York furnace model # p3urb12n07501e has bad gas valve error code 6 , how do i test valve?
  • 1033 Answers
SOURCE: Gas furnace with Honeywell smart valve code error
Hello, it sounds like your Furnace might be shutting off due to your high limit switch.A limit switch will open when the furnace overheats due to low airflow, . check air filter, clean blower wheel, and check to make sure the blower wheel is running at proper speed and not dragging sometimes cause by a weak capacitor. Anything that restricts airflow will cause a limit switch to open.
Posted on Mar 08, 2011
TheMobilian
  • 8220 Answers
SOURCE: I have a model GMP075-3, S/n9509835876 that will
Unplug your quick connect at the ignitor and chek to see if it has continuity. If it checks good start the furnace and see if you have voltage present at the quick connect. If ya ain't got volts going in then their is a problem with the board. Rich has a nice video at HVAC for beginners HERE
Posted on Oct 29, 2011
  • 340 Answers
SOURCE: York Gas Furnace Model # P2MPD14N08001A - Combustion Air
where are you getting combustion air from now in the midwest 1sq" per 1000 btu York.com with the model number
Posted on Jun 17, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Posted on Nov 23, 2009
james3751
  • 614 Answers
SOURCE: I have a new York hybrid heat pump/gas furance
Did they check the sensor in the plenum. You are suppose to have bonnet sensor to switch from heat heat pump to gas whaen it is to cold for the heat pump. The bonnet sensor may be to bad. The unit is cycling ever five minutes because it may have five minute time delay.
Posted on Dec 15, 2009
5 u code is on how to fix it
Gas furnace fault or error codes for common furnaces - Gray ...
www.grayfurnaceman.com/-ifc-failure-codes.html
Here are error codes found on many York, Trane, Luxaire, Lennox, Carrier, ... If younotice 5 red colored flashes on your York Furnace, it signifies that your
Oct 03, 2015 | Cars & Trucks
York furnace won't ignite
Is the igniter receiving 120 volts after the pressure switch closes? If not, either the board is bad or the pressure switch is open
Nov 27, 2012 | Heating & Cooling
CAN FURNACE BLOWER BE REPAIRED???
sorry but a search for that did not locate anything here in USA
Nov 18, 2017 | York Furnace Draft Inducer Blower Fasco #...
My York Stellar PLUS furnace (Model P2UDD12N07601C) will not stay on; The ventilator fan runs, the main blower runs, the igniter comes on for approximately ten (10) seconds and you can hear the gas valve...
Check gas pressure, inspect manifold & make sure there is not a blockage.Make sure gas is present and main gas shut off valve to furnace is on also check the knob on the 24 volt gas valve and see if it is in the on position , check the MV terminal on the gas valve to 24 volt common with a volt tester to see if you have 24 volts present, if you do have 24 volts at gas valve, replace valve. if you do not have 24 volts at gas valve check high limit control & roll out limits for a open circuit, Good luck.
Feb 20, 2010 | York Furnace Draft Inducer Blower Fasco #...
York furnace model p2mpd12h06401f flashes 4 times for trouble code does'nt have code list inductor motor comes on but ignitor does'nt come on
Check pressure switch for inducer motor. If switch closes, check for crack in ignitor. If gas valve opens and you can hear/smell gas, the ignitor is bad probably. If pressure switch isn't closed you need to check for blocked vent/chimney/heatexchangers.
Dec 18, 2009 | York Furnace Draft Inducer Blower Fasco #...
York 92 % eff. furnace shuts down on # 3 error (pressure switch)
i have fixed almost every one of pc9 -----we have installed in our company,code three{flashes} at first new presure switches installed, same thing,york knows about this,induction motor bearings,could be bad.our local york dist, has boards,inducer, ***.motor, dual press.switch,free.as is known as the only way to fix.after all else is ruled out.one local competator called us if we wanted to join class action suit . good luck.furnaces work good at first, season or two then bam
Nov 28, 2009 | York Furnace Draft Inducer Blower Fasco #...
York high effenciency furnace not firing all the time
has anyone worked on this furnace because the error would indicate that the positive 120 volt and the neg 120 volt is swapped , these units will also do this when the ground wire to the furnace or gas valve or furnace or @ the panel is lose , corroded , or missing , the gnd must be present to open valve , I am aware that ac is is not usually polarity sensitive but in this case it most certainly is ...have seen many time and know it to be true