Question about Goodman GDS80904BNA Open Flame Heater
Goodman gmp125-5 burners ignite, then shut off after about 5 sec
Burners ignite then shut off after about 5 seconds, it repeats this process several times then shuts down completely.
    President:
  • 1,902 Answers
One of two problems are happening here, your flame sensor is bad, your thermo pile or thermo couple is bad, or last is that the cap on the flue is blocking the exhaust from escaping
Posted on Feb 09, 2009
My burners turn on for 2 minutes then shut down for 30 seconds, then turn on again while repeating this process.
Have you checked the air filter? Also make sure the room air blower turns on to distribute the heat throughout the house.
Jan 23, 2011 | Goodman GDS80703ANA Open Flame Mid-Size...
Hi Im having a problem with my furnace. Igniter lights up blower kicks in it ignites for about 10 sec then goes out and blower blows cold air It repeats this process over and over It is now 50 degrees f in...
look for the flame sensor , its a small metal rod in front of one the burners you need to sand it with some sandpaper and it should stay lit. attached is a pic of what it looks like.
Dec 13, 2010 | Goodman Heating & Cooling
Inductor blower comes on and runs then the ignitor glows flame comes up and burns for approx. 10-15 sec then goes out then fan comes on. Model number is PBKMLB12N0B0F I believe this is a goodman furnace.
I cleaned the sensor that was at the the right further most burner on my Goodman and it worked. got the answer to my problem here at fixya. My burner flame only lasted 5 secs before it shut off. Thanks to all who took the time to send me a response.
Nov 13, 2010 | Goodman Heating & Cooling
Burner ignites and goes out (Goodman Gas-fired furnace)
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Dec 24, 2009 | Goodman GMS90703BXA Heater
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
Goodman furnace seems to be cycling too often. Burner not staying on long enough to put warm air into system. Burner quits after a few seconds then repeats.
dIf the burners are only staying on for about 5 seconds, you proably hav e a dirty flame sensor. Watch the burners light, the glow plug will light one end of the burners, in front of the last burner to light the will be a small thin rod, this rod must sense the flame or the gas will be shut down. Take a piece of steel wool and gently cleqan the rod.
Oct 11, 2009 | Goodman GDS80904BNA Open Flame Heater
Furnace tries to ignite
thi is either a sensor or the control module
Dec 07, 2008 | Goodman Heating & Cooling
My goodman gmt090-4 shuts off about 10 sec. after burners ignite
Check the pressure sensor. I tapped on mine a few times, removed the hose and checked it for blockage and replaced. It has been working fine since. I do have a new sensor on order.
Oct 04, 2008 | Goodman GMS90703BXA Heater
GMPN 120-5 FURNACE
If you want some help on this I will need some more info. Does the unit shut off completely? does the fan run after the burner shut off, or is off simultaneously? do you have a digital thermostat or the old type?
Dec 01, 2007 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
281 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others