Question about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
Ingitor comes on but main ports wont ignite
Hi I have a carrier super saver model 58ssb it is about 20 years old. My ignitor will light the pilot flame but when it asks for the main port to ignite all it does is click continously. I have changed the pressure valve to no avail. Is the problem the gas solenoids? Because I do hear them clicking. It was working fine up until now I even had the furnace checked over and everything was fine until now.
  • 11 more comments
  • playground2 Feb 04, 2009
    I checked that also and thats not it. I replace this part last year so it is relatively new, however who nows nowadays. I believe it is a white rodgers it is stamped "wr" as for part # I think it is #36e 93 304
    This unit is older than that I also replaced the circuit board the year before last. Because on the
    last one the solenoids went bad.
    The draft inducer motor does not run until the furnace kicks on there by exhausting any fumes if this the motor which you are talking about.
    I havent checked inside the motor istself for trash but I will do that. As for the tube itself I didn't see anything inside it.
    As for the pressure switch it is normally open held closed.
    Yes it is natural gas.
    The tech told me that the gas pressure was 3.5 which was on the money he said.
    The controller board is a hamilton test systems model #990-490 with a 24vdc airpax attached to it the # on that is 37a11z24-0021 8718
    Just to let you know that board is the original its about the only thing I haven't replaced.
    And yes that inducer ran up until this problem.
    Sorry took so long I have a new problem now the pilot light isn't even igniting now? Don't know what to think now!
    And I do believe you are right that inducer motor did come on prior to the furnace igniting and now it aint working either.
    Yes that airpax is connected to the control board that switches the pressure switch. Are these problems connected to this board?
    The board I did replace was to the blower motor I figured it was important enough to mention. Don't know if was or not.
    Hey that's what I thought it was too I was going to purchase the board but I was told it might be the pressure switch. Yes it is a spark ignitor and it is controlled from the board. Which I believed would control everything else in the working sequence. I can get the board at a cost of $170 which is why I came to this website first before purchasing it.
    Hey its me again the board didn't work. Would like to know could it be the igniter the place where I purchased the board told me it could be that. Its a 3 wire igniter and they said if its calling for the gas and its not sensing it then it would be bad. Any thoughts?
    Yes I'm sure it was the valve because I put my hand on it and I could feel it. It was replaced 2 years ago and it has a electronic control module in the middle of it controlling the 2 valves.
    It comes on for about 15 seconds then it goes through the motions of the valve clicking, and the ignitor keeps on clicking also all while the pilot light stays on. But the ignitor clicking and the valve clicking are two different clicks. If that makes sense.
    Yes it is the ignitor that is clicking it's an electric current jumping across.
    As for the board there is no identification mark on who the it except this number which was on the back it is 1010-93-9192a
    Model #58ssbc8c-cc
    Series #100
    Serial #3287c89149
  • playground2 Feb 06, 2009
    Hey I don't know who you are but I want to thank you for help over the last few days. However nothing worked. I decided to just leave it off and use space heaters.I would like to have worked on it longer but I'm going back to Fllorida this morning. I guess I'll just have to leave it to the junk yard and buy a new furnce come spring. If you have any suggestions on what make I should buy please let me know. I take anything into cosideration. Thanks again. Patrick
    Brigadier General:
  • 8,619 Answers
Hi!
I think water has entered into the knobs or near the igniter connections, that is why the connections are getting short and it is clicking continuosly
Posted on Feb 04, 2009
  • Rylee Smith
    Rylee Smith Feb 04, 2009
    Use a blower or hair dryer to blow out the moisture and it will definetly work fine. Also clean all the connections and see whether for any shorted wires or connections
    President:
  • 1,214 Answers
Check that the inlet filter screen to the gas valve is not plugged.
You have to turn the gas off, then remove the fitting at the inlet to the valve. I've had this happen before, especially if a copper line was used (hopefully not, as this is totally a No-No.).
