Series 100 model no. 58ssb095bc carrier gas fired surnace

The existing inducer fan is making some loud sounds when comming on. The existing heating system is locking out. When testing and jumpering out the blocked vent switch the system comes on. The existing flue serving the existing heating system is open. The system will fire normally for serveral days and lock out again. Are the blocked vent switches only good for sensing only one flue gas failure or should it be replaced. Also could the existing fan induced motor be defective and is not removing all the flue gases causing the blocked vent switch sensor to open and lock down the heating system. I thank you in advance for your attention to this matter.

Bill

1 Answer

Richard Sanderlin

Level 1:

An expert who has achieved level 1.

MVP:

An expert that got 5 achievements.

Hot-Shot:

An expert who has answered 20 questions.

Corporal:

An expert that has over 10 points.

  • Contributor 31 Answers
  • Posted on Feb 01, 2009
Richard Sanderlin
Contributor
Level 1:

An expert who has achieved level 1.

MVP:

An expert that got 5 achievements.

Hot-Shot:

An expert who has answered 20 questions.

Corporal:

An expert that has over 10 points.

Joined: Jan 11, 2009
Answers
31
Questions
1
Helped
18945
Points
59

If it is making noise, the motor may be ready to give out. The pressure switch could be faulty, but it sounds as if you need to replace the vent motor if you can find a replacement. Otherwise you've got to replace the entire vent.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Gas furnace inducer fan make whistling sound before burner fires

A whistling sound from the inducer fan of a gas furnace is often an indication of a problem with the fan, which could be due to several reasons such as:
  1. Dirty or clogged fan blades: Over time, the fan blades can accumulate dirt, dust, or debris, which can impede the flow of air and cause a whistling sound. In this case, cleaning the blades can often solve the problem.
  2. Worn out bearings: The bearings in the fan motor can wear out over time, which can cause the fan to make a whistling sound. If this is the case, the motor may need to be replaced.
  3. Damaged or loose fan blades: If the fan blades are damaged or have become loose, they can cause the fan to vibrate and create a whistling sound. In this case, the blades may need to be repaired or replaced.
  4. Improperly sized ductwork: If the ductwork is too small or improperly sized, it can cause air to flow through the system at a higher velocity, which can create a whistling sound.
It's recommended to call a professional HVAC technician to inspect and diagnose the issue with your furnace and perform any necessary repairs or replacements.
tip

Heater check out list for heater failures

Almost all furnaces built after 1978 have intermittant type pilots.
Ca banned them requiring electronic spark or hot surface ignitors, followed by induced draft motors, pressure switches or centrifigal switches that "prove" a induced draft exists, allowing the pilot sequence to commence.
electronic spark type units have a high voltage low amperage spark that is AC. Fire rectifies electricity that passes through it meaning AC becomes DC ! Fire is a terrible conducter however as a result , the DC signal is only milliamps/volts signal strength. the DC prescence is proof a flame exists for pilot, and safe to commence to mainburners.

As long as pressure switches stay closed, safeties and limits stay closed
and the DC signal to the ignition module is not broken, the furnace will run.

The normal sequence of operation is upon a call for heat from the thermostat a 24 volt signal is sent to W white (heat circuit) at the low voltage terminal board on furnace.
from there depending on unit and age the heat circuit may include a circuit board, but it still has the typical limits and safetys reqired for operation
its just not using electromechanical relays to control fan and induced draft motor etc.

for the induced draft to begin ,all limits, safetys in heat circuit must be closed.

induced draft begins and a proving switch, either pressure or centrifigal close allowung the pilot to begin, a spark or hot surface ignitor is energized and a pilot flame established,modern types use flame rectification to prove a flame, older Carrier, Payne,types have a 3 wire switch in the piloyt assembly that is a bi metal that expands and contracts clicking open and shut, allowing pilot or main burners, depending if cold or hot.

pressure switches are attached with tubing to the induced draft wheel housing and sense pressure differential and close upon induced draft running, the orifices that the tube attaches to on induced draft housing often plugs or is restricted causing pressure switch to fail to close, or waver on open and close , open , close, .

if you can run the fan in the on postion , you have both high and low voltage to the furnace.

if you dont have fan control check power, breaker , fuses.
on Dec 04, 2009 • Heating & Cooling
0helpful
1answer

I have a technical question regarding implementation of my Carrier furnace within my residence. Specifically, the furnance has been installed for 17 years and I have not had any problems with it. I have...

Thats a safety.

The unit senses a failure to ignite, so it goes into safety mode keeping the blower running to prevent overheating and fires. And keeping the inducer motor running to prevent the same, as well as raw gas build up inside the unit.

The newer systems are "smarter" and can detect more specific problems and failures. The older ones simply know that the thing didn't light, so they bring on the fans for safety.


1helpful
1answer

Inducer Fan Seems To Be Rattling

what make of furnace check for birds and blockage
unfortunatley when they go there gone the squirrel cage wheel will not come of shaft u will need motor n wheel or a "plug n play housing all in one"
0helpful
1answer

Urnace fan of some sort runs all the time - set on automatic

If you have it cleaned twice a year they should be able to find this problem. It is one of two thinkgs. There is a limit switch on the fan at the top (inducer) this may be weak and causing the inducer run frequently. The other is there is another limit switch it is a main limit on the fire wall it is also weak and that is why the main blower is running it is trying to cool that limit.
2helpful
1answer

HEATER MAKING LOUD NOISES

Check the draft inducer motor for any partial blockages or dibri.

I've seen sticks, birds nest particles and pieces of deteriorating fan blades (squirrel cage type fans) cause this.

You might also find that the inducer motors bearing are going.

If its a loud vibrating grinding type noise, I'd suspect bearings or missing pieces of the blades. (unbalanced)
If it's a clanking type noise I'd suspect loose items hitting the fan.

The inducer motor will only operate right before and during burner operation, while the blower motor can operate at any time depending on your setting.
0helpful
1answer

Turning on the heat makes a loud noise then i turn it off and just run the fan no noise

This sounds like an oil burner, which would mean your getting an oil biuld up in the fire chamber when the burner fires up. If it is a gas furnace you need to ajust the air flow.
Not finding what you are looking for?

320 views

Ask a Question

Usually answered in minutes!

Top Carrier Heating & Cooling Experts

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Grand Canyon Tech
Grand Canyon Tech

Level 3 Expert

3867 Answers

Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...