Nordyne electric furnace. T-stat replaced last year. Fan comes on when set to auto in A/C mode but fan will not come on when t-stat is set to heat. Is this a bad sequencer or fan relay. This is a Nordyne E2EH-015HA model.
  • ptricia325 Feb 28, 2009
    Yes. all elements heat up. fan won't come on in auto mode, but will in A/C.
  • Farley Redfield
    Farley Redfield May 11, 2010
    from the model number it looks like this is a 15KW heater?
    3 elements usually? And do you know if any of the electric elements are comming on?
  • 334 Answers
Does ANYTHING come on when set to heat?
Posted on Mar 06, 2009
Blower fan continually runs
It may be but the fan control may be set to turn off at to high a temp, or theres a short between ;r; and g at the stat or furnace or sequencer, IF it runs through it. A limit or rollout switch may have failed but this will keep the unit from firering. Check for a manual blower switch that may be on. At stat it should be at auto and alsso at the fan control. A stuck relay is always possible,
Mar 08, 2015 | Coleman Home Electric Furnace Eb15b/Eb15d
I need a wiring diagram for a furnace Nordyne model # E1EH-012HA. the problem is, the fan will not run in heat mode. The fan works in AC mode and when the t-stat is set in manual mode. (fan) I found a...
you need to set either the switch on the back of the tstat to HE NOT HG or in configuration mode you want the "tstat controls the fan" not "equipment controls the fan" or ELECTRIC HEAT NOT GAS HEAT.
Oct 10, 2017 | Heating & Cooling
I have an Intertherm electric furnace an sometimes it won't start but if I shut off the Tstat then turn it back on the furnace runs fine for awhile thought that it was T stat then thought that it was...
Electric strips have what's called a Sequencer also called a stack relay it's a relay that brings on the fan and strips at the same time on a call for heat. If you have more than 5kw you will have more than one Sequencer in fact you will have one for every 5kw.(only the first one will bring on the fan) It could be your high limit making your unit stop heating before it reaches the temp set on the T-stat. Check and see if your getting proper air flow across the electric strips your filter could be dirty. If not remove the cover from your T-stat and take the red and white wires off and twist them together this will bring on the heat then just watch the unit for about an hour if no problems then you have a bad T-stat. If the unit does cut off and the fan seems to be blowing fine you might have a bad high limit switch.
hope this helps........
Nov 18, 2010 | Heating & Cooling
I have an intertherm electric furnace FEH-A020, with multispeed blower installed when A/C added. My problem is blower operation. at the end of the cooling season with fan set to auto operation the fan ran...
The model of T-stat you gave comes up as a discontinued model on Honeywell's web site, but it looks to be a manual stat that type of stat would have to be wired with a summer winter switch with electric heat, allowing it to turn on the fan with a call for heat. If yours is a programmable T-stat you would need to select electric heat or in the installers set up change the default setting for fan from unit controls fan in heat to thermostat controls fan.
Oct 17, 2009 | Intertherm P3RA-048K Air Conditioner
Bryant-Carrier Furnace Fan Stays On
I suspect a bad fan relay or bad fan control. Maybe the longer the control or relay is in the on position the more chance of it sticking on.
Oct 17, 2009 | Bryant 462AJC021BA Air Conditioner
Fan will come on for heat(auto), but not for AC or set to ON
You have a blower relay in the furnace that's probably bad. In the heat mode the blower is on a temperature relay, in cooling mode the blower has to come on immediately so there is another relay for cooling. The green wire on the thermostat feeds that relay, so if you go to the furnace and shut the power off and find the green wire from the thermostat that feeds that relay and replace it, being careful to mark all the wires before removing them, also the relay terminals have numbers for identification.
Apr 07, 2009 | Heating & Cooling
I have a nordyne elec furnace just put in a new heat sequencer
You need to check the low voltage side to see if the t-stat is calling for heat. If it is, it is either the sequencer or a fuse to the heating elements (older model). But most likely the squencer. If you have a meter, you can check to see what side of the sequencer is burnt. Could also be a relay depending on the model number. If you get me the model number, I can send you a copy of the wiring diagram for the unit. This is the brand that I deal with.
Mar 02, 2009 | Better Living SPP High Efficiency...
Fan relay or sequencer.
If it were the sequencer, the heat wouldn't come on at all but the fan would blow. It's the fan relay but it could be the t-stat again. If you get a power surge when the unit is running, it can short out that portion only but typically, it will short out either the heat or the cool side depending on what is running not just the fan.
Feb 28, 2009 | Better Living SPP High Efficiency...
Nordyne electric furnace heats up but fan won't come on when set to auto. Is it a relay switch. Have installed a new thermostat.
If the fan runs in the ON setting then you have a bad fan relay for the heat mode.
Did you install the t-stat before or after the problem?
If after, you have a bad fan relay.
Feb 21, 2009 | Heating & Cooling
Furnace will not turn on in Auto mode thermostat
It sounds like you T-Stat is messed up. Look in your manual to see if there is set up instructions. If not I would change the T-Stat.