Keeps tripping the breaker
Trips the breaker with all devices disconnected
  • 31 Answers
You have an opencircuit possibly at the wall outlet. Shut off breeaker, pull off outlet cover and take out plug unit. Check to see all wires are secure and no indication of burning or melting. Any black marks indicate an arc of electricity has occured. If suspicious, replace plug with new one.
Posted on Apr 23, 2013
SOURCE: Heat pump trips circuit breaker
i want to know the size of breaker to use.we are using a 30,30,30,30but it is kicking off.would a 40,40,40,40or higher be better if they sell them.
Posted on Nov 22, 2008
cactus bob
  • 267 Answers
SOURCE: Electric Furnace Trips Breakers
it is normal for a breaker that is run right on the edge (50 amp and your furnance to use 45) to get weak after a while . the first thing you should do is change the breaker with the same type and amp rateing . it should take care if it
Posted on Jan 16, 2009
  • 166 Answers
SOURCE: keeps tripping breaker when running ac
you need to check that the breaker it rated high enough for the ac unit
Posted on Jun 04, 2009
  • 10865 Answers
SOURCE: dometic rv air conditioner over 100 deg. trips breaker.
The problem is that when u add up the electrical draw from all of these appliances running full bore, your draw exceeds your available amperage. Now you are doing the math and saying no...... Let me tell you why. It is rare to find a situation where a 100 amp service actually porovides 100 amps. You almost always have voltage dropo. And when you are adding extension cords to the mix the drop is even more. That said, When you are using the AC try to minimize the use of other appliances, especially the microwave which is a big draw too.
Posted on Jun 25, 2009
  • 82 Answers
SOURCE: a/c is drawing 20 amps and keeps tripping breaker after running
If the fan is running and the compressor is getting hot and tripping off you may have a failed capacitor.
Posted on Jun 29, 2009
Breaker for hot tub keeps tripping
Leaking heat element.
2 GFCI on same circuit.
Rat-chewed wire. Inspect wiring.
Nail through wire.
Melted wire nut in junction box.
Undersized wire and breaker has been overheating breaker, and breaker has gone bad.
Shorted breaker. Move wires to different same-size breaker.
http://waterheatertimer.org/How-to-wire-GFCI.html#2-pole-gfci
http://waterheatertimer.org/Color-codewire.html
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Apr 21, 2013 | Pool & Spa
Model 4001-ov trips the circuit breaker.
Assuming you have Paragon 4001 40 amp 120Volt timer
By-pass the timer so only pool pump is connected to breaker.
To do this, move wire from terminal 2 and connect to terminal 1.
If breaker no longer trips, then replace timer with Intermatic T101
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html#T101
Crossover wiring: Paragon terminal 1 goes to Intermatic terminal 1.
Paragon terminal 2 to Intermatic terminal 2.
Paragon terminal 3 to Intermatic terminal A
If breaker keeps tripping after bypassing timer, then tighten wires on circuit breaker and test again.
If breaker keeps tripping, then move wires to another same-size breaker.
http://waterheatertimer.org/How-to-replace-circuit-breaker.html
Breakers trip when they sense overheating.
If motor is causing problem, you might need electrician to track down source of overheating.
Jun 19, 2012 | Paragon 4001-0G Defrost Timer
Breaker installed on generator. Keeps tripping under no load after approx. 1 minute of generator running
A tripping circuit breaker is an indication of an overload. You say there is no load on the breaker - how are you making this determination? Are you using an amprobe or some other meter?
A circuit breaker with NO load shouldn't ever trip. Likewise a circuit breaker carrying up to 80% of of the current it is rated for shouldn't trip either. Circuit breakers that carry more than 80% of their load will trip - if the load remains connected long enough. This is called "duty factor" or "service factor" The greater the load is in excess of 80%, the less time that the breaker will carry it before tripping.
An example of a 100 amp breaker with different loads on it (this 100 amp value was chosen for ease of doing the math):
80 amps - never trips
85 amps - trips after 48 hours
90 amps - trips after 16 hours
95 amps - trips after 8 hours
100 amps - trips after 4 hours
105 amps - trips after a few minutes
120 amps - trips after a few seconds
150 amps - trips instantly
This is only an example to show how a certain circuit breaker might trip under a load less than the rating stamped on the body or handle.
A circuit breaker that trips with no load or a load equal to or less than 80% of its rating is most likely defective. You need an amprobe or ammeter for amp readings. If the load is found to be 80% or less, there may be an issue of harmonics that is causing the tripping. You'll need to have special equipment and qualified persons to check harmonic problems. Most harmonic problems occur when the loads are not linear device (transformers). Examples of non-linear devices are "switching" (or solid state) power supplies like those in computers.
I hope this helps and good luck. Please rate my reply. Thank you.
Apr 07, 2011 | GE Tjk436f000 3pole 400a 600vac Circuit...
Furnace keeps tripping the breaker changed breaker and wires all good up to the furnace still keeps tripping when i try to turn power on. nothing happened to the furnace and the wires were tested up to the...
Disconnect the black power wire where it is connected to the furnace with breaker off. Put a wire nut on it and then turn the breaker on. If it continues to trip, the problem is not the furnace and you will have to trace the power wire back to the breaker box to find problem. Next, disconnect the black wire from the breaker (with breaker off) and then snap breaker on. If it trips, bad breaker. If the furnace was disconnected and breaker did not trip, you have a short either on the P C Board or the transformer.
Mar 31, 2011 | Heating & Cooling
Trips breaker and will not cool or heat
Disconnect compressor leads and tape them up. Restore power, if the breaker does not trip, than you have a grounded compressor.
If breaker trips again, hook compressor up and disconnect blower, if breaker does not trip you have a
bad blower motor.
Jun 18, 2010 | Coleman Mach 15 Air Conditioner
Spa keeps tripping breaker shows pr
two main reasons breaker trips is the pump motor jammed [not turning]or the heater shorted out --disconnect power open access panel disconnect the lines to the heater turn on power if breaker trips than motor /pump problem if doesnt trip than heater problem can order heater replacement online or pool spa store--if motor pump check pump for debris and motor for lube if u can turn shaft or impeller oil motor and work it into bearings if still not turning possible need to replace motor unit
Apr 26, 2010 | Heritage Pool & Spa
Dishwasher keeps tripping the electrics
Hi .. when a breaker trips immediately it can mean there is a problem in the circuit. You can start troubleshooting by unplugging the washer, or disconnecting it and trying the breaker again. If the breaker holds with the washer disconnected, then the fault is inside the washer. You would be better to have a tech look at the washer for a solution.
Mar 23, 2010 | Hotpoint 24 in. FDW60 Free-standing...
The Lights circuit breaker keeps trips without load
try a new breaker, they do wear out over time
Feb 08, 2010 | Electrical Supplies
Gfci breaker keeps tripping
sometimes gfi outlets go bad and trip try testing with a heavy draw machine in it or just replace it and see if this fixes the problem
Jun 22, 2009 | Balboa Instruments Duplex Digital Panel 2...