Question about Better Living SPP High Efficiency Home Heater, ...
Fan relay or sequencer.
Nordyne electric furnace. Heats up but fan only comes on in fan on mode. T-stat replaced last year. Is this a sequencer or a bad fan relay?
  • 659 Answers
If it were the sequencer, the heat wouldn't come on at all but the fan would blow. It's the fan relay but it could be the t-stat again. If you get a power surge when the unit is running, it can short out that portion only but typically, it will short out either the heat or the cool side depending on what is running not just the fan.
Posted on Mar 16, 2009
Blower fan continually runs
It may be but the fan control may be set to turn off at to high a temp, or theres a short between ;r; and g at the stat or furnace or sequencer, IF it runs through it. A limit or rollout switch may have failed but this will keep the unit from firering. Check for a manual blower switch that may be on. At stat it should be at auto and alsso at the fan control. A stuck relay is always possible,
Mar 08, 2015 | Coleman Home Electric Furnace Eb15b/Eb15d
Nordyne model FEH-017HA-04 furnace...the fan comes on full force with ac but not when furnace comes on
On newer furnaces the fan starts in a period of time factory set and is initiated by the control board. The air conditioning fan is started by the thermostat and starts right away when the stat calls for cooling. You will need a tech. familiar with this model and carrying the right parts to look it over. Does the furnace fire and then shut off in a few minutes? If so, it is most likely to be the board. Sorry. It may be pricy.
Oct 24, 2013 | Electric Circuit Breaker Kit for Furnace
I need a wiring diagram for a furnace Nordyne model # E1EH-012HA. the problem is, the fan will not run in heat mode. The fan works in AC mode and when the t-stat is set in manual mode. (fan) I found a...
you need to set either the switch on the back of the tstat to HE NOT HG or in configuration mode you want the "tstat controls the fan" not "equipment controls the fan" or ELECTRIC HEAT NOT GAS HEAT.
Oct 10, 2017 | Heating & Cooling
I have an Intertherm electric furnace an sometimes it won't start but if I shut off the Tstat then turn it back on the furnace runs fine for awhile thought that it was T stat then thought that it was...
Electric strips have what's called a Sequencer also called a stack relay it's a relay that brings on the fan and strips at the same time on a call for heat. If you have more than 5kw you will have more than one Sequencer in fact you will have one for every 5kw.(only the first one will bring on the fan) It could be your high limit making your unit stop heating before it reaches the temp set on the T-stat. Check and see if your getting proper air flow across the electric strips your filter could be dirty. If not remove the cover from your T-stat and take the red and white wires off and twist them together this will bring on the heat then just watch the unit for about an hour if no problems then you have a bad T-stat. If the unit does cut off and the fan seems to be blowing fine you might have a bad high limit switch.
hope this helps........
Nov 18, 2010 | Heating & Cooling
Bryant-Carrier Furnace Fan Stays On
I suspect a bad fan relay or bad fan control. Maybe the longer the control or relay is in the on position the more chance of it sticking on.
Oct 17, 2009 | Bryant 462AJC021BA Air Conditioner
I have a nordyne elec furnace just put in a new heat sequencer
You need to check the low voltage side to see if the t-stat is calling for heat. If it is, it is either the sequencer or a fuse to the heating elements (older model). But most likely the squencer. If you have a meter, you can check to see what side of the sequencer is burnt. Could also be a relay depending on the model number. If you get me the model number, I can send you a copy of the wiring diagram for the unit. This is the brand that I deal with.
Mar 02, 2009 | Better Living SPP High Efficiency...
Bad sequencer or fan relay?
does ANYTHING come on when set to heat?
Feb 28, 2009 | Heating & Cooling
Nordyne electric furnace heats up but fan won't come on when set to auto. Is it a relay switch. Have installed a new thermostat.
If the fan runs in the ON setting then you have a bad fan relay for the heat mode.
Did you install the t-stat before or after the problem?
If after, you have a bad fan relay.
Feb 21, 2009 | Heating & Cooling
1970's Rheem electric furnace
no the older rheems had a sequencer for the heat that turned on the blower at the same time that the heat strios are energized. so the first thing that you need to do is figure out the sequencer that is keeping the fan running and get it replaced.
Jan 30, 2009 | Honeywell CT3200 5-2 Day Electronic...
Wiring NO, NC relay on Nordyne furnace
NORDYNE , GOODMAN, AND NUTONE ARE ALL BUILT BY SAME MFG SO IF YOU TRY ALL THESE MAYBE YOU CAN FIND THE HELP YOU NEED
Jan 12, 2009 | Electric Circuit Breaker Kit for Furnace
Better Living SPP High        Efficiency Home Heater, ... Logo
154 people viewed this question
Top Better Living Pool & Spa Experts
Jay Finke
Jay Finke
Bill Jordan
David Spradling
David Spradling
Are you a Better Living Pool and Spa Expert? Answer questions, earn points and help others