Question about Ruud UBHC Air Conditioner
One of Rudd outside units fan does not come on
We have two units. One of the the fan in the outside unit does not come on. Help! Winter storm coming and my downstairs is freezing!
  • 10 more comments
  • frank_nancyb Feb 13, 2009
    The particular outside unit simply doesn't work. If the unit is low on freon, I understand there is a automatic shut off switch to unit'? Could this be my problem? We've had to charge the system a couple of times in the past.
    We hit the reset button and the unit started up. Do you think the issue is low freon?
    I hope this will be a "fix ya"! We will charge the system and see what happens. Thanks! This is the greatest site!!
    The unit began running. We turned it off while still in the heat mode. I connected freon guages. The low side read 136 and the high side or large side ran 165. This doesn't sound normal. I thought it would be a bigger differentiation that that? Any suggestions?
    Okay, I am letting the system run for 15-20 minutes at 70 degrees, hoping if there were any irregularities that they would level out. I will turn the system off, reconnect the guages, turn the system on and get new readings and advise. Does this sound like the appropriate next step?
    Do I wash from the inside out or just on the outside?
    Will do and will be back in touch. I'm sure you'd like to hear the outcome.
    After washing off coils, turned it off, hooked up the gauges. The high side or large line measures 125, the low side or small line measures 145. What do you suggest I do next?
    And these readings are for the Heat Mode, not A/C mode? Also, what do you mean by "correct settings" on the gauges? They zero out when disconnected.
    Low side: 136
    High side (large side): 165
    Great! Thank you so-o-o much! For future reference, what should the settings be for heat mode? You certainly are the "guru" of HVAC! Any way we can commend you to your upline or supervisor? Thanks for hanging in there with us. Have a great weekend!
    Frank and Nancy
    Awesome site! I will recommend it to all my friends!!! You guys are the greatest!
    President:
  • 1,902 Answers
Check to make sure that your contacts are ok and the fuses on the main breaker disconnect are ok. If those are good then replace the fan motor
Posted on Feb 13, 2009
  • 12 more comments
  • Jeremy Reddick
    Jeremy Reddick Feb 13, 2009
    Do you still need more about this problem?
  • Jeremy Reddick
    Yes the automatic shutoff switch could be the problem. Just a piece of advice though. If you are slowly losing freon. The company should charge the line with nitrogen and check for leaks. Your unit should not be losing freon at all. If it gets to low on freon by reseting the switch will not work until it is full again
  • Jeremy Reddick
    Yes, that is the only reason that the switch will go off. The problem is now though that if you continue to just do resets, you are going to ruin the compressor since it is running on low freon. You should really have the system charged and checked VERY well for leaks and the leaks to be repaired. If not after time you are just going to ruin your compressor anyways. Just a little extra info for you to save you from spending really big money.
  • Jeremy Reddick
    You are welcome come back anytime you have a questions about anything. A lot of techs on here that specialize in a variety of different areas. Everything from cars to household aplliances, even on how to start a garden. So have a great weekend, and I hope you stay warm. Take care
  • Jeremy Reddick
    Actually that sounds WAY to high. You should be high side 160 and low side 70 to 75. It seems that you have to much freon in the system. This will also cause the switch to pop
  • Jeremy Reddick
    You may want to shut it down. Take a garden hose and clean the coil out very well using a blast of water moving up and down. Try not to cross the fins due to the fact that you will cause them to bend and create blockage. Try this before the storm hits if you can
  • Jeremy Reddick
    If you are going to shut it down then go ahead and clean out the coils. Then put gauges back on a fire it back up. If the coils get blocked or dirty the system cannot breathe. Like a car radiiator. If it gets blocked it will cause the car to over heat. This is how your system breathes
  • Jeremy Reddick
    Just spray it from the outside of the unit
  • Jeremy Reddick
    Yes please let me know what is happening or going on. I am certified tech for 11 years so I do know this just harder to do when on the computer then in person
  • Jeremy Reddick
    Let it run for about 15 minutes with the gauges on and check it again. Make sure gauges are on the correct settings. But it is getting better slowing. Let the freon circulate a little bit longer. Pressure is still to high. And to recount my other post on the gauge setting. The high side needs to be between 75 to 90 and the low side to be at 125-160
  • Jeremy Reddick
    Yes those readings are for heat mode. And the meaning with your gauges being on the correct settings meant that they were set to zero everytime they where plugged in. What is the reading on the system now?
  • Jeremy Reddick
    Ok you are good to go. I was telling you reading for cooling not heating. Sorry backwards today. Your settings are good. Why you tripped the switch is still unknown. did you have a power surge or failure anytime within the last 48 hours? Maybe while the system was running?
  • Jeremy Reddick
    Low side: 125 - 145
    High side 155-185
    There is not a way to contact my supervisor. We are on here providing free tech support for different things or at low rate. We do not make service calls only coverage over the internet. You and your family have a great and safe weekend. And you are welcome for all your help and support. Take care
  • Jeremy Reddick
    Thank you you and your wife take care and feel free to come back at anytime
Rudd A/C. Why does the fan run constantly and the outside unit doesn't turn on?
could be a outside power board
could be that the temperature setting equals the atmospheric temperature and not turning the outside unit on as it is not necessary
May 29, 2015 | Heating & Cooling
I have a Rudd Achiever 10 . The unit was working yesterday morning, it stopped in the afternoon , and is still not working. The fan in the unit in the basement is working fine. Do you think it could just...
you will need to check you condenser unit(the outside unit) here is a website that may help,Tim:
http://www.air-conditioning-and-refrigeration-guide.com/air-conditioning-troubleshooting.html
May 30, 2011 | Ruud UBHC Air Conditioner
My goodman central air unit quit working after a storm. The circuit breaker is not blown. The furnace fan kicks on when ac is turned on at the thermostat but unit outside does not operate. Is there an...
