Question about Goodman CLJ30AR32 Air Conditioner
Code #33 on Bryant 355MAV 90i Furnace
Have been getting a code #33 on my Bryant 355MAV 100k btu furnace, Evolution controls (installed new 2006) every heating season for three years since we built the house. Installers solution was to turn down gas pressures (lp) which, while allowing the furnace to run, ultimately led to heat exchanger clogging (soot)and replacement (parts covered under warranty, labor $1,500 not covered). Control Board and personality plug also replaced. Now back to the same code #33, just replaced fan limit switch with same OEM model limit switch - same problem. Furnace will run fine if I jumper fan limit lead wires. Otherwise, I have to go down and turn breaker switch off then on again to clear the code 5-6 times per day. Output temp at top of plenum is 120 deg, return air 64 deg. Limit is not suppossed to trip until 180 deg! Return clean, new 30 day filter (not HEPA), 2 returns, one each side of return cabinet, one 14" and one 20". Installer is now out of business and I have been through 2 other service companies. Bryant has been very little help, other than covering parts under warranty - they just keep suggesting other parts to replace.
Any help appreciated.
  • jeepfamily1 Mar 01, 2009
    Thank you for your response. The LP conversion kit was installed originally (LP stickers present on gas valve) and the orifices were changed out again with the correct LP orifices by the first svc co just to be sure. I tried to include as much info as I could in the initial post. I have checked static press. (using the Evolution control) on both high and low fire: Low: CFM = 1097, Blower RPM = 608, Static Press 0.11 High: CFM = 1520, Blower RPM = 868, Static Press = 0.27.
    2 zones, both Airflow limits set to MAX, all registers open full, No Dehumid installed, but Dehumid set to High (to increase airflow). New, low resist 30 day filters installed in both returns.
    Jeepfamily1
  • jeepfamily1 Mar 08, 2009
    Resolution:
    After many phone calls to customer service, Bryant has reviewed our case and agreed to replace the furnace with a newer model (3-stage 355CAV 95S) at no charge. It was installed Friday and so far has been working like the first one should have. One note, the new 3-stage furnaces require a new Evolution thermostat to fully utilize the 3 stage abilities of the furnace (low med hi). Bryant has agreed to replace our original 2-zone Evolution thermostat controller as well, since they suggested the 3 stage furnace as a replacement.
    All told, we have spent over 40 hours and $2,000 getting this resolved, but now that we are warm again - what else can we say?
    Be persistant and don't let the manufacturer off the hook.
'Limit or flame rollout switch is open'. In my case, the flame rollout switch had tripped due to an overheating? I had to push the button between the wire leads to reset the switch. Then when I turned the power back on, the furnace started up like normal.
Why did the switch overheat and trip? My current theory is that there was a rubber grommet around a pipe near the switch that had slid down and was no longer sealing the furnace?
Posted on Dec 21, 2009
Evaporater coil condensation with air on unit 14 years old 90i forced air
Posted on Aug 04, 2009
  • 360 Answers
Make sure the unit is properly set up (jetted/orifices) for LP. It sounds to me like the unit is setup for natural gas and is being used on propane.
Posted on Mar 01, 2009
I NEED THE HEATING CAPACITY FOR A Bryant mod 580JE05A072A2A0AAA
All heating capacities are on the furnace label. Inlet BTU's and Outlet BTU's. Outlet BTU is what is heating your home.
Apr 19, 2017 | Bryant Heating & Cooling
Bryant plus 80 furnace no fan/ operation , yellow constant flashing light code , power to furnace was rerouted during remodel and since then furnace stopped working. Any suggestions ?
You need to have/ know the "fault code" chart for that specific furnace. Count the number of flashes and refer to chart. Look on the inside of the furnace blower door or other panel. Also look up on internet and print it off. If the furnace was allowed to run during the remodel it voids the warranty automatically. Read the installation manual.
Try resetting the electronic board by turning the power off then back on.
Mar 29, 2017 | Bryant Heating & Cooling
On a Bryant furnace 373lav what is error code 41 furnace tries to light imonitor lights up but the won't light
Code 41= blower out of valid speed range. you will more than likely need a new motor module. they are not cheap 300$ to 400$. If you call a carrier or bryant tech out they should have a test module they carry on their truck that lets you know if its the furnace circuit board or motor module.
Jan 02, 2015 | Heating & Cooling
HK42FZ034 status code light blinks in pattern
Located on the schematic on the inside of the furnace door should be a key for the blink sequence. 2 short blinks then 4 long ones would be a code 24 on that data plate
Apr 13, 2014 | Carrier Furnace Control Board Bryant...
Bryant furnace plus 90 led code is blinking once then 3 times fast. What does it mean?
these codes are on the inside panel of the front cover of the furnace. lift off and look inside.there should be a code explain chart on the panel by the light. this panel will need to be replace correctly for the furnace to work as there is a door switch.
Jan 31, 2011 | Heating & Cooling
Code 33 - changed filter need to reset - how??????
Should reset by shutting off power to furnace and then back on With a Bryant if you turn power off and then on, if the thermostat is calling for heat when power is restored blower will run for couple minutes before trying to fire furnace. This is normal
Jan 23, 2011 | Bryant Heating & Cooling
Bryant Plus 90i furnace vibration
You have not mentioned if the vent pipe has any anti-vibration mounts or not. If not, use rubber mounts to suspend the vent. It may be transmitting your noise.
Mar 11, 2010 | Heating & Cooling
I have a Bryant Plus 90i furnace and a Bryant2.5 A/C
go mid.range....cfm dont go to hi spd or no cooling pick up
Aug 18, 2009 | Bryant Heating & Cooling
Filter for Bryant plus 90i
Bryant Furnace Filters www.iaqsource.com Every Bryant filter in stock For every Bryant furnace and AC
may want to check on the filter itself and the housing for numbers that could assist its type and size
this site may help you
Jul 04, 2009 | Goodman CLJ30AR32 Air Conditioner