My heat pump was running fine untill a week ago, the ouside unit star making a noise and stop working, check for freon it was okey , but one of the two contactor was bad, so I replace it and still doesn't work, the inside unit works fine, can you get me advice on this?
  • 3,361 Answers
Need a brand name and model number.
Heat pumps only have one contactor by that part name.
Posted on Mar 02, 2009
Brand New 2 weeks old 4 ton Trane compressor leaks a lot of water onto pad
If the unit is running in cold weather than there is ice building up on the coils located outside. This is normal in that the unit is running in heat pump mode heating inside and cooling outside, After the unit detects the ice build up it briefly reverses the cycle heating the outside coils melting(defrosting) the ice which you observe as water on the pad.
The video gives you an example of the defrost cycle!
2012 Trane XL15i Heat Pump Defrost Cycle Steam Show
Dec 21, 2015 | Heating & Cooling
I have a RUUD Heat Pump Model UPPB-024JAZ the outdoor pump stopped working last week. The reset button fixed the issue but whhy does it keep going off.
To start with, the tech charged you for an hours worth of service and only pushed the button. GET YOUR HOURS WORTH!
•The outdoor coil needs to be cleaned. Turn off power at the breaker and t-stat, clean the coil with water hose
•The outdoor fan motor may be slowing down or stopping due to motor bearings dry or weak run capacitor. Any noise/squealing from motor?
•Too much freon in the system.
•A restriction in the freon system.
•A improperly installed/mismatched system
•A (kynk) in the liquid line(3/8 copper)
•A stopped up or clogged filter dryer
•A dirty indoor coil that has an expansion valve(txv) will run too cold and the valve can close near "seated"
All of these, and more, can cause a HIGH PRESSURE SWITCH to open. When yours open, you have the red button to push which resets it(the switch). I have also found that the plenum(duct box that connects to your indoor unit at the discharge air) is supposed to be tapered to the air opening size of the blower outlet but that's hard to explain. If the plenum size is the same size of your indoor unit, width and depth in the upright position, the your plenum is not "tappered"(goes from one larger size to smaller size where connected to the I.d. unit). In that scenario, the high pressure switch opens during heat operation, not cool. I know, confusing. Try cleaning your o.d. coil first. And try to get an hour of work(or close) for an hour paid. And WORK SAFE!
Jun 20, 2015 | Ruud Heating & Cooling
Hammering sound ptac
heat pump? possible causes: low freon. clogged / dirty coils. blower motor running?
Jan 20, 2014 | Heating & Cooling
I have a Pentair Mastertemp 400 using LP that stopped firing 2 weeks ago. Troubleshooting showed igniter so I replaced it and all worked fine. Old one still showed about 50ohms but was still replaced. The...
Is it Propane or Natural gas? Check your gas supply pressure.Also, open up control panel, accessable by removing the plastic exterior panel with 4 screws, check to make sure no critters got in and chewed wiring.
Jul 20, 2017 | Heating & Cooling
2 weeks ago one of my units stopped working properly. It got warm during the night even though I heard the unit running. I shut it off and called for repair service. They changed the thermostat and it...
sounds like the coils inside the air handler/furnace are freezing up. likely cause is the freon charge is incorrect (probably undercharged). it may have been correct when the tech did the work but some may have leaked out. it is slightly possible too that the system is overcharged. you should have the system pressure verified, and then have it checked for leaks.
Jun 16, 2009 | Goodman CLJ36AR42 Air Conditioner
My haier a/c window unit is spitting water through the vent
check the filter located behind the front panel it usually snaps out also make sure the drain holes on the out side bottom of unit are not stopped up and that the unit is leaned back slightly for drainage freezing is a sign of low air flow or low on freon the coil actually gets colder when freon starts to leak out hope this helps with your problem
May 15, 2009 | Haier hwr10xc6 Air Conditioner
Fan motor comes on, however, when a/c is turned on, breaker pops
If the unit is working fine in heat mode and in fan only mode, you have a short in the wiring going to the ouside unit. If it were a fan relay, then everytime the fan came on the breaker would trip. But either way, there is a low voltage short taking place in the unit. If the compressor was bad, the indoor unit would run fine and would only blow the breakers to the ouside unit. I had a unit last summer that did the same exact thing. After I replaced the control wiring to the outside unit, everything worked like a charm. Good luck!
Apr 04, 2009 | GE Heating & Cooling
Triton electric shower T90si ran dry and not now working.
pump needs attention and the heating element has burnt out
pump needs water to run and the heater element needs water to keep it cool
Sep 07, 2017 | Heating & Cooling