Question about Carrier Heating & Cooling
Furnace comes on for 1 min then kicks off, repeats this cycle
Have Carrier 58GP075-3 furnace
The burners come on and run tell the blower kicks on, at the exact same time blower comes on burners go off.
Blower runs for about a minute, then at the exact same time blower goes off burners come on again, keeps repeating this cycle.
MY FURNACE WOULD RUN FOR ABOUT TWO MINUTES , THEN THE BURNER WOULD GO OUT BUT THE BLOWER WOULD CONTINUE TO RUN , LONG ENOUGH TO COOL THE FAN LIMIT SWITCH DOWN , THEN IT WOULD START THE PROCESS ALL OVER. WHAT FIXED MY PROBLEM WAS THE SECONDARY HEAT EXCHANGER THAT IS LOCATED JUST ABOVE MY BLOWER MOTOR WAS PLUGGED WITH DIRT , WHICH RESTRICTED THE AIR FLOW , CAUSING THE FAN LIMIT SWITCH TO REACH 200 DEGREES AND SHUT THE BURNER DOWN . YOU'LL HAVE TO TAKE THE BLOWER MOTOR OUT TO GET TO IT , BUT MY FURNACE IS RUNNING PERFECT NOW
Posted on Jan 11, 2010
    Sergeant:
    Champion:
  • 373 Answers
Sounds like mine did
it was a realy switch
Posted on Feb 06, 2009
1999 Goodman down draft natural gas furnace. It starts as normal, the burners fire and it warms up, but the blower doesn't start, after a couple minutes the burners shut down and the blower immediently...
IT SOUNDS LIKE THE FAN CYCLE RELAY OR BOARD IS NOT MAKING THE FAN COME ON WHEN IT SHOULD THE BURNER SHUTS OFF PROBABLY BECAUSE IT REACHES THE HIGH LIMIT.
Feb 03, 2015 | Heating & Cooling
Coleman evcon furnace
How old is your furnace? Does it have a circuit board that controls everything, or are there separate controls for each function?
Nov 19, 2013 | Heating & Cooling
The furnace will start and run for 5 mins and kick off. Then the burners will not reignite after that. However, after everything cools down (about a half and hour later) it will restart and run for...
Hello, sounds Like the Furnace is tuning off due to the limit switch or rollout switch opening. A limit switch and rollout switch are safety swtiches that will turn off the furnace if it gets to hot or the burners flames are abnormal. Usually a weak blower motor, dirty blower wheel , dirty burners or even a crack in the heat exchanger can cause this problem. Best bet is to call a hvac technician and have them check it out.
Sep 14, 2011 | Heating & Cooling
Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...
Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
Oct 29, 2010 | Electric Circuit Breaker Kit for Furnace
Carrier Weathermaker SX model 58SX060-CC Blower runs all the time
Remove all power from the furnace, it is likely the brain in the furnace is need of being reset, from the battery replacement, why did you change the battery, was there an indicator telling you to change it?
Many times just removing all the power to the furnace will do the trick with a reset, if not let me know and we will go from there, but it sounds like the main brain is confused or bad, more likely confused, so try the power removed first.
Than let me know wbwill@sbcglobal.net
Oct 22, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...
Carrier weathermaker sx 58 furnace
I have serviced these furnaces for 20 years and I can tell you most of these models did not have diagnostic lite on them. (although some did, especially if the control board has been replaced) The problem is most likely a bad 3 wire pilot. This will cause exactly what you describe. 2 things to consider though. 1, If you were to replace the pilot don't get a cheaper knockoff. In my experience these do not last long at all. Get the right one from a carrier dealer. It will cost more but be much more reliable. 2 What is the condition of the secondary heat exchanger? Most if not all of the sx series had issues with the secondary heat exchangers rotting out and leaking. If the furnace is out of warranty you would be much better replacing the furnace as the cost of replacing the secondary heat exchanger will probably be almost the same as a new furnace. ( those babies are EXPENSIVE!)
Dec 17, 2007 | Heating & Cooling
Heating & Cooling Logo
1,119 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others