Reply back what you find. It could be a bad valve, and I will need to know whose valve it is (Honeywell, White-Rogers, etc.) and P/N's on the valve.
  • 13 more comments
  • Mark Egan Feb 04, 2009
    Are you getting any blink codes on the controller circuit board (or is this unit just a little older than that?)?
    OK, I found a manual for that furnace.
    Is the draft inducer blower running?
    Have you check that there is not a little piece of trash inside the inducer motor housing that might be partially blocking the rubber tube, or even worked it's way up inside of the tube?
    The manual didn't have a wiring diagram, and I don't know for sure if the pressure switch is wired normally closed, held open, or normally open held closed. See if you can tell, and defeat the logic to see if the valve will light.
    I assume your on natural gas, correct?
    Do you know what your gas pressure is?
    Presently, does the draft inducer ever run?
    Normal sequence for draft inducers is they come on before the gas valve to purge the heat exchanger. The pressure switch tells the control board that the inducer fan is running, giving the OK to turn on the main gas valve, provided a pilot is detected.
    Can you give me the make and model number of the controller board? I need to see what it's sequence of operation is and connection points are?
    Sorry. Have been digging to see if I could find anything on this furnace (did find the manual, but manual doesn't help.). Hamilton Test Systems was spun off back in the 80's (I think it was), and I can't find anything on the controller board.
    Temporarily jumper the pressure switch and see if the gas valve will open on a call from the T-stat. Something is acting funny here.
    Was I correct that the draft inducer ran prior to call for main gas valve?
    The airpax relay must be a part of the controller board?
    And you said you replaced a board last year, but not this one ("because the solenoids went out")?
    Based on what your saying right now, I am leaning toward that board being a problem.
    As I mentioned before, the sequence of operation is pretty much the same for all of these systems.
    And I just noticed in some of your previous postings -
    The draft inducer motor is the small blower on the front of the furnace that should run prior to pilot ignition. The fan or air blower is the one that comes on shortly after the main gas valve opens and the heat exchanger warms up.
    Is your unit used spark ignition? And is the ignition module separate from the control board that controls the startup/shutdown sequence? If so, I'll track a board down for you. If not, I'll need to know more.
    Well, I'll support your decision at this point (at least from a distance, and based on what I can see looking through these teeny tiny wires to see what you are seeing.).
    Let me know if it works.
    Yes, but it seems odd that you are hearing a clicking sound from the valve. That would indicate to me the board is OK, and telling the valve to open, although the board only sends one continious signal, not a pulsing signal, to the valve (so does not explain ticking.).
    Are you sure it was the valve going tick, tick?
    If it's a three wire ignitor, are there three probes that you can see where the pilot flame lights up? (If it's three, I would guess ground, spark, and sense).
    Does the pilot flame remain on, or does it go off after say 1-2 minutes?
    Does the ignitor really click? Or is it something the ignitor attaches to, like a circuit board of some type?
    Can you ID the circuit board or controller that drives the gas valve (I think that's the board you replaced a year or two ago)?
    Give me the full model number of the furnace.
    I finally found the gas valve. And the furnace was probably built in 1987 date code you gave 8718, is the 18th week of 1987).
    I've found some controller boards but none with numbers like you gave. I have also found where Carrier has developed a kit where they can decrease the number of boards they need to keep in stock. But still have not identified yours.
  • Mark Egan Feb 05, 2009
    Yaaaaa-heeeeeeee! I found a wiring diagram. Give me a bit to figure it out, and I'll get back to you.
    OK, looked the wiring diagram over, and the guy at the store is probably correct. It's a 3 wire device, connected to a SPDT heat sensitive switch. Normally closed is YEL/GRN, Normally Open is YEL/WHT. I had read somewhere that you can tap on the pilot assembly with a plastic handled screwdriver one the pilot has been lit a few moments, and if the gas valve opens, then that's the problem.
