Question about Aprilaire 600 Humidifier
Solenoid won't open--voltage drops when connected to humidistat
Our Aprilaire 600 humidifier's solenoid doesn't open, so no water ever goes through.  I think I've isolated the problem to the solenoid itself.  The humidistat is providing the right voltage to the solenoid when the heater is on and blowing heat (I verified this by disconnecting the humidistat's wires from the yellow solenoid wires and used a multimeter--showed 24V).  But when I connect the wires back to the solenoid, and go through the same process, it only shows 0.1V, and the solenoid doesn't click or open. So it seems the solenoid is messing with the voltage?
My humidistat is set to manual, and I've verified the voltage as well at the humidistat H terminals and found the same results (24V when not connected to the solenoid and heater on, 0.1V when connected and heater on).  On a side note, the humidistat clicks but the solenoid never does.
Any ideas what to test next?  Everything else in the chain is working (checked filter, saddle valve, and blew through top part to make sure there were no obstructions--there weren't).
The coil may shorting out the 24vac supply to the solenoid. Recommend replacing soleniod.
Normally you should be able to read the 24vac across the solenoid when energized.
The other option is to get a 120vac to 24vac transformer and test the solenoid. This way you will know if the solenoid is the cause or the 24vac source is the problem.
Posted on Mar 10, 2009
Solenoid valve
The humidistat could be defective.
Dec 04, 2013 | Aprilaire 700 Humidifier
Water to humidifer won't turn on.
Check if there is power to the solenoid valve, if ther is , then the solenoid is bad and must be replaced. If there is no power could be a bad humidistat or transformer.
Dec 19, 2012 | Aprilaire 600 Humidifier
My aprilaire 600 continues to have water running down the drain at all times, whether the furnace is running or not.
Hello, usually when a humidifier continues to run with the furnace off it means that the solenoid valve is stuck open and must be replaced.
Feb 19, 2011 | Aprilaire Humidifiers
Have Aprilaire 600. Water will not flow thru unit
Hello, most likely the solenoid is bad and must be replaced. If you are getting 24 volts to the solenoid and it does not open replace the solenoid valve.
Feb 13, 2011 | Aprilaire Humidifiers
Air inside house feels dry. Not sure if humidifier is workng. 1. regardless of outside temp (between 10 degrees and 40 degrees F) the humidity never goes above 28% even with the humidistat turned to the...
Sounds like you are not getting the proper voltage to the solenoid valve...
Check for 24v coming off of the transformer...that may be 24vac not vdc...
Then check to see if there is power coming from the humidistat...
unhook the wires to check for the power at the solenoid valve...
check across the two wires...
if there is power the valve is bad and that alone will cost about 90 bucks with shipping...
if there is no power trace back and see where the power stops at...
heatman101
Jan 20, 2011 | Aprilaire 400 Humidifier
Aprilaire 400 humidifier. No water flowing to the pad. I've checked the supply -- working. Replaced the solenoid, not working. Checked the electrical to he solenoid wnen system callilng for water -- no...
Check to see if you are getting 24 volts from the transformer, if not, turn off power to the transformer and check the resistance of the secondary side, if no resistance the transformer is bad and need to be replaced. Also check to make sure all the wires are secure. If you are getting voltage at the transformer then bring power directly from transformer directly to solenoid valve and it should click open and let the water through, if it does then either the sailswitch/current sensing relay is bad or humidistat is bad.
Jan 17, 2011 | Aprilaire 400 Humidifier
Should water be continualing running through the drain tube?
Water will flow over the filter pad as long as the unit is calling for humidity. once the unit is satisfied the solenoid valve should stop the water flow. if the water continues to flow with out call then solenoid valve has failed open. hope this helps.suppling an owners manual in case you need one.
http://www.aprilaire.com/themes/aa/en/manuals/AA-Humidifier-Owners.pdf
Dec 21, 2010 | Aprilaire 600 Humidifier
There is no water coming out, i have an aprilaire 600 model with a manual controler
The first thing you want to check is that the saddle valve is open and that water is getting to the solenoid. If you are getting water to the solenoid but it's not going through then most likely you are not getting power to the solenoid. When there is a call for heat you should be getting 24 volts to the solenoid and it will open allowing water into the humidifier, if you are not getting 24 volts then check the transformer make sure it is giving you 24 volts.
Dec 18, 2010 | Aprilaire 600 Humidifier
We just bought a house with an existing Aprilaire 600 humidifier. It is now heating season and we ae running the furnace. I turned on the humidifier and no water is getting to the pad.The water line is ok...
Hello,Make sure the heating blower/fan is running when you turn the dial as the humidifier might not have power if there is no heating blower operation.
Nov 06, 2010 | Aprilaire 600 Humidifier
Aprilaire 600 problem
It sounds like you got it...
The solenoid will not open with only 13 volts to it. Jump or apply the full 24-27 volts to the solenoid and see if it clicks and opens and allows water to flow.
If the valve still won't open or pass water, start looking for a plugged inlet solenoid inlet screen or a faulty solenoid valve as well as a faulty humidistat.
Jan 06, 2010 | Aprilaire 600 Humidifier
Aprilaire 600 Humidifier Logo
708 people viewed this question
Top Aprilaire Humidifiers Experts
Paul Carew
jdthefixer
Mack Baxter
Are you an Aprilaire Humidifier Expert? Answer questions, earn points and help others