Voltas 5.5 tr, R22 gas, 3phase
SOURCE: Suction line ices up from the suction line
Is there a base valve or valve by the schrader?
It sounds like you have a restriction where the line starts to freeze up,like maybe there's a valve there thats not completely open, if not then you could be low on refrigerant or your metering device isn't opening completely.
SOURCE: 1.5T Voltas Vetris window AC. Ice formation
I think the more likely problem is that the unit is slightly short of gas\ refrigerant, which is a common cause of icing up evaporator coils and this sound you describe. First check that the air filter is clean. Another cause could be the defrost sensor is faulty, but I would think not. Some ice isn't actually a bad thing, but quite common as long as it doesn't form over too much of the coil, or get too thick.
SOURCE: when i was fixed a problem in central ac trane i
You are still low on freon.
Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
SOURCE: AIR CONDITIONER IS NOT COOLING,
there is probably a leak in the systems somewhere, it needs to be inspected for a leak and charged with R-22 for proper cooling.
There is a stop leak for air conditioning systems available to licensed technicians to buy, might work if the leak is very small.