    I'm pretty confident in this one being the culprit. I hate that you had to ge tthe controller board, but fhese old furnaces are difficult because the manufacturers had to scamper to meet DOE requirements back then. Even Carrier now has a retro kit for the boards because it was just too hard to keep up with all the different versions.
  • Mark Egan Feb 06, 2009
    Well,
    I hate that we couldn't get it fixed, but sometimes it's hard to see the obvious over these teeny tiny wires.
    Back in the day when I used to put equipment in, I preferred Rheem/Ruud. I have not serviced or installed any of it in the past 10 years, but furnace design is pretty striaght forward. I've got 2 Rheems in my house that have worked flawless for the past 10 years.
    Oh, and thanks for the pat on the back! HVAC is a business I have a passion for.
  • Brandon Carmany
    Brandon Carmany Jan 23, 2014
    I am having the same exact problem with my Carrier super saver with the white rogers 36e valve
I have a Lennox furnace Model G19 and the pilot will not light.e You get the normal clicking sound and the ignitor lights but it seems to be a very small flame and the pilot does not light. The ignit
probably need a new control board. so it sparks but gas not coming on? usually you will hear a click then hear gas coming out. if you have a voltage meter check voltave going to gas valve while ignighter is clicking if you have voltage bad gas valve. you should read about 24 volts at gas valve.
Mar 09, 2014 | Heating & Cooling
How to install a spark ignitor in a gas furnace?
How to install a spark ignitor in a gas furnace? - Fixya
www.fixya.com/support/t15727344-install_spark_ignitor_in_gas_furnace
Jan 8, 2013 - How do I connect the high voltage wire to the Model 990-516 spark - Air ... SOURCE: Goodman furnace wont light, ignitor suspected. Notice.
carrier igniter
Jan 08, 2013 | Heating & Cooling
MY ruud silhouette gas furnice unit comes on but burners don"t.can't see pilot light.the unit has electic ignitor
You either have a spark ingitor or you have a glow coil ignitor. The glow coil ignitor is located on the left hand side of the burners. It is a very fragile part.
If you have a mirror or have good eyes, look to see if
it has a crack in it.
Feb 19, 2010 | Ruud UBHC Air Conditioner
I can here ignitor sparking but no flame, on a Carrier RTU.
Can you see the spark? It shoud be around about 1/4" gap. Make sure the igniter is sparking on the burner. Can you smell gas or hear the gas coming on? The pilot if it has one could be dirty or if it does not have one then the main burner cross over may need to be cleaned. Be careful and stand away from the heater while checking.
Jan 04, 2010 | Carrier 38CKC036 Air Conditioner
Delayed ignition of a Ruud high efficiency upflow 90 plus propane
It sounds like the first thing to do is have burners and pilot cleaned and adjusted so ignitor and pilot flame is close to main burner ignition rail.
The "whoosh" is due to delayed ignition because the pilot flame does not come in contact with main gas.
One more thing that should be tested is the gas pressure and combustable air mixture to be sure it is correct.
It is always best to have a qualified technician do this for you, In many areas the gas supplier with check and safety test this for you.
Nov 24, 2009 | Ruud UBHC Air Conditioner
Gas heater won't ignite
I agree. Either the pilot flame is dirty and is not making good contact to heat up the bi metal strip on the pilot assembly, or the pilot assembly is defective. 90% of the time if you clean the pilot orfice and the pilot burner it will take care of the problem
Nov 16, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling
How to light a American Standard furnace
If it is an old furnace with a manual pilot light there are pilot lighting instructions usually on a door or panel. If it is 15 years old or newer it probably has either a spark ignition or a hot surface ignitor. These can't be lit manually. If they fail they usually require parts to be repaired.
Jan 01, 2009 | Heating & Cooling
Burners wont ignite
does unit have thermo-cupling
Nov 23, 2008 | Carrier 52PQ307 Wall/Window Air...
Furnace pilot is on, pilot ignitor continues to click, no main flame
sounds like the sensing bar on the spark ignition is dirty.....a wire brush works nicely.
Oct 17, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo
579 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others