Question about Cooper Wiring Devices Three Way Grounded Switch, 15 Amp
Need UK wiring diagram for a 2 amp torpedo switch ( 3 terminal)
    Problem Solver:
  • 21 Answers
Old school hollywood baseball old school hollywood baseball old school hollywood baseball old school hollywood baseball
Posted on Feb 10, 2009
I need a wiring diagram for an intermatic timer model et70215c
Add a comment and say what voltage you are working with and what you are controlling with timer. Example wiring:
http://waterheatertimer.org/images/Intermatic-et70215cr-wiring-900.jpg
ET70215C timer is a 2-channel timer that can be wired MANY different ways, to control multiple voltages in different ways.
Each channel can be programmed separately to control 2 different loads with different schedules for each load.
Clock terminals are 1 and 2, and default clock voltage is 120Volts, but can be set for 208, 240 or 277Volts.
The switching terminals 3 4 5 6 7 8 are 'dry.' Max load rating is 20 amps per terminal
Dry terminals receive no power when voltage is applied to clock terminals 1 and 2.
This lets you to have 120Volt clock, but control 240Volt circuit with one of the channels, and 24volt with other channel.
Or you can jumper from the clock terminals and put power to terminals 3 and 6 as shown in illustration above.
The timer ALSO has NO and NC terminals that reverse the circuit each time the program turns the switch on-and-off. So when timer program is OFF then power travels from terminal 3 to terminal 5. When program is ON, power travels from terminal 3 to terminal 4.
Oct 01, 2011 | Intermatic ET70215C Electronic Energy...
The Casablanca 88U33M Scandia Ceiling Fan only has three wires, a black, a white, and a green wire (ground). How do you wire the fan and light on seperate switches?
If you want to control both the light and the fan using 3-ways, then just wire 2 sets of the 3-way circuits. For this you need two sets of 3-wire between the switches, and one 3-wire cable from the switch location to the fan/light box.
At box #1 (a 2 gang box), you will run a power cable (marked cable #1) into it. From there you run 2 sets of 3-wire cables (identified as cable #2 & cable #3) to the other switch location, which will also be a 2-gang box (box #2).
Also from box #1, you will run a 3-wire cable (cable #4) to the fan/light box (box #3).
Hook up is as follows:
Box #3: connect black of cable #4 to black (fan), connect red of cable #4 to blue (light), connect white of cable #4 to white (fan/light), and connect the bare to the green.
Box #2: Connect white of cable #2 to identified terminal on 1st 3-way switch (#3). Connect red & black of cable #2 to the remaining screws of 3-way switch #3. Next connect white of cable #3 to identified terminal of 2nd 3-way switch (#4), and connect black and red to remaining screws. Tie all grounds together and terminate to both switches.
At box #1, connect black from cable #1 to whites in cables #2 & #3, using a wirenut. Connect white in cable #1 to white in cable #4. Connect black and red in cable #2 to 3rd 3-way switch (#1) and connect black and red in cable #3 to 4th 3-way switch (#2). Connect black in cable #4 to identified terminal of 3-way switch #1, and connect red in cable #4 to identified terminal on 3-way switch #2. Tie all grounds together and to the switches
Jul 04, 2011 | Casablanca Fan (88U33M) Ceiling
Need wiring diagram for T104M 208-277v Mech. Time Time Switch
Here is the basic instructions:
http://www.intermatic.com/~/media/files/intermatic/products/instructions/timers/t104%20-%20english.ashx
Below is a larger and better diagram of a 240V connection Terminal connections are White to White on 3 & 4 Black to Black on 1 & 2:
http://waterheatertimer.org/images/T-104-control-240V-Load4-35.jpg
More info: http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html
I am assuming you have the 240 VAC clock motor so the clock timer motor wires are connected to terminals 1 and 3.
If you only have the 120 VAC clock motor the wires will be connected across terminals 1 and 2.
Thanks for choosing FixYa,
Kelly
Jun 27, 2011 | Intermatic T104 24h 208-277v Mechanical...
