Question about Goodman GMS90703BXA Heater
Furnace shut off after 3 time flame from pilot
Hi a have problem with my furnace.Thermostat call for heat ignition start in time and flame com out for about 5-10 sec then off,ignition com back the same thing for 3 time and my furnace shut off.please help me .THE FLAME COME OUT FROM PILOT THREE TIME AND SHUT OFF FURNACE
  • 56 Answers
Sounds like you may have a weak or bad flame sensor. If the circuit board does not sense a good flame it will not light the burners. Also if your furnace is 5 yrs or newer it should give you a fault on circuit board in the form of a blinking or a code itself.
Posted on Feb 16, 2009
How do I light pilot light?
There should not be a pilot on a direct vent furnace. When you turn up the thermostat for heat the 1st thing to happen is a venter motor should start, it should vent for approximately 45 seconds, the air switch will verify a vacuum in the burner box, then a spark igniter should start clicking to start the pilot, then the flame rod will verify the pilot, the igniter will stop clicking, and the main burner will ignite and remain on until the thermostat has satisfied the set point. These guideline steps must be satisfied before the controller advances to the next step. The 1st step is the venter motor running, sometimes the motor will stick over the summer months, spin it manually to unstick it. PS, nothing runs if the fan door cover is open, as that shuts down the power to the whole furnace.
Oct 02, 2015 | Coleman Gas Fired Mobile Home Furnace,...
Why does it start, then shut down followed by 3 clicks?
  • Thermostat calls for heat
  • Venter motor starts
  • Air switch verifies vacuum
  • Igniter sparks, or glows - depending on furnace
  • Flame starts in burner
  • Flame rod senses flame
  • Burner continues to burn until thermostat stops calling for heat
By your description, I would polish your flame rod, it will be a metal rod that is insulated from the bracket that is screwed to the furnace case and it will have a single wire attached to flame rod,
Sep 29, 2015 | Intertherm 56000 Btu Gas Furnace
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Thermostat calls and from time to time won't ignite
I would first look at any wire connections both at the furnace and the thermostat. Then I would replace the thermostat. Check the units control board when it does not start for an error code. There should be a small viewing port to look into the furnace cabinet to see the control board.
Feb 12, 2010 | Goodman Heating & Cooling
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
Jan 26, 2010 | Goodman Heating & Cooling
My furnace will not shut off on auto. the fan will not run when switched to on. what should I check?
Some new furnaces have a feature that when it has an issue, it starts the room air blower until you reset the thermostat or kill power to the furnace. Not knowing what you have for a system I can offer you only how a furnace works and what you could look for "generically".
Jan 18, 2010 | Honeywell Heating & Cooling
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
Nov 23, 2009 | Heating & Cooling
FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Amana furnace main burner intermitent
Sounds like dirty flame sensor. You can either clean it orreplace it.
Apr 21, 2009 | Honeywell Power Humidifier: Furnace...
1986 Weathermaker SX 150 series, model S85X060-CC-1
There are 4 -steps for full run time to kick in a furnace.. step-1, inducer fan runs & prove thru the air tube which closes a switch and tell the circuit board to go to step-2, the igniter lights the pilot & prove its lit by heating the thermocouple, which tells the circuit board to go to step-3, opens the gas valve to dump gas in, which will light from the pilot light, and prove by a flame sensor metal stick on the last burner , which heats up and tell the circuit board Saying, ok , I've got flame.. step-4. when the box heats up, it closes a switch and turn on the main fan...! (Some gas-valves has a brain -or circuit board on top of them and are real sensetive to moisture..)
Sep 05, 2008 | Heating & Cooling
Goodman GMS90703BXA Heater Logo
289 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others