Question about Pool & Spa
Qo260gfi not tripping
I have a Thermospa concord hot tub with a square d 60 amp gfi pt# qo260gfi gfi has no way to run a neutral from gfi to spa 60 amp gfi does not come with one.
  • 5,245 Answers
Question is not fully clear.
2-pole 240Volt gfci circuit breaker requires the white wire be connected to neutral busbar.
Easy solution for 240Volt spa that comes with gfci:
Replace spa gfci with regular non-gfci breaker.
Install 2-pole GFCI breaker in main panel, and connect wire to spa breaker.
http://waterheatertimer.org/How-to-wire-GFCI.html#2-pole-gfci
Having 2 breakers is not a problem.
Having 2 GFCI on same circuit is a problem.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Posted on Apr 19, 2013
  • 990 Answers
SOURCE: Motor is hooked up correctly according to
You have 220v running into your motor, the red and the plack are in most cases the same 110v line and what your calling a white netural is a common line. In other words the second half of your 220v line. If your red and black are the two opposing 110v lines that make up your 220v and they are put on the motor and turned on they short aginst each other and blow the breaker. One of your 220v lines should come into your hi -low switch and then split to your high and low on the pump. The other half of your 220v line will go to the common or what your calling nuteral. The difference is a netural completes a 110v circut and a common completes the 220v circut it will take to run the motor. One of the splits will complete the low speed circut and the other will complete the high speed circut. You need to check your voltage comming into the spa, the way the spa is wired (110v-220v), and how the motor is wired (110v-220v). For your spa this will be in your owners manuel or on a scematic inside a panel or door and is quite often a plug you change from one spot to another. On your motor will have a scematic on the back of the motor that will tell you haw to adjust the wireing already in place on the wire board of the motor. This may sound deep but if all your voltages are set the same and your high and low are the same leg of power, this should fix your problem.
Posted on Oct 31, 2009
djxtreme979
  • 151 Answers
SOURCE: 115 volt 20 amp breaker for hot tub keeps tripping
Is there anything else on the same breaker? Is that the proper amperage for the pump? How long has the pump been in service? It may need to be cleaned as possible obstruction causing too much strain.
Posted on Dec 28, 2008
SOURCE: Running a 220 volt 40amp service for my hot tub.
By code, this would require underground cable to a breaker panel with a double pole GFI (maybe that's what you were planning). Then from the breaker panel to outlets, pumps, etc.
40 amp breaker will require 8 AWG cable.
More info, let me know...
Charlie
Posted on Aug 23, 2009
Testimonial: "BY CODE, means it's the law!!! I didn't want to cut thru my black-top driveway. It's about 130 feet around the yard to the hot tub."
SOURCE: I have a Sundance Spa that has started tripping the breaker
It is unlikely the Breaker is BAD, that just doesn't happen. To trip a breaker there MUST be an Overload, or a Short circuit, that's it. You will have to use a meter an troubleshoot the system. Something is very wrong..please use the links below to troubleshoot and repair. Please Be careful. http://spababes.com/heaterhelp.html
http://www.spadepot.com/spacyclopedia/spa-heater-element.htm
http://www.poolandspa.com/page596.htm
Posted on May 07, 2010
Testimonial: "Looks like this info may save me a service call. Many thanks for the answer and the links."
  • 8 Answers
SOURCE: Coleman 500 series SPA 50A circuit breaker trips
bad connection follow wires from breaker to to moter theres abreak causing arc find it
Posted on May 09, 2010
My hot tub works for about 20 mins and clicks the GFI off. Then I reset the GFI and the spa comes on for about 7 mns and trips the GFI again. Is this my heater doing this?
Easy way to test for the heater issue is to disconnect the heater from the board. Disconnect both leads from board and let the spa call for heat. There is also a chance the GFI breaker is bad however most times the heater fails and the breaker is doing its job.
Apr 01, 2017 | Hot Tub Works Pool & Spa
I have a spa berry 2 person hot tub. Tried resetting it but as soon as I let go of the reset button it trips the breaker. Can't get it to stay on. Tub is 4 yrs old. Where do we start?
Melisa, Breaker/GFI may be going bad. You may have to get an electrician to check for short or faulty motor/heater, etc. Check the attached links,instruction and guides, Good luck
"I hope this helped you out, if so let me know by pressing the helpful button. Check out some of my other posts if you need more tips and info."
http://ehottubsandpools.com/?p=320
Troubleshooting tripping hot tub GFCI breaker
Hot tub GFI keeps tripping
Spa Circuit Breaker Mysteriously Tripping Any Clues Portable Hot Tubs amp...
Jun 27, 2016 | Pool & Spa
What's youI just wired in my J-300 Jacuzzi hot tub. The GFI trips every time I reset it. I took the GFI out of the equation and the tub runs fine, does not trip the breaker at the main breaker box
#1. DO NOT GET INTO TUB FULL OF WATER WITH A GROUND FAULT.
2. There is a short. You need to get multimeter and start checking each part for current running to ground wire.
3) Power is ON. Connect power without GFCI.