I bought a Leviton 1201-PLC 15 Amp, 120 Volt, Toggle Pilot Light, Illuminated ON to replace a traditional 3 way switch (without a pilot). I replaced it by connecting the existing wires to the new switch in...
Your screw terminals are 2-brass and 1-dark.
Dark screw is considered 'common'
http://waterheatertimer.org/ST01C-program.html#3-way
Leviton shows a 3-way 1203-2, but not 1201
Wiring diagram indicates that pilot light is ON whenever switch has power.
http://www.leviton.com/OA_HTML/ibeCCtpItmDspRte.jsp?item=2681§ion=10046&minisite=10026
Check your instruction sheet that pilot light is supposed to turn on-off with Load.
I don't think it is, without additional terminal on switch for neutral wire.
And then it would only work on switch located closest to light.
You can wire this type of thing separately.
Buy ordinary pilot light or indicator light from WW Grainger.
Look at diagram on following image:
http://waterheatertimer.org/images/3-way-circuit-with-pilot-indicator.jpg
Upvote the help.
And take advantage of fixya expert assistance live.
For a price, expert works with you while you work on circuit or any do-it-yourself project.
Fixya is always less expensive than a service call.
May 08, 2011 | Leviton Snap On Mount Switch Pilot Light -...
I just bought an older electronic Intermatic timer at a yard sale. Model ET7215C. Timer power can be 120/240/277. There are 5 terminals for this, numbered 1-5. Looks like a variable tap power transformer....
I think you have the ET70215C SPDT
http://www.intermatic.com/products/timers/electronic%20time%20switches/next%20generation%20time%20switches.aspx
If this is not your timer, then add a comment.
Manual for ET70215C (same manual is for other models too)
http://www.intermatic.com/~/media/files/intermatic/products/instructions/timers/et70215c%20-%20english.ashx
Just as you figured, timer has selectable voltage.
Page 28 shows wiring diagrams and jumper settings:
Timer comes with a jumper, and then you select with voltage by installing jumper
Sample wiring diagram below shows 120Volts:
ET70125 appears to have 8 terminals.
Some models have 5 terminals.
There are many ways to wire this timer. Off hand I can think of 10 different ways.
Add a comment if you need help with a specific project.
In any case, the clock terminals are 1 and 2.
To put voltage to the timer switches in the simplest wiring options, is to put a jumper wire from terminal 2 to 3
If you are using 240-277 voltage with two hot wires, you still need to jumper from clock terminals to switch terminals. For example one jumper wire from terminal 2 to terminal 3 & then second jumper wire from terminal 1 to terminal 6
Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, fixya expert speaks with you over phone while you work on timer.
Jan 08, 2011 | Intermatic Hardware & Accessories
I have a Et 70115C Intermatic Timer, I want to install it on my Hot Water Heater, I have connected the 2 110V leads from my breaker to Terminals 1 & 2 and connected the two leads from the hot water...
A) 5 terminal ET70115C.
Voltage selector set to 240.
B) BUT you say you have 120Volts from breaker >>> confusing, so I'm proceeding on basis that you meant to say 240V from breaker.
Add a comment at any time.
C) Review timer:
5-terminal ET70115 timer has NO and NC terminals
NC is normally closed >> this terminal has power when timer is OFF
NO is normally open >> this terminals has power when timer turns ON
For water heater, you want NO terminal 4 so water heater turns ON when timer turns ON
D) Wire for 240Volt water heater
Two hot wires from breaker connect to terminals 1 and 2. This powers timer clock.
Jumper wire connects between terminal 2 to terminal 3. This sends power to the switch circuit.
Wires to water heater connect to terminals 1 and 4
E) 5-terminal timer turns off 1 hot wire to 240V water heater.
Turning off 1 hot wire will stop 240V circuit from working; Water heater thermostats also turn off one hot wire.
240V water heater has black and red wire.
Wire from terminal 4 should connect to Black wire on water heater.
