Question about Goodman GMS90703BXA Heater
Shutting off on pressure sw. 2 yr old goodman counter flow 80+
Unit in closet question whether switch is bad or blockage in flue or elsewhere. The inducer blower seems to be fine.
What should pressure be at inducer or switch?
  • Anonymous Mar 27, 2014
    Open pressure switch no power going to inducer motor
    Guru:
  • 462 Answers
The problem is your gettign a code and the legend is telling you its the pressure switch? From your description.
Well it is going to be rather difficult for you to check the switch without a .10" gauged water manometer gauge. It would be easier and cheaper for you to purchase another switch but if its only 2 years old the factory warranty is usually 5 years on parts. All you'd owe for is labor and freight if you have to have it sent to you. Take your model and seril no and go to who you purchased iot from and tell them what code your getting.
Some of these pressure switches and the boards that control them look for the switch to acuate both ways on and off knowing that the switch is actually working and not stuck. So you could start out by jumping the correct NC normally closed circut turn on the furnace and remove this jumper and then close the NO normally closed circut with a jumper. This isnt a fix but may help you see if the switch is actually at fault. If you get it to lite off let it cycle back off and note if it works all way through the cycle. If it does Your problem is most likely the switch because you just did all it does only by hand. DO not leave it this way because you can cause a more seveer problem and it is can develope dangerious consequences. This is just 1 way to check the switch. Another way is to check it electrically. If your femilur with open and closed circuts check across the closed and open circut whith it off then with it running and (if it has 3 terminals wires in, if it just has 2 wired in then it is not going to look for one of the operations Ive discribed). And then check and see if the voltages reverse while beginnign to lite off. If it does reverse Im betting you have a different problem and the swich is what the board has been told is giving the trouble.
Hope this is clear. If not get back to me. If it helps please grade me accordingly. THANK you and GOOD LUCK
Posted on Mar 04, 2009
The green led is flashing 3 times telling me I have a pressure switch problem My flue is clear what else could be clogged the unit is 1 yr old
its the pressure switch where the problem is Why are you looking at the flue .check connections on the pressure switch and the hoses are not split or blocked.
Dec 10, 2017 | Heating & Cooling
Furnace problems
On - OK
1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
6 Blinks - False flame sensed. Check sticking gas valve.
Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.
Closed pressure switch can be from dirty combustion vents, bad chamber pressure - like missing screws, maladjusted gas pressure, failing pressure switch, loose hoses, moisture in the hoses or fan blades The switch need to be closed to ge the unit to work
Jan 23, 2008 | Goodman GMS90703BXA Heater
I have a CCA24FCC that keeps shutting the furnace off for lack of air flow. The blower seems o be working well, i have replaced the filter even when it appears to be clean. Is there a sensor that measures...
There are 2 blowers to be concerned with. The main blower simply passes the household air over the heat exchanger to provide warm air for the supply vents. The other blower, which is more important, is the draft inducer blower. This is a smaller blower that starts first to create a negative pressure in the fire box to ensure that carbon monoxide gases will pass up the flue when the gas jets ignite. There is a pressure switch associated with this blower. When the inducer blower starts, it pulls air up thru the flue until the pressure switch activates. Then the gas jets can ignite, warming the heat exchanger. A few seconds later, the main blower will start to warm the air. If the inducer blower or the pressure switch is faulty, the furnace will not fire up.
Feb 24, 2015 | Filter Heating & Cooling
Lennox g1703-75-1 resetable switch periodically opens.
Might check you entering and leaving gas pressure first. The gas manifold I'd designed for a certain amount or positive pressure. If its a flue restriction, the induced draft motors' pressure switch wouldn't close, normally. The orifice may be damaged, crooked, or dirty? If it's just the 1 acting this way, inspect the orifice. Some furnaces have a piece of metal, inside the heat exchanger, that sends the flame/heat in a spiral form. Peer inside the openings to the heat exchanger. You should be able to see them if present. Hope this helps!
Mar 19, 2017 | Heating & Cooling
Two year old goodman gas fired unit. Led light blinks once , furnace starts up fan turns on and turns off. will not fire gass. art.obryant@yahoo.com
Hello. sounds like a pressure switch issue, the pressure switch is open it must checked for a restriction in the flue pipe or blockage in the vent, the tubing going from the inducer motor to pressure could be loose, blocked, or have water in it, or the switch it self is going bad.
Mar 05, 2011 | Heating & Cooling
My furnace will not light. What does it mean when the red light on the circut board flashes 3 times?
Hello, a 3 flash on a circuit board means that a pressure switch is open, this could be due to a blockage in the flue pipe or the small tubing that goes from the inducer to the pressure switch is loose, leaking, or is blocked. You can try taking the tubing out and checking if there is anything in it blocking the pressure between the pressure switch and inducer motor and then attaching back on and make sure it's secure and tight. If that does not work that the switch itself is bad and must be replaced.
Jan 22, 2011 | Goodman GMS90703BXA Heater
Hi I have a old unit built in my bedroom closet! I hear heat pump sleep pump...? Well anyway it runs off water for cold air then returns (recycles) for the heater! There is only one part to my unit (In...
Seems like 80-85psi is too much supply pressure. I would adjust the pressure switch on your well pump. If it's a 1 horse pump or so- you should be able to go buy a new pressure switch that is pre-set for about $20.
Jan 20, 2011 | Heating & Cooling
New gmh95/gch9 system. getting a diag. code 3 flashes, [pressure switch area]. all flues clear, hoses clear,drain lines working. left side down application and i just installed kit #000143- flue drain ....
I like the unit.How new?Check the pitch/tilt of flues they cant sag or haue dip/low spots.How many 90degree elbows on exaust pipe?Approxmately how/long many feet is pipe?
Mar 27, 2010 | Goodman Heating & Cooling
Heater wont start
does inducer motor come on?motor will be right below flue pipe inlet.if so make sure pressure switch closes.pressure switch tube could be kinked.also make sure furnace has good ground.sometimes not being grounded will cause this
Dec 31, 2008 | Goodman GMS90703BXA Heater
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.