Heat pump cycling on and off.
Exterior heat pump, Carrier Mdl 38YCC036340, cycles on and off when thermostat set on heat and fan on auto with ambient interior temp at 65 deg and thermostat set at 72 deg. Emergency heat function working properly. In Emer Heat function, heats house to desired temp and keeps it there. I have turned the heat pump off and am relying entirely on the emergency heat function to heat the house. What can I do to test the heat pump and or the thermostat? Thanks
  • mikie1999cr Mar 11, 2009
    mastatech,
    Any way to check the r22 level on the system, before, calling out the A/C guys? Just to make sure 'that' is the problem?
    Mike
  • victor mosley May 20, 2013
    breaker popping
  • 478 Answers
It sounds as if you you have a low charge of refrigerant, r22. When the unit comes on outside, the outdoor coils become the lowside, there is a low pressure switch that is tripping out contactor protecting the compressor.
Posted on Mar 11, 2009
  • mark milligan
    mark milligan Mar 12, 2009
    Without gauges doubtfull, but in a fix a tire gage can give an indication, but you would have to short the lowpressure switch.
Need a quick fix for a Carrier that won't heat. Ac works, fan works, auto for heat doesn't.
Could be the capacitor or the heating element (or igniter if it's a gas unit). Unless you're a qualified HVAC repairman, call your local HVAC company to come take a look at it.
Dec 13, 2017 | Carrier Heating & Cooling
My termost set to a/c, the fan auto, blow very well, but when I switch to heat and the fan auto, doesn't work, but if I put fan on work why?
the thermostat says to call for heat buildup in the work if its not cold enough the thermostat won't call for heat and I won't go on but when it gets cold and the thermostat set to the temperature you want or hire someone that doesn't cycle
Oct 12, 2014 | Heating & Cooling
The heat come on turn off but fan will not shout off.
if you have a gas or oil furnace then the limit control is probably bad. If you have electric heat or a heat pump then the sequencer is probably bad. But first make sure the thermostat is not set to "FAN". The thermostat must be set to "AUTO". Many systems have a time delay on the fan to capture the remaining heat after it completes a heating cycle. Usually several minutes.
Feb 17, 2011 | Heating & Cooling
FAN MOTOR CONTINUES RUNNING AFTER HEATING CYCLE IS COMPLETED BLOW
Check the thermostat. Make sure it is set for AUTO fan not ON fan. If that is OK replace the fan relay.
Apr 08, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Honeywell YTH9421C1002, heat pump puts out cool air in heat mode
You have the stat programmed incorrectly or wired incorrectly there are alot of settings for installers in that stat and all of them have to be set correctly
Apr 05, 2009 | Honeywell Programmable Thermostat Heater
My air handler comes on ,not the outside unit when my thermostat is in the off position even if i turn the thermostat down to 50 and have it turned off the air handler comes on for about 5 to 10 minutes...
If you have a standard thermostat the fan switch is for the air handler only. It completely over rides the thermostat for most settings. Now lets see this is what I'd expect:
fan switch on Indoor fan runs all time
Fan switch auto Indoor fan only runs when thermostat is set to cool or heat and the thermostat is turned up above room temp for heat or below room temp for cooling. In both of these modes the furnace blower comes on and stays on til the room temperature is satisfied. The outdoor unit only comes on for AC the out door unit will not come on for heat or the "on" setting on the thermostat. See exception 1 & 2 below...
Exception 1- (in a heat pump the out door unit runs in both heat and cool mode unless it has emergency heat turned on then it will not come on outside in the heat mode, and depending on the type of heat pump and furnace or air handler it is). A heat pump thermostat usually has "backup heat" and an "emergency heat" setting switch on the thermostat.
Exception 2 - On some thermostats they are made to cycle on the heat if the temperature reaches a preset temp (around 50'f usually but definitely by 40'f). This mode prevents freezing when if instance the homeowner is away or while the home is under construction. In this mode the fan inside can run but the heat usually comes on with it.
Exception3 - On some electric furnaces the heating strips may be individually controlled and thus not all come on at one time. This may give the feel of no heat especially if the room is cold.
Now there may be other exceptions but Ive tried to give you a heads up on some of the most common ones.
If you need more help please post more specifics about your unit/system as to for sure what switches are set to what setting and what is happening with each. My first though was that maybe your system is OK and you needed to know if the thermostat was working properly.
If this helpd you understand your problem would you please give me as hifgh a mark as you can. Thnaks for using fixya and good luck.
Mar 28, 2009 | Carrier Heating & Cooling
My cARRIER ROF TOP IS SHORT CYCLING IN THE HEAT PHASE
have you checked the filters? May be cycling on the high limit due to not enough air going across the burners.
Also what type of thermostat do you have if it's a manuel one then the heat anticipator may be set wrong.
or the air from a register may be hitting trhe thermostat causing it to short cycle.
Dec 20, 2008 | Carrier Heating & Cooling
Heating & Cooling Logo
901 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen