Heat temperature issues with Goodman GMP 100-4 furnace
The problem that i am having is that the furnace blows around 92 degree air. It cycling and getting my thermostat to temperature. I have extra thermometers sitting all around my house and i have confirmed that i have about a 3 degree temperature drop from shoulder level thermostat to floor. When i raise the temp on the thermostat the furnace will blow much warmer air(around 130 or so) until it gets the thermostat there and then cycle off. Then the cycling from there on to hold that temperature goes back to the cooler air unless i raise the temperature so more. When that cooler air i can never get from about waist down to heat up. It always does heat up when that warmer air is blowing, but it doesn't do it everytime the furnace comes on, only when i raise the temp. Hope this makes sense to someone. I have only been told by a professional that my unit is undersized. They said it is 69,000 btu's. My house is 2000 square feet of conditioned space. I use propane and propane alone is costing $300 per month and i am still not comfortable. Thanks so much for your time.
  • 3,361 Answers
69,000 btuh is adequate for a 12-1400 square foot house.
Otherwise, your thermostat simply tells the furnace to cycle on/off.
If it calls for heat and does not come on, the problem is with switches and relays within the furnace.
Your setting the temp higher only causes the other parts to keep trying until they finally light and heat.
This is based on your information saying it will cycle on and blow cool air--not hot air.
You will have several temperature variations from floor to ceiling.
You probably have ceiling vents as well.
You need a technician to verify the rollout switches, fan relay, inducer fan etc. if the furnace is not firing everytime you call for heat.
Posted on Feb 21, 2009
Goodman GS9 blowing air but not getting hot
Does furnace fire up ,if not you have a issue with your furnace and not thermostat
Feb 12, 2018 | Goodman GMS90703BXA Heater
Goodman furnace fan cylcing
The fan switch is set to turn on at approximately 125 degrees and run until the heat exchanger temp drops to around 105 degrees. With age the sensitivity of this switch varies and summer heat can cause the switch to turn on if the outside temp is over 100 degrees. Only the fan is running, not the burner but you can shut off the power to the unit if this is an issue.
Aug 27, 2012 | Heating & Cooling
How to change fan speed on a goodman gmp 100-3 furnace
Usually you can find the control board on the lower part of the furnace. Turn the power off and remove the
doors. This board is usually located directly in front of the blower motor.
On the control board locate the terminals marked heat/cool/park and Park Lets say the Heat Terminal
has a red wire attached to it and you want a higher
Red is uasually low speed, remover the red wire from
heat terminal and exchange it with a wire attached to
a terminal lab eled park. Black is usually high spped
Jan 01, 2010 | Goodman GMS90703BXA Heater
Furnace runs but does not heat up the house to thermostat tempera
Did this problem just start? Or has it been a long term issue? Check for broken ductwork, return air pulling outside air in. Check supply air temps, should be 100-140° or more. And what is the outdoor temp? If it's 0° outside, 74° is doing good. Is the home insulated properly? And there is a small hole behind the t-stat where the control wire comes through the wall. Plug that hole, seal that hole to prevent cold air from fooling the t-stat. The furnace has 3 fan speeds and it may be in low speed. If so it should be in medium speed. I'd suggest a service tech doing this for you unless you are experienced in furnace repair.
Nov 02, 2017 | Goodman Heating & Cooling
Goodman heats but defrosts turns on before desired temp.
Yes. The defrost cycle of a heat pump is actually turning on your airconditioning to heat up the condenser to thaw it out. During this cycle your electric strip heaters "should" be adequate enough to compensate for the a/c being on. At about 30 - 34 degrees outdoor temp there is not enough heat in the air to to adequately heat your home with the heat pump only. Some technitions will use an outdoor thermostat to turn off the heat pump when it is under 34 degrees outside. If you are to cold when its under 34 degrees intall more electric strip heaters.. But if you do this your electric bill may go up significantly.
Welcome to the wonderful world of electric heat pumps (lol).
Good luck.
Mar 29, 2009 | Goodman GMS90703BXA Heater
Goodman Dependable 92 blowign cold air only - no heat
blowing cold air on this furnace usualy caused by high limit trip, or flame roll out. the first one, (high limit) is from insf. air flow. (blocked filter,bad zone damper?
The second,(flame roll out) caused by bad heat exchanger,blocked vent.ect.
Jan 09, 2009 | Heating & Cooling
Furnace Blower cycles on & off
check out the fan switch on the unit and make sure that its the correct one. it should cycloe on @ 120 degrees and cycle off around 100 degrees. Someone may have put in a different one and that is not the approve one.
Dec 23, 2008 | Heating & Cooling
Goodman gmp075-3
I am confident the technician(s) have done this but check anyway.
Gas pressure 4-7 inches W.C for natural, 10 - 11 for Propane.
Air filter clean and unrestricted.
Temperature over supply plenum 140 degrees F.
All registers open and unrestricted.
Vent and intake unrestricted and not blocked.
Condensate hoses free of debris and draining.
OK now lets check to see if the furnace is staying on long enough.When it runs for a heat cycle, is the flame staying on until about 2 minutes prior to achieving the set temperature or is it cycling everyfew seconds and never reaching temp? To check you will need to view the flame through a small viewing port of thru the fins in the front door. Watch them for 10 to 15 minutes.
If they are staying on a long time, we will need to see if the room blower is working properly. If they are going out quickly and or cycling. Get the technician on the pone to talk it over. It could be a safety sensor.
If the blower stays on and the burners are on as well, you have a door open somewhere. Just kidding. Remove the thermostst documenting which wires go where. Take the white wire and cross it with the red wire. This will (or should) turn on the furnace. Clamp them together untill the either the house gets warm or you are confident it is not going to reach temperature. If it did get close to the temperature you wanted, it is a thermostat issue. If not, you got me!
And they say we have an easy job! Get beck to us with your results.
Jan 22, 2008 | Goodman GMS90703BXA Heater
Goodman GMP100-5 Rev Furnace Manual
I don't know where you are located, but there is a Goodman distributor in Sacramento, CA. Also in Ontario CA. They are a distributor so they may be able to help you or tell where to find someone who will help. Goodman is also known as GMC or Janitrol.
Jan 07, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
285 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others