Ducane 20kw furnace with heat pump/ as long as the outdoor unit is running the indoor unit runs fine. If the outdoor temp falls below the setting on the outdoor units outside stat the 30amp breaker to the furnace breaks. Pulling 21amps. on the circuit when the outdoor unit is running. The wire is 10-2 w/gr. The 60amp circuit will pull 42amps or 21 depending on the number of strips that are on. It is on 8-2 w/gr. The unit is new. Of course didn't have the problem till outdoor temp dropped enough to show the problem
  • 3,361 Answers
20kw heat should have 2 separate 60 amp circuits on number 6 wire.
Posted on Mar 03, 2009
My heat pump froze and now has an E-6 error on screen and does not run
Lost communication between indoor and outdoor, did you shut both indoor and outdoor off?
Feb 11, 2015 | Heating & Cooling
Model Number: UACC-036JAS The unit works fine. The problem is it doesn't shut down after the specified temperature has been reached. The furnace blower shuts down, but the ac unit keeps on running....
Hello, usually a stuck contactor coil will cause this on the outside unit. When the outdoor unit runs continously and the indoor blower does not run no heat is being absoebed by the evaporator coil and thus the line freezes. Replaceing the contactor will fix the problem.
Aug 30, 2011 | Ruud Heating & Cooling
No heat, no ac. Power apparently not getting where it needs to be. Checked the fuse in the unit (5amp) still good. I have non-fusable boxes located next to furnance inside (crawlspace) and outside unit....
Hi, you do have a power problem, that's for sure.If the indoor unit has a non-fused box, and condenser also, it would have to be at the main breaker. That's the only power source you have that supplies power to everything is the main breaker. If you are sure you have power to the main unit, 120 volts to the furnace, you should have a led light that's is on, and its either red or green. This will tell you there is power there. The 5 amp fuse is for the secondary control voltage, 24 volts.If you could unplug your furnace in the craw space and plug something else in to check for power, you would know for sure. You may just have a faulty thermostat. If you turn the switch, fan switch to on, it should come on. If not, you have lost power. If you have a volt meter, this would be very helpful. You could have a bad transformer, but normally the 5 amp fuse will blow to keep the transformer from blowing out. I would check the fan switch, turn it to on and see if it runs, if not, you have lost power at your indoor unit. Make sure the panel on the indoor unit is put on right, as most of them have a panel switch on the perimeter that closes when you put it on to restore power. If its not on just right, it will keep the switch open, and you will have no power, so double check that panel. Check the led light, door switch, power to the indoor unit, and let me know what you find. It should be pretty easy to find where the problem is, if you are in the heat mode. This eliminates the outdoor unit, so you will know it is the indoor unit. Please let me know and keep me posted. You will find it, its a easy fix.
Shastalaker7
A/C, & Heating Contractor
Nov 30, 2010 | Heating & Cooling
I just turned on our heat unit "FA4A AC/Heat Pump"
There probably isn't a reset button=magic fix. With it in heat pump mode and tstat set above indoor temp, check your outdoor unit to see if it's operating. If not, check all breakers to it. Can you see any ice accumulated on the outdoor unit? If it is running and not producing heat, turn the tstat to emergency/auxiliary heat. and the heat pump turned off to prevent damage. You'll need a service tech.
Nov 04, 2017 | Heating & Cooling
I have an goodman model # gsc130241ae ac unit outside it will not come on, no hum, fan doesn't run thermostat control is good swaped out with downstairs unit. Gas heat unit is in the attic, I don't use...
Does the blower indoors run and move air? if not it would mean that you don't have power to the furnace.
The 24 volt transformer in the furnace is used to power the thermostat and the control circuit on the A/C unit outdoors. Or you could have blown a fuse on the computer board in the furnace.
If this has helped please rate me, and If you need more help, give me some more info.
Thanks,
Paul
Apr 02, 2010 | Goodman CLQ36AR49 Air Conditioner
It's cold out, and my Central Air kicks on every time my furnace kicks in. I get heat, but don't think my outside unit (fan) should be kicking in each time my furnace kicks on. Suggestions
Hi, If you have what is called a heat pump, the outdoor unit is supposed to run. It has a reversing valve which reverses the flow of refrigerant and the indoor unit becomes the condenser and the outdoor becomes the evaporator coil. Now, if you don't have a heat pump and the furnace is gas fired, then the control wiring or thermostat is calling for both to come on. Control wiring has to be touching together somewhere and bringing on both. Look over the exposed stat wire outside if you have a dog that may have chewed the wires, I have seen this happen. If all wiring looks good, then the stat is faulty and must be replaced. Make sure you don't have a heat pump first, as the fan, compressor, and all will run on heat and cooling. I hope this will solve you're problem, please let me know, I would like to hear back. Sincerely,
Shastalaker7
Nov 20, 2009 | Heating & Cooling
I have power running to the indoor units but the heat pump and the indicator lights are not comming on. It's like there is no signal from the heat pump got any ideas?
Have you checked the breaker to the outdoor unit? Have you checked to see if your indoor unit is calling for it to come on? You will need to do a complete breakdown on the unit to see if the two are communicating with each other. It could be the control board outside.
Apr 01, 2009 | Mitsubishi MXZ30TN Air Conditioner
Furnace runs on heat, air conditioner does not
If you have a Gas furnace in the Attic then the answer is yes. The outside condenser will not run if in fact you have a gas furnace.
Feb 11, 2009 | Ruud Central System Air Conditioner
Heat pump not running
Depending on the age of the unit it could be several things, does it have a circuit board? Contactor could be bad, freon leak if it has a low pressure switch, burnt wires, connections, etc. Do a complete visual and check for 24 volts, does the indoor unit run? Transformer may be bad.... No indoor unit - no outdoor unit, most of the time the outdoor unit gets its 24 vac power from the indoor unit which runs them both, look for fuses (like car fuses)..