1 posible cause.the thermostat supplies 24 volts to the outside unit to control the contactor if you hear a ligth huming on the outside unit this is the being activated. if this is the case then
check to see if any ants are in or around the unit see video, they will usually climb to dry areas before during or after a storm and for some reason they like the contactor if this is the case cut all power to the unit and clean contactor spray the area around the unit with an insecticide ( not the contactor) replace cover and test unit. Best of Luck. raypena_4.jpg
May 30, 2011 | Goodman Heating & Cooling
Rudd Achiever series model RQNJ-AO42JK 000 mfg
Turn the thermostat as low as it will go and have someone stand out side, they should here the condensor fan and compressor come on at the same time. They are two distinctive sounds so you should
be able to tell if the compressor is running.
If nothing happens and you are skilled with electrical
you can turn power off and remove the electrical
cover to the outside unit. Restore power and carefully
push in the contactor, if the fan and compressor
starts you have a thermostat or low voltage problem.
If just the outdoor fan runs on any attempt, more than likely you need a new capacitor.
Jun 18, 2010 | Ruud Central System Air Conditioner
Rudd heatpump compressor runs outside fan dose
I don't think the fan on it' own crates the problem. Could you find out what should be and what actually is the flow through it. If you needed <!-- MOJAIZBA.COM LINK CODE START --> <a href="http://mojaizba.com/convert-units-of-flow" title="Flow units converter page on mojaizba.com - Convert flow units online. Use the calculator for making conversions from one flow unit measure into another flow-volume amount between; acre foot per: acre-ft/day, hour acre-ft/hr, year acre-ft/yr, bar/day barrel Oil per day, hour bar/hr, minute bar/min, second bar/sec flow, cubic centimeter per day cm3 / day, hour cu cm/h, minute cm3/min, second cm3/sec flow, cubic foot feet per day ft3/d, hour ft3 / hr, minute ft3/min, second cuft/sec, cubic inch per day in3/day, hour in3 / hr, cubic inch per minute cu.in/min, in3/sec, cubed meter per day m3/day, hour cu m/h, minute m3/min, second m3 / sec, cubic yard per day yd3/day, hour cu yd / h, yd3 / min, cu-yd/sec, gallon US gal/day, gal/h, gal/min, gal/s, gallon UK per day gal/d, gal/hr, gal/minute, gal/sec, hundred cubic feet foot per day 100 cu-ft/day, 100-ft3/hr, hundred cubic foot per minute flow 100ft3/min, 100 cubed ft/sec, kilogram per day - Petrol kg/day, hour Gasoline kg/h, kg/min, kg/s, liter per day l/day, l/hr, l/min, l/sec, milliliter per day ml/d, ml/h, ml/min, ml/sec flow, ounce US per day oz/d, oz/h, oz/min, oz/s, ounce UK per day oz/day, oz/hr, ounces/min, oz/sec, pound per day - Petrol flow lb/day, Gasoline lb/hr, lb/min, lb/sec. USA – Imperial UK and Metric SI system units of flow. Buy the JavaScript JS and HTML code for this web flow converter tool application for your website." target="_blank">flow units converter</a> <!-- MOJAIZBA.COM LINK CODE END --> for a unit you'are comfortable with here is one we use if it's necessary. Let me know that...
Mar 21, 2010 | Ruud Heating & Cooling
Air not circulating through vents
is the unit running outside? did you check the breaker? Ruud units often times will have a reset bitton on the outside unit to the left of where the freon lines connect. It is a high pressure switch if it comes on when reset make sure the coil is clean and the fan runs(outside)
Sep 20, 2009 | Ruud UBHC Air Conditioner
Has not ever run properly
is it a heat pump? I would be suspect of the line voltage transformer have 24v. if transformer is not matched to line voltage you can have erratic problems their is an under lying problem. that is being missed find a good contractor . Tom
Jun 17, 2009 | Ruud UBHC Air Conditioner
Ice build up out side hitting fan
pop out drain plug heat up pan with heat gun to melt ice
Nov 24, 2008 | GE Zoneline AZ38H12DAD Split System Air...
RUDD A/C not running, only fan
ok it unit is a central I'm suspecting a voltage transformer is defective you see these units need 24v to turn on certain components but if your air handler turns on, your getting 24v to the fan relay, the problem would be elsewhere. if your handy with a volt meter open the thermostat(if applicable) put the meter on ac volts and measure to see if there's 24v between the R and Y terminals
if so your cooling contactor is defective. (If you get 24 v and unit outside dosen't turn on) if there isn't some fuse on the air handler control board blew out.
you can e-mail me @ hvac.tech7872pr@gmail.com if you need more info
Jun 16, 2008 | Ruud Heating & Cooling
Non-working outside unit
If your unit is blowing heat inside and it's not a heat pump. It will be most likely electric heat in your case.
Sounds like you have a split unit meaning the condenser is outside and the cooling and the heat features are inside or under your home.If your Rudd is a heat-pump the outside unit will cycle/blow cold air outside in winter and hot air will cycle/blow outside during the summer season. Now, if for some reason the heat  is not coming on inside the house, would be the only reason that you would need to be concerned. Being a heat relay or breaker of could cause that problem. Hope this helps you, Sea Breeze