Carrier a/c tripping circuit breaker
This is a fc4bnb054 carrier heat pump. It occasionally trips the breaker on the unit. I have used a meter and checked electrical connections and voltages and the only thing that I found was that I could not get a reading from the output side of the transformer. Could this be the problem or do I need to look somewhere else?
  • 1 more comment
  • bennettstuff Feb 04, 2009
    I am sorry.. It is the breaker on the unit itself that feeds the transformer, heat strips, fan etc.. I pulled the heat strips out and they visually look ok with no breaks or burned spots on them.. thanks fotr the assistance.
    This is an older home and has been working in the past... It is a heat pump and the heat strips are not even in use when this is happening..Could a bad transformer be causing the problem as it is hooked up to the breaker? thanks again for the assistance.. ric
  • Chris Parrish May 11, 2010
    Which breaker you should have one at the unit on the heat strips and one in the panel for the house?
  • 10,865 Answers
I believe you are tripping the breaker because you are too close to the capacity of the breaker based upon the distance from the panel to the heat pump. If you are electrically skilled you could check this by measuring the distance and then looking at the standard to see. If this makes little sense to you, you may need to have an electrician check for u. Either way, good luck with it.
Posted on Feb 04, 2009
Carrier edge thermostat screen went black. won't do anything???
Check your drain line. Likely tripped the float switch and killed the power to the tstat. Must vacuum and clean drain.
May 17, 2017 | Carrier Heating & Cooling
Any ideas as to why the panel breaker for my Goodman CPE24-1AB heat pump would immediately trip when the air conditioner is turned on?
Without looking up the specifications for this heat pump, I cannot be certain, but I expect the operation to provide cooling may require more power than when heating. You probably can find the specifications online for this unit. As you probably know, power is measured in watts and is calculated by voltage times current. This also is likely to be 240 volts operation. If you take the specified power on cooling and divide by voltage (240), that will indicate the current in amperage that will be required to start it. Your circuit breaker is set for current and needs to be a higher current than is required. If that is the problem, you can buy circuit breakers at Home Depot or Lowes. You have to remove the front panel of your breaker box and snap out the circuit breaker. To be safe it would be good to turn off the main breaker switch before you open the front panel and remove the circuit breaker for the heat pump. Should your calculation of current required be less than the rating of the circuit breaker, that implies a malfunction of the heat pump in the cooling mode and would require a service call to the local representative of the heat pump manufacturer.
May 16, 2014 | Goodman CLQ36AR49 Air Conditioner
I have a carrier air conditioner 38TKB024. About 15 years old I think. Accidentally ran it with the cover still on after the winter. shut it off after about a day when I realized. Went to try it the...
You probably just blew the fuses or tripped the circuit breakers. There may be fuse right beside the unit in a box with a door on it. The fuses will be in a cartridge inside the box. You will need to change them both unless you have a ohm meter to check them. Also check your circuit breakers. The will more than likely be in your main circuit box. It will be two joined together, probably 20a or 30a. Trip them all the way back and then forward and try the unit again.
Jun 11, 2011 | Carrier KCA101P Air Conditioner
My unit is tripping the main breaker what should i look at first
With this cold weather, -- it is not likely tripping off because it is too hot!
Are you familiar with the history of this unit?-- Like has it tripped in the past during HOT weather?
This might be a clue, that the circuit is really loaded close to its limit--
This leads to the next possibility: That the breaker is getting weak (They do after many hard starting loads!
Now-- If you can get the system to start and run for just a few seconds-- can you put a Clamp around Amp meter on the wires?-- and read the full load current?
How close is this to the rating of the circuit breaker?
Is the breaker, and the wire size marginal?
Another thing to look for, is loose lug screws at the main fuses, and the Main contactors, and the motor leads--- for loose wires result in overheating, which raises the current, and leads to tripping, too.
How long ago was the condenser cleaned-- this leads to high amp draw too.
But the first thing would be to learn more about the age of the Main Breaker, and what the 'normal' run current is for that system.
Mack B
Dec 28, 2010 | Carrier 38CKC036 Air Conditioner
I have a Carrier AC unit with a heat pump. I noticed that it wasn't cooling and the circuit breaker had tripped. When I reset the breaker and try to start it again, it trips againafter 10 seconds. The...
Check with your contractor to see if their repair is warrantied. If it is not call someone who carries a warranty and satisfaction guarantee on repairs. It is likely that you got a bad capacitor, however, this typically will not trip a breaker. It's possible that other issue(s) caused the capacitor failure.
How old is this unit?
Aug 26, 2010 | Carrier 38CKC060 Air Conditioner
Breaker trips on roof top RV A/C
check your breaker is it hot to the touch?
check the wire tightness at the breaker?
remove the circuit breaker and inspect the terminals on the breaker and in the panel and the breaker itself for signs of overheating and discoloration due to the fact
check the connections at the unit itself
check that you have proper voltage to your unit
find the nameplate and look for FLA full load amp draw
is the breaker properly sized for the unit and is the wire size correct for the breaker?
(Check nameplate on unit)
buy a clamp on amp meter and see if it is under or over the nameplate rating when unit is running
take great care when you venture into electric,if you arent comfortable find someone who is.
you may have a weak breaker if all the above pass?
Replace it
Jul 05, 2009 | Dometic Rooftop RV Air Conditioner
Central air conditioner will not turn on at all.
I understand this to be a heat pump. Check your thermostat settings, and the filters. And make sure a breaker isn't tripped.
May 21, 2009 | Carrier Heating & Cooling
Breaker on transformer trips periodically
You have a low voltage short in the system. The only way to find where the short is is with a amp probe. Do you have any dogs that like chewing. i have had many cases where the outside unit has chewed up thermostat wires causing this. If you do not have the amp probe you may need to get a service tech to come out and find short
Feb 13, 2009 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
506 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen