Goodman pgb 0300751 gas package unit. The unit started running both the combustion and circulating fans. Technicians have put two new honeywell boards in it. the fans are still running. all circuits and loops and voltages have been checked, but the unit is still running the combustion and circulating fans. the combustion fans is what pulls the heat through the heat chambers to the outside.
Ever so often the exhaust fan comes on and then the burners ignite and burn for a minute or so and then go out. The exhaust fan continues to run sometimes about 4 minutes or longer then the indoor circulating fan comes on with heat. WHAT IS THE PROBLEM----goodman gaspack.
Posted on Mar 23, 2010
  • 700 Answers
Then you need toi have them check the fan high limit that is mounted in the blower compartment. if it's closed then the blower fan and the conmbustion air fan will run together.
Posted on Feb 04, 2009
Have a Goodman GPG13 single package gas-electric heating and cooling unit. Turned on the heat and the outside unit ran a short time then shut off. Smelled gas after it shut off. Is this an igniter...
There is a induced draft motor that will run first to purge the combustion chamber and induce a draft, a pressure switch closes proving an induced draft exists, thus allowing the spark and pilot gas, or hot surface ignitir and gas to pilot rsil and /or burners, a trial period for ignition about 30 seconds each for 3 attempts will be made and if not lit by the 3rd attempt it locks out, requiring a reset of power to unit to reset the module or circuit board etc. 1st see what motors running, is it the flue exhaust motor/induced draft??
Nov 02, 2010 | Goodman Heating & Cooling
We have a Goodman gas pack (PGB 030075-1)and no heat. A/C works fine. We can get the blower to come on but nothing but cold air comes out. Do we have a pilot light on this unit that needs to be lit?
Amy,
There is no pilot light. It is electronic ignition.
If you have a gas supply and it is turned on you have electrical problems inside the unit.
Jan 04, 2010 | Goodman Heating & Cooling
Combustion fan and circulating fan running and no heat
Check near the squirrel cage fan and see if there is a sail switch.  Sometimes these are used to confirm air movement prior to firing off the gas furnace.  It is simply a square piece of metal on a stick that attaches to a microswitch.  This switch is then depressed when the fan pushes the air (and the metal piece) allowing the burner to fire off.
Hope this helps.
Feb 03, 2009 | Goodman GMS90703BXA Heater
Older Goodman gas package unit combustion and circulating fans
There is a limit switch tripped somewhere. it is either the main limit in the firewall orthe limit switch on the small fan (inducer) that is tripped some of these are manual reset try pushing the button in and see if that stops it.
Feb 03, 2009 | Goodman CLQ36AR49 Air Conditioner
My father has an older model two and a half ton goodman gas package unit. it has had two boards put in it, the problem is that the unit will go through a heat cycle and the combustion motor and the...
the fan induction motor produces a vacuum, check of orofice on motor is plugged by pulling hose off switch end and putting in mouth while running and sucking, this will make a whining sound immediately if no restriction. the fans are controlled through the board by vac., swich, limit sitches, and timers in the board itself. maybe a bad ground on flame sensor.
Jan 29, 2009 | Heating & Cooling
Older model Goodman gas package unit
It sounds like it is still receiving a "call" for heat from the thermostat. First check that the thermostat is set for gas heat and not electric.(There may be a jumper or dip switch on the back). Read the directions with the thermostat.
Secondly, Verify that the wiring at the thermostat is correct. (R- to red, W to white, G to green etc.)
Third, If the first two do not fix the problem, then there is definitely a problem in the thermostat wire between the furnace and the thermostat. (usually the "R" and "W" wires will be crossed or shorted to the sheet metal around the furnace. You may just have to replace the entire wire. Best of luck!
Jan 28, 2009 | Goodman GMS90703BXA Heater
Two and a half ton Goodman Package Unit
goodman boards really have to have a very good ground. make sure the ground wire is securely attached. also even though you say the limits are all good, you need to check the wiring that goes from one limit to the next. they should make a loop that goes from the plug at the control board to each limit and then back to the plug. take the plug loose and locate these 2 wires. ohm them out. if it is open, your problem is somewhere in the loop. the fact that the blower is running all the time tells me the board is not getting the signal it is looking for from the limits. I have seen some goodmans that have a rollout problem at the burner box and it melted the wiring to the limits on top of the box.it is hard to see so you have to look closely. also if this is the case, you need to have someone check the heat exchanger for a crack. the rollout usually does not happen till the fan starts blowing while the burners are on. if this is the case, you do not want to run the furnace for any reason as this is a carbon monoxide risk.
Jan 27, 2009 | Goodman CLQ36AR49 Air Conditioner
Gas Package Unit Keeps Running with all T- stat wires unpluged at the unit?
does that unit run heating or just the fan run? if just the fan you may have a bad fan thermostat
Oct 21, 2008 | Goodman CLQ36AR49 Air Conditioner
Newly installed Goodman GPG13 gas/electric package unit installed. Cannot get AC to cycle on. Unit produces heat at all thermostst settings.
new unit and old thermostat/wire? thermostat could be bad or bad thermostat wires. try putting in new of anything old. do this wiring practice with the terminals being the letters.
r- red (24 volts)
w- white ( heat)
y- yellow (cooling)
g- green (fan)
Sep 21, 2008 | Goodman Heating & Cooling
Heating & Cooling Logo
345 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen