Carrier Weathermaker SXI Model 58SX8100LG Code 12

When I wake up in the morning the furnace is out and Code 12 is flashing which is blower calibration lockout. I turn off the power which resets the computer and the unit restarts and runs fine but the Code 12 reappears and it goes out again.

The unit is 19 years old.

What do you suggest?

Posted by on

  • ky302z28 Mar 11, 2009

    Only had time to check out the door swicth and the door seems to fit good and tight and the swicth looks to be o.k.Today there was a code 44 flashing any ideals? Thanks

×

Ad

1 Answer

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Guru:

    An expert who has written 7 tips or uploaded 3 video tips

  • Master
  • 462 Answers

Code 12 I believe is power up after power off and a call for heat from the the thermostat. If you have a weak door switch that may be vibrating and going on and off it would cause this as would any thing that causes the power to drop low or out then reapply its self. try holding the door switch in while watching the board and after 2 or 3 minutes the furnace should go on to lite and the blower cycle off. If it stays in this mode try turning the thermostat off (heat - OFF -cool) and then push in the door switch nothing should happen except the lite on the board come on and stay on. If it does this than have someone turn the thermostat to heat and see if it starts or put the door on and set the heat and see if *** goes through the normal cycle of heating. If however it goes right back into the blower mode and shows the 12 code your problem is still with you. So next remove the wire on the "W" terminal on the board. Retry power to the door switch and now nothing should be on except the red lite. If it tries to start the 12 code and blower up again Im pretty sure you have a bad ignition/blower control board.

Posted on Mar 09, 2009

  • Farley Redfield
    Farley Redfield Mar 10, 2009

    Did this clear up your problem?

  • Farley Redfield
    Farley Redfield Mar 14, 2009

    Look inside the door for a legend of the codes. I don't remember what a 44 is but seems Ive seen it before.

×

Ad

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi there,
Save hours of searching online or wasting money on unnecessary repairs by talking to a 6YA Expert who can help you resolve this issue over the phone in a minute or two.

Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.

Here's a link to this great service

Good luck!

Posted on Jan 02, 2017

Ad

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Error code= two red flashes, lockout/ no flame


Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...

www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com

7 Tips and Tricks to repair your Furnace DIY - YouTube

? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check

Jan 23, 2016 | Heating & Cooling

1 Answer

I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help


A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
themobilian_3094.jpg

Oct 28, 2011 | Goodman Heating & Cooling

1 Answer

I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong


Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Oct 18, 2011 | Goodman GMS90703BXA Heater

1 Answer

Suddenly not working im not sure if there even is a pilot to be lit


Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Feb 03, 2011 | Goodman Heating & Cooling

1 Answer

My central heating is on lockout and the burner is with red light


A sampling of various codes on a furnace

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

Dec 02, 2010 | Heating & Cooling

1 Answer

I have a 90+ gas down draft furnace what burned a few minutes on and then off before turning the furnace off. The fault code would seem to indicate a Low Flame Sensor Signal. The sensor was removed and...


Hi,
What you are describing would seem to indicate that the high limit switch tripped....

Check to see if there is a manual reset high limit in that heater...also recycle the power at hte circuit breaker to reset it from a lockout to see if the high limit is an auto reset...

If none of that works then the high limit may be bad or the circuit board is bad...

heatman101

Nov 25, 2010 | Heating & Cooling

1 Answer

What are the carrier 8000ts led error codes?


They are listed inside the front panel of the main unit.

LED CODE

EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST

DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY

THE NUMBER OF LONG FLASHES.

STATUS

11 NO PREVIOUS CODE - Stored status code is erased automatically after 72

hours. On RED LED boards stored status codes can also be erased when power

(115 VAC or 24 VAC) to control is interrupted.

12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90

seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens

during blower on-delay.

13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is

open longer than 3 minutes.

- Control will auto reset after three hours. - Refer to #33.

14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.

21 GAS HEATING LOCKOUT - Control will NOT auto reset.

Check for: - Mis-wired gas valve -Defective control (valve relay)

22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is

de-energized. Inducer will run until fault is cleared. Check for:

- Leaky gas valve - Stuck-open gas valve

23 PRESSURE SWITCH DID NOT OPEN Check for:

- Obstructed pressure tubing. - Pressure switch stuck closed.

24 SECONDARY VOLTAGE FUSE IS OPEN Check for:

- Short circuit in secondary voltage (24VAC) wiring.

31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than

five minutes, inducer shuts off for 15 minutes before retry. Check for:

- Excessive wind - Proper vent sizing - Defective inducer motor

- Low inducer voltage (115VAC) - Defective pressure switch

- Inadequate combustion air supply - Restricted vent

- Disconnected or obstructed pressure tubing

- Low inlet gas pressure (if LGPS used)

If it opens during blower on-delay period, blower will come on for the selected

blower off-delay.

33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will

run for 4 minutes or until open switch remakes whichever is longer. If open

longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes

status code #33 continues to flash until blower shuts off. Flame rollout switch

requires manual reset. Check for: - Restricted vent

- Proper vent sizing - Loose blower wheel - Excessive wind

- Dirty filter or restricted duct system.

- Defective blower motor or capacitor. - Defective switch or connections.

- Inadequate combustion air supply (Flame Roll-out Switch open).

34 IGNITION PROVING FAILURE - Control will try three more times before lockout

#14 occurs. If flame signal lost during blower on-delay period, blower will come

on for the selected blower off-delay. Check for: - Control ground continuity

- Flame sensor must not be grounded

- Oxide buildup on flame sensor (clean with fine steel wool).

- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).

- Gas valve defective or gas valve turned off - Manual valve shut-off

- Defective Hot Surface Ignitor

- Low inlet gas pressure

- Inadequate flame carryover or rough ignition

- Green/Yellow wire MUST be connected to furnace sheet metal

45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;

- Gas valve relay stuck open - Flame sense circuit failure

- Software check error

Reset power to clear lockout. Replace control if status code repeats.

If status code recall is needed, briefly remove then reconnect one main limit wire to display

stored status code. On RED LED boards do not remove power or blower door before initiating

status code recall. After one status code recall is completed component test will occur.


Thanks for Choosing FixYa.


Kelly

Oct 05, 2010 | Heating & Cooling

3 Answers

Pilot light not coming on


sounds like the unit goes in lockout mode which shutting off the power and putting it back on will reset the computer now the next time it happens dont shut off the power and in the blower compartment on the board there will be a blinking light count how many times and on the door it will explain do not remove the door until you have counted the beeps throgh the little hole

Dec 24, 2008 | Ruud UBHC Air Conditioner

Not finding what you are looking for?
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo

1,364 people viewed this question

Ask a Question

Usually answered in minutes!

Top Carrier Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8220 Answers

Bill Long

Level 3 Expert

588 Answers

Donald DCruz
Donald DCruz

Level 3 Expert

17130 Answers

Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...