Goodman furnace GMPN080-4 Getting 4 RED blinks/Open Limit Swtch

I have a Goodman furnace GMPN080-4 REV B. I had the blower motor take a dive, so I replaced it with another equivalent 115 VAC 60 Hz 1/2 HP motor. I replaced the 10.0 MFD +10% -5% capacitor with a 7.5 MFD +5%-5% capacitor ( Grainger said it was the capacitor for that motor.) I started the furnace and it ran great for 7 days. Great heat and the blower was operating as it should. Then at the end of the 7th day I noticed the blower motor was running but the house felt like it had dipped in temperature. I checked the furnace and I had my status light blinking 4 times (red). The furnace door indicates: 4 BLINKING RED -
OPEN LIMIT SWITCH -- AUX LIMIT OPEN/ MAIN LIMIT OPEN.
I don't know what to do next. I do know that when ever the furnace was operating as normal, the exhaust (?) fan motor would engage for about a minute or two, then the ignitor would activate, the gas would flame and then within about another 2-3 minutes the blower motor would kick on and I could then check my registers to confirm heat was being sent throughout the house. Now when I set my thermostat to 78 (house is
at 68 now) and turn on my power to the furnace it starts the blower motor- but minus the exhaust blower, ignitor, burners flaming,etc. I don.t know where to begin with the Open Limit Switch,... any help??
Thanks.

Posted by on

  • slump_jockey Feb 24, 2009

    I have the same problem with a Goodman GMP075-3. The LED blinks 4 times and the blower runs constantly. I jumped the switch with a wire and the inducer blower came on. The igniter never gets hot, though. I double checked the gas is on and double checked the thermostat to make sure it is calling for heat. Still no flame.

  • Sherlock Ohms
    Sherlock Ohms Apr 29, 2016

    On the circuit board where the 2 high limit leads terminate, the terminals wil be marked hi lim or hl etc.
    Since the high limit is in series with other high limits and flame roll out sensors, to test the units operation, just remove the high limits 2 leads from the circuit boards hi limit terminals and install a jumper between the 2 hi limit terminals. This simulates a closed high limit switch/es and roll out sensors etc. You can check every safety on the circuit by ohming the 2 high limits leads, if all the safeties are closed you will read continuity between the leads, if not then chase them all down in their various locations

    Typically the high limit opens for a reason such as obstructed evaporator coil , dirty air filter, closed supply grilles, dirty squirrel cage blades, the limit can simply fail as well.

×

6 Answers

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    MVP:

    An expert that got 5 achievements.

    Governor:

    An expert whose answer got voted for 20 times.

    Hot-Shot:

    An expert who has answered 20 questions.

  • Expert
  • 61 Answers

You have a limit switch located in the furnace (a little bigger than a dime and located near the center of the front panel, sometimes the switch is mounted to a small fiberglass board) . There will be two wires going to it. They sometimes trip so often that they fail to automatically reset(due to dirty filters or undersized ductwork). You can SHUT OFF POWER TO THE FURNACE, then remove the two screws holding the switch in the furnace, pull the switch out of the furnace and tap on it and wipe it off.
The switch may work a few more times but should be replaced with the same size and type. You will see some rating printed on the switch somewhere. Write down all the numbers and get a replacemet from a furnace/AC supply house. If you have a meter and know how to use it you could check the switch for continuity.

Sometimes just a tap on the switch will get it going. There will also be a couple of rollout switches that could be tripped. They have little buttons on them to reset them. If they trip it may have other issues to be solved.
Hope this helps!
Matt

Posted on Feb 01, 2009

  • lovemybob119 May 11, 2012

    What kind of warranty comes with a Goodman furnace?

  • Sherlock Ohms
    Sherlock Ohms Nov 23, 2014

    If it has an AC coil on the furnace I bet its really dirty, high efficiency air filters reduce the air flow by about 400 cfm even if new, just try it with no air filter to test it out, as you know trying to remove the filter with the fan running is really tough as the pressure drop is usually tremendous with those type filters.

×

  • Level 1:

    An expert who has achieved level 1.

    Mayor:

    An expert whose answer got voted for 2 times.

  • Contributor
  • 1 Answer

Thanks Machtcl1!!!!! You're a genius! I had the same problem too (no heat/4 blinks). The motor had been replaced during the summer and yesterday I turned the heat on for the first time (man it was cold here in Ottawa, Canada) and no heat was coming out of the vents. I did what you suggested, located the switch (glad you described it as "a little bigger than a dime" because I would have never found it! Mine was located inside and on top of the fan stuck on the top part of the whole box. But a little tap mad it work like a charm. Weird how this thing works but it worked!!! Light was not blinking anymore and was good to go. I did write down the serial as you suggested in case it happens again and I neet to replace it. So now I feel like a genius too! Saved me a $90 service call.

Posted on Oct 01, 2009

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 1 Answer

Mine was black, round, about 2 inches in diameter, 2 screw mount, but also had a small diameter black rubber hose (vacuum line?) to the housing around the exhaust blower. I took it off, cleaned it, blew into itand sucked on it through the vacuum hose connection (it went from nothing to clearly clicking on-off or such), put it back on and the furnace worked! I will replace it on Monday when I can go buy one. This thread probably saved me a 200-300$ on a Friday evening house call on a cold February Baltimore night. Hurrah internet.

Posted on Feb 22, 2013

  • Sherlock Ohms
    Sherlock Ohms Nov 23, 2014

    Pressure switch's are often replaced when it is the orifice on the induced draft assembly for the tubing to the induced draft proving switch, if this orifice is not cleared every year count on this happening.

×

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 1 Answer

We had a pressure switch problem. The burners would work then not. The exhaust fan would start then after 1-2 minutes it would shut off. The local heating guy was busy so he talked me thru a diagnostic and determined it was either the hi limit or the pressure switch. Glad it wasn't the first one.fix is simpleand glad to save the $75.00 per hour.

Posted on Mar 25, 2011

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    MVP:

    An expert that got 5 achievements.

    Cheetah:

    An expert who has answered 20 or more questions within one hour.

    Night Owl:

    An expert who has answered 10 or more questions between 12 midnight and 6am on the same day.

  • Expert
  • 83 Answers

By saying it should not have a reading, means it SHOULD read continuity, as far as any ohms valuesthe reading wil be near zero as he said but an open circuit is reading nothing to some folks, just wanted to be clear about that, if the meter has a continuity buzzer try it or test it by shorting the probes together, whatever it does when you do that is what you want to see . this is what you should read.

Posted on Nov 23, 2014

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 1 Answer

Thank the Lord for fine people like Matt ! Theres no telling just how much money and discomfort he has save others. A HUGE heartfelt "Thank You!" to Matt.

Posted on Nov 12, 2014

2 Suggested Answers

  • 96 Answers

SOURCE: I have a Goodman furnace

limit switch is on the heat exchanger black plastic about 1and1/2 in. by 2 in. with 2 wires going to it , it has 2 screws holding it in take it out and check it with an ohm meter and you should not have a reading if it is good

Posted on Feb 01, 2009

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Blower motor makes noise, but does not work goodman


its either a bad motor or bad capacitor if you try to spin the wheel by hand and it starts then its the capacitor

Dec 26, 2012 | Goodman Heating & Cooling

3 Answers

1993 goodman status light 4 times blinking


Witch blower is running, the inducer or the systems blower?
System blower could mean the the high limit is opening and shutting down the systems gas train, I would check this out first.

The other problem could be with the pressure switch for the gas train, it is supplied from the inducer motor, check to see if it is operating fully.

HSI boards do go from time to time, this sounds more like a system control problem.

Jan 24, 2008 | Goodman GMS90703BXA Heater

1 Answer

Gmp075-3 which is the main limit switch ?


The limit switch is a credit card size shaped switch right behind the burners which has two wires attached to it. This switch will trip if the Furnace is overheating, this can be causes by a weak blower motor, dirty air filter, dirty blower wheel....anything that restricts airflow.

Dec 17, 2012 | Goodman GMS90703BXA Heater

1 Answer

I have a goodman gpmn furnace. The ignitor lights, and then the flames turn on, then the blower kicks on, and about 30 seconds later the flames turn off, and the blower continues to blow air. We have tried...


Hello, looks like you limit switch keeps opening because your furnace is overheating, Check your air filter and blower wheel to make sure it is not dirty and make sure you blower motor is moving at the proper speeed. Usually when air flow is cutoff the limit switch will open.

