Question about Cutler Hammer 1 Pole 15 Amp Ground Fault
Ground Fault circuit Breaker trips each time a load is applied
A Cutler-Hammer Ground Fault circuit Breaker Type GFCB - Type HAGF trips each time a load is applied. If the circuit is changed out to a regular (non- ground fault) circuit breaker the load will not cause the circuit breaker to trip. The circuit is for 6 outside receptacles app. 100 feet of 12/2 w/ ground Romex wire.
  • Anonymous Mar 24, 2014
    The light keeps tripping the gfi then shuts off circuit breaker
  • swaa88 May 02, 2014
    sounds like the gfi was wired wrong or it is defective
  • 653 Answers
The most likely causes in their order of probability are: 1) water somewhere in the circuit causing the hot wire to ground; 2) a legitimate trip caused by a defect in a device plugged into the circuit; and 3) a defective GFCI breaker. In the first case, wait until it has been dry for about a week and see if it trips. In the second case, make sure there is nothing plugged into the circuit and try resetting. In the third case go ahead and put the regular breaker in, then put a GFCI outlet into the first box downstream from the breaker. If installed according to the directions, that outlet should protect all of the outlets downstream.
Posted on Feb 27, 2009
  • Fahr Quad Mar 06, 2009
    I forgot to mention that with 12/2 wire, you can use a 20 amp breaker with up to 13 duplex outlets (120volts x 20 amps = 240 volt/amps. 240 va/180 va per duplex outlet = 13.33333 outlets allowed). On a 15 amp circuit, there can be up to 10 outlets (120v x 15a = 1800va/180va=10 outlets). The issue is not that the circuit is overloaded.
  • Jake Meffer Jul 16, 2013
    Ok ,it suonds like the breaker so I will just go ahead and swap it out . If I can only find it.
Ge circuit breaker tripping
1. Replace breaker (quick & cheap) ... they do go bad.
2. Find the short.
Jan 11, 2014 | Cutler Hammer 1 Pole 15 Amp Ground Fault
Arc fault breaker trips when you turn florescent and can lights on
Sounds like something is wrong with the light check the wiring. Unhook the light and try ther breaker if breaker does not trip then problem is in the circuit.
Jul 24, 2011 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
Bought a Eaton Cutler Hammer Arc Fault 15 amp Single Pole circuit breaker for my old CH20 model Cutler Hammer CB Box (vintage about mid 1960s). CB package says "Use in Type CH" boxes. It...
I used to run into that being a service electrician all the time Smains! These problems can involve a little more legwork to figure out than some. The best advice that I can give you is, if at that age you can still find a part number on the breaker panel (they renamed them load centers to sound fancy lmao), if you can actually fine a legible one. Write it down and go to Eaton's website, then to load center. They have a parts number search that should take you right to your PANEL lol, and all the specs. I'm not there or if do it for you, hope this helps!!!
Aug 18, 2017 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
Cutler-Hammer RD320T33W. I am experiencing random trip events with no load or very little load. What should I check for defect?
If I remember correctly that is a pretty good size breaker, and I would strongly suggest that if you are not a qualified journeyman electrician or higher I would not go any further with this it can be extremely dangerous. Random tripping can be caused by several causes good chance that breaker is faulty. If this is the 2000 amp 600 volt breaker I strongly suggest calling a fully licensed electrician.
May 19, 2011 | Cutler Hammer Electrical Supplies
Our circuit breakers keep tripping. The house is only 12 months old and our electrician says the builder installed Cutler Hammer Combination type AFCI is the problem. Is there a problem with these being...
They can be defective, but usually not. It is usually something that is plugged in that will not operate on the arc fault circuit. Brush type motors are bad as they are actually arcing at times. Unplug all devices, and try to find the culprit. These are for your safety, and once you find the problem devices you should be fine.
Sep 09, 2010 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
How to reset Cutler Hammer 1 pole 15 Amp
Turn handle to off position and then back on. Same as any other breaker. The red test button can be pressed which will trip breaker. If it trips immediately,unplug all devices on circuit and try to reset. Reconnect each device and see which trips breaker. If this goes to outdoor receptacle, check behind cover for moisture.
May 25, 2010 | Cutler Hammer 1 Pole 15 Amp Ground Fault
I have a question
Sounds like the breakers are mis-wired. This is a common mistake with those kind of breakers. The white wire that is permanently attached to the breaker (usually coiled) connects to the neutral bar in the panel. Look closely on the breaker, you will see two terminals. The white (circuit) wire that goes out to load connects ONLY to the neutral terminal _on_ the breaker itself, _not_ to the neutral bar in the panel.
Dec 17, 2009 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
Cutler Hammer 1 Pole 15 Amp Ground Fault Logo
1,182 people viewed this question
Top Cutler Hammer Electrical Supplies Experts
Steve
Hippy_dd
Craig Butler
Craig Butler
Are you a Cutler Hammer Electrical Supply Expert? Answer questions, earn points and help others