Diagram shows two wires on terminal 1
Two wires on terminal 2
One jumper wire on terminal 3
One wire on terminal 4
Zero wires on terminal 5
Dec 03, 2010 | Intermatic ET70115C Electronic Energy...
Triing to install intermatic t103 please help. Source is 3 wire 110v want to run 3 blower 110v 9.5 amps each off the t103 timer. Don't have 220v in house just 110v. I need a very simple wiring diagram I...
T103 has 120Volt clock motor, so we can wire this timer.
T103 timer is rated for 30 amps and 2horsepower and your blowers use 28 amps.
So we're getting close to max on the timer. Hopefully blowers won't all be started at one time since motors draw maximum amperage when they start.
However, you need 30 amp breaker and orange 10 gauge wire for that much amperage >> unless only one blower is turned ON at any given time.
Always match wire size, amperage of breaker and amperage of Load or it will trip the breaker.
If you put 30 amp breaker on size 10 wire it is good. But 30 amp breaker on smaller size 14 or 12 gauge wire is fire hazard.
http://waterheatertimer.org/Color-codewire.html
Add a comment at any time, and I will respond
Look at the basics:
You have 2 cables.
One cable comes from breaker box.
Other cable goes to three 120V plugs (120V is same as 110V).
Each cable has black-wire, white-wire and bare-copper-ground-wire.
How to wire the timer.
Timer has 5 terminals: A 1 2 3 4
A) Cable from breaker box:
White wire from breaker connects to terminal A
Black-wire from breaker connects to terminal 1
B) Cable going to 3 plugs
Black wire to plugs connects to terminal 2
White wire to plugs connects to terminal A
Ground wires connect to green ground screw.
Terminals 3 and 4 are not used in this case.
Here is a wiring diagram that shows 120Volt from breaker box and 120Volt going to Load
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html#T103
Nov 27, 2010 | Intermatic T103 Indoor 120-Volt 40-amp...
Need diagram showing a/c power and switched termanels
You posted under EH40 Intermatic timer.
The EH40 has a 240V clock
http://waterheatertimer.org/How-to-wire-EH40-hot-water-heater-timer.html
The terminals are numbered 1 2 3 4 5 6
The 240Volt clock is terminal 1 and 2
The first HOT wire from breaker connects to terminal 1 and 3
The second Hot wire from breaker connects to terminals 2 and 5
The wires to Load connect to terminals 4 and 6
If you need more help, add a comment and I will help
Nov 01, 2010 | Intermatic EH40 Energy Controls -...
Low/High Switch wiring for Hayward Superpump
I do not read anywhere that you have a 230V DPDT switch which you will need in order to select the high or low speed. You will have 6 terminalas on the switch. Line connections usually go to the middle set. Put put sides of one pole to the common terminal and put one of the other posts to the hi and the other to the low terminal. I prefer to use am on-off-on switch so the switch in the middle turns off the pump. Flip it one way for hi and the other for low. If you post your stock number from the two-speed motor I could give you a more accurate diagram if you need it. Generally, 1 is common, 2 hi and 3/4 low.
Apr 26, 2010 | Pool & Spa
Lakewood heater 7101 schematic
The power cord goes the switch terminal 1 and 3.
Terminal 2 must be the opposite of terminal 1, such that when switched on, 1 & 2 connects. Terminal 4 must be the opposite of terminal 3, such that 3 & 4 connects.
Under this setup, you may connect red to terminal 2
and black to terminal 4.
Be sure of the 1 & 2 pair, as well as the 3 & 4 pair.
then, connect the red and black wires.
Hope this will help you.
Jan 06, 2010 | Lakewood Oil-Filled Electric Radiator...
Cooper Wiring Devices Three Way Grounded Switch, 15 Amp Logo
1,403 people viewed this question
Top Cooper Wiring Devices Electrical Supplies Experts
ken skalski
Jim Y
Jim Y
Are you a Cooper Wiring Devices Electrical Supply Expert? Answer questions, earn points and help others