I have a coleman furnace with a pilot light that keeps going out.When i manually light it the furnace runs 12 to 14 hours, then no more pilot light and i must relight.
    Guru:
  • 462 Answers
Remove the burner and gas valve from the furnace and use compressed air to blow the area under the pilot area ans all around it. The dust and stuff usually cause a condition called "Lazy Pilot" and the flame is probably not going in the designed directions. While you have it out Id replace the thermocouple with a new one reassemble and re-lite and note the difference. The flame should be mostly Blue and no yellow (or vary little at the top end of the flame only) Orange in the top area indicates a good burning flame and the closer to the base the bluer it gets.
While you have the burner out look inside and inspect the inner heat exchanger for cracks or rusted open holes there should be none. Turn on your fan while inspecting and see if you feel the steady blow of air from it inside the heat exchanger indicating a hole. Don't confuse the air that may come down the flue with the air from the blower though. A little breeze is expected from this.
This will take care of over 90% of the problems with the "Blow out" symptom.
If you still have problems you can try and "turn up the pilot". Usually a screw close to the pilot tubing is covering the adjustment screw. Put some soap bubbles around it so you can see if it leaks or not and turn the screw out for more flame (CCW) and in (CW) for less.
Hope this helps Please grade me accordingly and good luck.
Posted on Mar 11, 2009
Colman gas furnace wont light
Is it natural gas or propane? If propane, make sure you are not out of gas. Does it have electronic ignition or a manual pilot? if pilot, make sure the pilot flame is still lit and the control knob is turned to the "On" position. If it has electronic ignition, shut off the power to the furnace and then turn it back on and see if resets and lights.
Feb 16, 2015 | Coleman 7990-319p Evcon Gas Furnace...
Why wont furnace light past the thermol coupler
There is really not enough information here to go on. If this furnace has a thermocoupling, the pilot will need to be lit manually. Follow the manufacturers lighting instructions carefully. If it still will not light you may have a dirty pilot assembly or a defective gas valve. Modern furnaces do not use a thermocoupling. There is no standing pilot light. Each time the furnace needs to be lit it will be done electronically. Many reasons why it wont light in this case. Safety control could be preventing it from lighting for safety reasons. A bad ignitor, ignition module, circuit board, gas valve, pressure switch, gas supply, induced draft motor, blocked or restricted flue pipe, cracked heat exchanger, dirty flame sensor, ect. ect. ect.
Oct 07, 2014 | Coleman 7990-319p Evcon Gas Furnace...
Coleman evcon furnace
For sensor if you mean thermocouple that sits in the pilot light I say this is usually the problem. The thermocouple needs to heat up to a preset temp before it will allow the gas to remain on. Does the pilot light stay on? If so make sure you turn the gas knob to on from pilot/light
Oct 15, 2013 | Heating & Cooling
Coleman Gravity Floor Furnace need millivolt gas valve & pilot ki
Go to www.grainger.com and look for a "power pile generator" this is a millivolt thermocouple that may be just what you need to make your heater work again
Nov 12, 2009 | Heating & Cooling
My coleman floor furnace will not stay on
Have the thermocouple replaced, ensure the pilot flame is blue - not yellow, yellow indicates blockage in pilot
Oct 08, 2009 | Heating & Cooling
COLEMAN FURNACE BURNER NOT LIGHTING
There is a thermocouple "wire" that is supposed to be touching the pilot flame.
The thermocouple senses a flame (hot) and allows the heater to operate. If the thermocouple does not sense that the pilot is on, then it will not allow the furnace to operate.
Bend the thermocouple wire (or the pilot tube) so that the pilot flame is touchingg the thermocouple.
That shouls work now.
The air from the fan should not be blowing through the same cxavity that the pilot is in.
If it is, then you may have a leaking furnace whereby carbon monoxide may be seeping into your living quarters.
If the fix above works and the pilot stays on after the heater starts, then there is probably no leak.
Let us know the results ... post a comment or "RATE" this or another expert's solution.
Sep 16, 2009 | Coleman Propane Forced Air Heater...
Short cycling..continually..minimal heat
Is this furnace standing pilot or electronic? if standing pilot turn power off then take t-stat off wall and connect the wires labeled r and c together and see if that keeps furnace working. If electronic check flame sensor you can check flame sensor buy cleaning with steel wool. if that doesn't work then try t-sat.
Jan 21, 2009 | Coleman Propane Forced Air Heater...
Pilot won't stay lit
either you are haveing a backdraft situation or your furnace heat exchanger is cracked, What I woulc reccommend is to have a professtioal service technician checkout your furnace for a cracked heat exchanger. Thanks.
Dec 26, 2008 | Coleman Heating & Cooling
Coleman furnace fan keeps turning off and on every 10 seconds...
clean your heat/flame sensor with sand paper or steal wool. If the sensor is dirty, it won't detect the heat from the flame and it shuts the gas off. Clean the soot and junk off the sensor and it should work fine. I have to clean mine every year. After spending hundreds of $$ every yr on tech calls..I figured out the problem and in 30 sec I'm up and running again.