Feb 15, 2011 | Goodman GMS90703BXA Heater

1 Answer

Goodman dependable 92,7years old. Furnace works sometimes. Checked out by qualified technican. no problem found. Constant checks shows troubleshooting light blinks three (3) times. Help please. 3...


This indicates a open limit switch on the furnace, the heat exchanger is getting to hot therefore the limit switch is opening and not allowing the furnace to work properly. Did the techinician check the limit switch on the unit?

Dec 30, 2010 | Goodman GMS90703BXA Heater

1 Answer

PSE+G stated the problem was diagnosed as a pressure swith on my Goodman heater....any suggestions to fix? Is this an expensive job?


How do you test a pressure switch and other limit controls? This is for people who are experienced with electrical equipment and the use of a Volt Ohm meter. *Please never by pass a pressure switch or limit control. The pressure switch and limit switches are there for your safety. If you have an open limit control either the furnace has over heated or the limit has gone bad. Problems that would make a limit open up would be dirty filters, dirty evaporator coil causing a restriction in the air flow or a slow blower motor (check the capacitor on the blower motor to make sure it is good). A weak blower motor capacitor will cause the blower to run slow and eventually fail. Pressure switches, and limit switches can be tested with a meter in the same manner. With the furnace calling for heat you can test each of the terminals on the pressure switch to ground to make sure the pressure switch is closed. You should be getting between 24 to 28 volts from each terminal to ground if the pressure switch is closed. If the pressure switch is open you either have a stopped up vent, drain line (if you have a condensing furnace) or bad pressure switch. Please keep in mind there are many different types. The front terminal is burnt and discolored. This is a clue that this pressure switch has a problem.

Dec 22, 2010 | Goodman GMS90703BXA Heater

1 Answer

Red light blinks 4 times, will only cycle once


the high limit is sensing the internal temprature of the furnace.If your filter is very dirty or you have to many of the registers/dampers shut it will cause the temp. of the furnace to exceed its rating and the high limit will open the circuit and shut down the flow of gas. Your blower will then run until the furnace has cooled and the switch will close and allow it to come back on. This is bad for your furnace, make sure your filter is clean and you dont have to many registers shut. If you have run the unit without a filter the problem could be much more sever requiring blower wheel and coil cleaning and possibly a cracked heat exchanger.

Sep 12, 2009 | Goodman GMS90703BXA Heater

1 Answer

Goodman Model GMNT100-4 Auto Power Down and Up until Temp.


Keep in mind all furnaces and circuit boards are not the same. Look on the back of the door to the blower compartment. You should find the list of diagnostic codes. Look up four blinks it should narrow down the problem. Although from the discription you gave it sounds lie the high limit control. When a high limit appears to be acting up it DOES NOT mean that the high limit needs replaced. The high limit just may be doing its job. This means that the furnace is overheating. Check your filters. Are all of your registers open? Is your blower set on the right speed? Is your blower going bad? Is the blower motor capacitor bad? Is your evaporator coil restricted? Just changing a high limit switch does not always solve the original problem!
Good luck....

Apr 01, 2009 | Goodman Heating & Cooling

1 Answer

Circuit board blinks four times


check your filter if thats clogged that will send a four flash limit open or your blower motor might be bad these units are known to have popped rings and cracks on thier heat exchangers if there isnt enough airflow if your filter is clogged or motor is shot i would call someone monday and get your heat exchanger inspected

Mar 11, 2009 | Goodman GMS90703BXA Heater

1 Answer

I have a Goodman furnace GMPN080-4 REV B. I had the blower motor take a dive, so I replaced it with another equivalent 115 VAC 60 Hz 1/2 HP motor. I replaced the 10.0 MFD +10% -5% capacitor with a 7.5 MFD...


limit switch is on the heat exchanger black plastic about 1and1/2 in. by 2 in. with 2 wires going to it , it has 2 screws holding it in take it out and check it with an ohm meter and you should not have a reading if it is good

Feb 01, 2009 | Goodman GMS90703BXA Heater

Not finding what you are looking for?
Goodman GMS90703BXA Heater Logo

7,327 people viewed this question

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

paulcarew

Level 3 Expert

2046 Answers

Brandon Berry
Brandon Berry

Level 2 Expert

407 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...