of the screw driver.manually push it in.did the fan start to go???if so bad contactor or no signal from t'stat to turn machine on.if not no high volt to machine(breaker tripped or failed) or fan motor seized leading to compressor O.L.
Aug 03, 2009 | Goodman CKL60AR60 Air Conditioner
Heating & Cooling Logo
26 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen