Question about Coleman Mach III Air Conditioner
No cold air
Hi FixYa
I recently purchased a caravan with a Coleman "Mach EL RV Series" airconditioner. The unit on top of the van has written on it "Mini Mach".
When I turn it on, it seems to fire up OK, but does not produce any cold air.
The unit was made in the USA in 1982. Heats fine, blows fine - just doesn't cool. I left it going the other day for an hour or so but to no effect.
Any thoughts would be appreciated.
  • Rick Sillett Feb 09, 2009
    Thanks rockitman.
    No doubt this is s FixYa solution except that I haven't got a clue what you are talking about so can't be totally sure of that. From what I can make out however, sounds like I need a guru to look at it for me.
    Thanks again
    Rick
    President:
  • 2,559 Answers
  1. The filter could be dirty This is the most probable cause and, of course, the easiest to check and correct.
  2. The evaporator coil face could be coated with lint,dirt, etc.Dirt or lint on the coil will restrict the flow of air through the coil and the unit must be removed from the recreational vehicle and the soil must be thoroughly cleaned with strong detergent (Coil X,Calclean, etc.) and water. Be sure to protect the fan motor and electrical controls during cleaning by covering them with polyethylene sheet. After the system is cleaned, allow it to thoroughly dry for several hours (before turning it on) to prevent electrical shorts.Before system is put back into operation, be sure the filter is properly installed to prevent recurrence of dirty coil.
  3. No compressor (Does not try to start).The compressor does not run and it does not hum.
    1.The selector switch may be open.
    2. Thermostat may be open.
    3. Overload switch may be open.
    4. Compressor winding may be open.
  4. Selector Switch
  5. Thermostat
  6. Low Voltage
  7. Overload
  8. Compressor
  9. Wiring (Mis-wired)
  10. PTCR or Potential Relay
  11. Start Capacitor
  12. Run Capacitor
To check the selector switch, remove wires from the terminals
and rotate the switch to the proper position and read
continuity as follows:
Terminals Switch Position
L-1-3 Lo Heat
L-1 Lo Fan
L-2 Hi Fan
L-1-4 Lo Cool
L-2-4 Hi Cool
Compressor Motor
The compressor motor is located inside the hermetic
compressor housing and therefore not accessible for service or
visual observation in the field. However, the motor winding
condition can be analyzed by using an ohm meter. Be sure to
remove all the leads from the compressor terminals before
making this check.
1) If the resistance between any two terminals is 0
ohms, the motor windings are shorted.
2) If the resistance between any terminal and the
compressor housing is anything but infinity, the
winding is grounded.
3) If the resistance between any two terminals is
infinity, the winding is open.
On a good compressor, the highest resistance will be between
the R (run) and S (start) terminals. The lowest resistance will
be between the C (common) and R (run) terminals. The
intermediate resistance will be between the C (common) and
S (start) terminals. Notice that compressors have the
identification of the terminals marked on either the terminal
cover or on the compressor housing.
Capacitor Check
There are several capacitor test devices available. The ohm
meter is one of them. The ohm meter cannot verify a
capacitors MFD (microfarrad) value. However, the following
procedures will show you how to use an ohm meter to
determine if the capacitor is good, open, shorted or grounded.
Before testing any capacitor, always perform the following
procedure:
* This test must be done with a analog type meter.
a) Disconnect all electrical power to the air conditioner.
b) Discharge the capacitor with a 20,000 ohm (approx.
3 watt) resistor or larger.
c) You may discharge capacitors with a standard volt
meter if you use a scale over 500 volts and touch the
leads (one lead to each side of the capacitor). The
volt meter will discharge the capacitor.
d) Identify and disconnect the wiring from the
capacitor.
e) Set and zero the ohm meter on the “highest” scale.
When testing for a good, open or shorted capacitor,
perform the following checks: Place the ohm meter
leads across the capacitor terminals (one lead on
each terminal) and perform a continuity test. Then
observe the action of the meter needle or indicator.
Reverse the leads and test again. The result should
be the same. Note: If the capacitor had not been
properly discharged, a false reading could be
indicated on the first test. Always test several times
(reversing the leads with each test). This will verify
the capacitors condition.
Good Capacitor
If the capacitor is good, the indicator will move from infinity
(the left side), towards zero ohms and slowly return back to
infinity. Reverse the leads and test again. The result should
be the same.