4) Tape tester leads to wood sticks to keep hands away from power.
5) Do not touch anything directly or you will become the ground rod.
6) Ground wire must be present, and bonded back to main panel box.
7) Do not sit or touch directly on cement or bare ground. Do not touch or lean into anything made of metal.
8) Body and parts must be on sheet of plywood, or similar non-conductive dry surface.
9) Test each part with spa, but also test electric line coming from main box.
10) GFCI will also trip with any fault detected on line. So the wire coming to spa may have the fault.
11) Add a new dedicated line from main box to spa.
http://waterheatertimer.org/See-inside-main-breaker-box.html
Oct 02, 2012 | Electrical Supplies
QO115GFI breaker trips when I switch on the breaker next to it.
I happen to have one of these in the box, so I've reviewed the installation & on-line literature for this model. Let's address installation notes:
Don't connect more than 250 ft of load conductor for the total one-way run, to prevent nuisance tripping.
The breaker is to be used on grounded power supply circuits only. We're talking a properly-grounded breaker box, not just the protected circuit.
Look at the side of the breaker. You will notice that the curly white wire is meant to be connected to the (properly grounded) neutral bar in your panel.
The circuit neutral that you're protecting should be landed on the terminal just above that curly wire. Make sure you have the right neutral!
The circuit's hot wire would of course be landed on the topmost screw.
You did not state what you mean by "the breaker next to it": just above, just below, or directly across from the GFI breaker?
I suspect that you meant just above or below the GFI breaker. And I assume you've swapped out other breakers to rule out a defective breaker.
Now, it is possible that you have a "shared neutral" situation. It's a common wiring practice to use one neutral wire for two "hots", where one circuit is fed from the phase A side and the other is fed from the phase B side, (which you'll have in a two-pole, 220V breaker), picking up a 110 volts from each phase. The two 110v "Hots" share a single neutral wire between them to carry return current. The phase shift between the two phases allows this.
However, to avoid nuisance tripping of your GFI, your protected circuit cannot share neutrals with another circuit, as the "other" circuit's operation will cause the 6 milliamp differential between current out (hot) and current return (neutral) which the GFI by design senses and trips.
Your GFI-protected circuit probably needs its own dedicated neutral!
I'd like to hear what you find. Good luck!
Feb 24, 2012 | Square D QO115GFI QO Circuit Breaker
40 amp gfi on hot tub keeps tripping.I have a 50 amp.can I use?
Your hot tub needs GFI protection because it is electrical, and people sit inside water that could be exposed to electric current.
You have a fault to ground that needs to be fixed.
Size 8 wire for 50Amp breaker.
Size 6 if tub is 50-100' feet away
http://waterheatertimer.org/Color-codewire.html
Nov 09, 2010 | Spa Parts Plus GFCI, Circuit Breaker, 40...
I have hot tub control by Square D QO260GFI. The curcuit has tripped to off position and when I try to flip it to on position it just stays in nutral.
Hi!!
The breaker may be defective is not rated for the load been used or one of the devices the breaker is controlling is either defective and is drawing too much current.
try disconnecting the devices ie: pump motor or heather. one at the time, this is to find out if they work ok by themselves, test one by one. If the pump do not want to start up, it may be the start capacitor. If both devices trip the breaker, Replace breaker.
Good Luck!! Don't forget to rate this post!!
Sep 03, 2010 | Square D Circuit Breaker QO260GFI
Gfi Breaker 2 Pole 20 Amp: installed 20 amp dbl pole breaker to hot tub. Keep...
When Working with Household Electricity you want to always keep in mind that the BLACK wire ALWAYS carries DEATH. What I mean by this is that working with a Single Phase Circuit (one that uses 120VAC) the only wire that should be carrying a voltage is the BLACK one, the other 2 wires (typically the White Neutral and Green Ground) should both be electrically connected to Earth Ground (usually by being attached to your water pipe.)
It is also possible that your hot tub may use more than 20 Amps.
May 17, 2010 | Cutler Hammer Gfi Breaker 2 Pole 20 Amp
120v hot tub wiring diagram! Need to wire fro 120v! there is a red, white, black & green to connect the wire from the power plug. The power cord only has black, white & green. Which is the hot and...
I would expect your tub is either 110 or 220. Currently you are set up for 110. Based on that ... you disregard the red wire.
If your tub can run on 220, you should run it on 220 as this is more economical.
You should probably have an electrician check this out and make any changes to assure proper and SAFE operation of your tub. You are using a GFI, correct?
Thanks for your interest in FixYa.com
May 15, 2010 | Pool & Spa
Charlie
Aug 23, 2009 | Qca Spas GT 396 Hot Tub
GFI 'shorted'
load neutral connects to the neutral binding screw on the GFI, do NOT connect the load neutral to the neutral bar.
Mar 05, 2009 | Spa Parts Plus GFCI, Circuit Breaker, 30...
Pool & Spa Logo
147 people viewed this question
Top Pool & Spa Experts
Jay Finke
Jay Finke
john h
David Spradling
David Spradling
Are you a Pool and Spa Expert? Answer questions, earn points and help others