Start Capacitor
Most models use a start capacitor and a start relay to give the
compressor high starting torque. The compressor will,
therefore, start against normal pressure difference (head
pressure minus suction pressure) even when shut down for a
short period of time. The start relay will disconnect the start
capacitor when the motor reaches approximately 75%
running speed.
Start (Potential) Relay
The start relay consists of –
1) Normally closed contacts internally between
terminals #1 and #2 which switch in the start
capacitor in parallel to the run capacitor during shut
down and then switch out the start capacitor when
the motor reaches approximately 75% normal
running speed.
2) A high voltage coil internally between terminals #5
and #2 to actuate the contacts. The coil is too weak
on line voltage to actuate the contacts, but it is
connected in series with the start winding and it gets
the generated voltage of the start winding portion of
the compressor motor. This generated voltage is
much higher than line voltage and varies with the
speed of the motor. Therefore, since the relay is
designed to open the contacts at 75% of normal
running voltage (measured between terminals #5 and
#2), the contacts will open (thus disconnect the start
capacitor) at approximately 75% of normal running
speed.
(B) Positive Temperature Coefficient Resistor
(Commonly Known As PTCR Start
Device)
The resistor acts like a potential relay in that it takes the start
capacitor out of the start circuit, but uses resistance of
electrical flow (back EMF from compressor) instead of
opening a set of contacts. The service person should be careful
handling the resistors. They will be hot during operation (up
to 160 degrees F). The air conditioner needs to be off for 3-5
minutes during cycle time and when servicing to let the
resistor cool down.
That covers everthing.
Please rate this a fixya
Posted on Feb 09, 2009
  • Randy Hough
    Randy Hough Feb 09, 2009
    Some of this can be check fairly easy.
    1. Check the coils and see if they are clean
    2. check the filter.
    3. listen and see if you can hear the compressor try to start.
    If all this checks out,post back with your findings and we will walk you through it if you want.
    Thank you.
What is the BTU / size of my Coleman Mach model number 8333B6664; serial # 120219962
Most likely it is a 13500 BTU unit. The recommended replacement is the Coleman Mach 3 Plus 48203C966 which has a nominal 13500 BTU cooling capacity.
I hope this helps.
Jul 21, 2014 | Coleman Heating & Cooling
Btu of coleman 7830-901
That should be a 30,000 Btu unit. Its been a while since I worked on them. The 78 is the series or model, the 30 is the capacity or btu's and the 901 indicates it is a Copeland compressor.
Jun 09, 2014 | Coleman Air Conditioner Shroud Rv Roof Top...
How to do a freon recharge on roof top rv airconditioner
there are no access ports to add freon you would have to put a line tap valve on it.
May 10, 2014 | Coleman Mach 15 Air Conditioner
Coleman mach 6759C707 quit on us, only the fan is running. What do i need to replace? The compressor? WHat part number?
my coleman 7330 fan only runs when ac unit is on and then sometimes shuts off and then restarts
Aug 18, 2011 | Coleman Mach III Air Conditioner
Hello, I've recently purchased an old camper (84) with a coleman mach series roof unit. My question is I need a replacement shell (hard cover plastic body) for on top of the roof. It was damaged from a...
You can purchase one from any RV dealer usually, and they may even have some used ones cheap in their spare parts dept. Make sure if it's used, that it's not to brittle from the sun, otherwise you'll be replacing again.
Jul 31, 2010 | Coleman Mach 15 Air Conditioner
I need a motot for a coleman mach el
COLEMAN R.V. AIR CONDITIONER SERVICE AND REPAIR QUESTIONS
COLEMAN R.V. PRODUCTS
GO TO rvcomfort.com
Click on RVP (RV PRODUCTS)
Click on type of AC, if you can’t find the information you want there,
then click on contact us on the Green Bar.
You can get Service Support or Email address and Phone numbers.
Sep 28, 2009 | Dometic Rooftop RV Air Conditioner
AC motor not starting
You do not need a new motor, more than likely the contacts are going bad. You can clean these or replace them if you are mechanically inclined.
Jun 25, 2009 | Heating & Cooling
Coleman mach wire schematics?
GO TO
www.rvcomfort.com
Aug 04, 2008 | Coleman Mach 15 Air Conditioner
Wiring Diagram Coleman Electra Heat Mach EL
I need the motor for a mach EL air conditioner. I can not get a model number of the unit or a number off of the motor. Can someone help me. Its about a 1980 built unit.
Mar 29, 2008 | Dometic Rooftop RV Air Conditioner
Coleman Mach III Air Conditioner Logo
675 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
paulcarew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others