Coleman 7000w gen. I have 120 on only one side of my 240 plug. I disconnected wire assembly from control box.. Could get 120 out of various combinations of the 4 wires but never 240. Should I be able to? Trying to determine if problem is at generator or control box. Thanks
This is the same problem I am having, There are two sets of windings on the stator that are 180 degrees apart so you can get the 240 volts. By measuring the resistance of the exciter windings I found that one of the windings is open so half of the 240V is "missing. I have 600+ hours on the generator so there isn't any warranty. A new stator is $699. I'm going to buy a new generator rather than pay $600 to replace the stator..
Posted on Sep 10, 2012
  • 169 Answers
At the wire assembly there should be 2 white and 2 black wires, a white and a black are the ends of one 110v winding. With the 2 white wires connected together you should get 240 from the black wires. This sounds like it is a problem with one of the circuit breakers in the 240v outlet in the control box, check them with an ohm meter.
Posted on Mar 02, 2009
Coleman blower motor eb15b bought after market replacement, old motor no common wire on the motor but wire from capacitor to transformer. New motor has common wire directly from motor how do I hook it up?
Maybe this new motor is a multi voltage motor meaning it could work with 240 volts and also 120.
If needed for 120 then you used the common .if 240 you don't need it .
Most of the time wiring diagram is on the motor itself
Dec 22, 2017 | Coleman Heating & Cooling
I purchased a 7000W Westinghouse Portable Generator to back feed my circuit breaker box. The cable is rated to 30amps. Do I use a 30 amp or a 40 amp circuit breaker? Thanks, Mike
1) Match wire and breaker:
2) 7000 watts divided by 240 volts = 29.1 amps.
30 amp breaker x 80% safe maximum = 24 amps.
This means you should use 8 gauge wire and 40 amp double pole breaker for 240volt
3) 7000 watts divided by 120 volt = 58.3 amps.
60 amp breaker x 80% safe maximum = 48 amps.
So use 70 amp breaker and #4 wire.
Jan 30, 2013 | Electrical Supplies
Coleman Powermate 6250/500 PM0545005 has power to just one side of the 120/240 outlet. the 120 volt outlets have none. Ran just fine onr week ago
The capacitor has no bearing as you have output on one leg. Take or have an electrician check the power from L1 to N and L2 to N right as it comes off the generator stator, before any breakers and receptacles. If you have no power still on one leg, the stator is bad. The rotor is fine as you indicate you have power on one leg, you may have lost one set of windings in sthe stator. Good Luck
Sep 12, 2012 | Winco Electrical Supplies
Want to add 240volt outlet to generator
You CANNOT do this, USA 240V is derived from a poly phase scenario, IE 120V line to neautral and 240V line to line, UK 240V is derived from 1 line to neutral it will not work unless you power a transformer
May 16, 2012 | Coleman Powermate Powermate 5000W...
Three year old coleman 5000/6250 generator. High
Your RPM's are too high. There is no voltage regulator in coleman generators (generator is actually made by generac) and is 100% dependent on engine speed. There is a screw under the tank when your looking in from the recoil side. It controls the governor arm. Screw it in and it incresses the rpm, out decrease. Plug something in that draws a decent load while setting the rpms since you want it to put out 120 and 240 underload. Your idle voltage does not matter.
Apr 01, 2009 | Coleman Powermate Powermate 5000W...
240 volt supply not working
there should be a switch to chane over
Jan 31, 2009 | Coleman Powermate Premium Plus 6250W...
Coleman 6250 gen
Assuming there is nothing wrong with the generator, I'm not sure what the Amp rating on a 1 hp compressor is, but starting currents can be 5 or more times the rated current, especially for starting heavy loads like compressors. While the motor only needs it for a short time, if it doesn't get it, it ain't gonna start. If you really need to run this compressor off this generator, one possible solution is to see if the compressor motor has connections inside to wire it for 240 volt operation. I realize in theory you should have available the same full power rating from the generator at 120 v and 240 v. However, many times a motor will still start more easily on 240 than 120, for the same reason that automobile starters went from 6 volt to 12 volt. If you do change the voltage to 240, BE SURE TO CHANGE THE POWER CORD AND PLUG ON THE COMPRESSOR!!!
As a side note, I have one of these generators I purchased as "refurbished", and it is flakey. It works, mostly, but not exactly right. I'm working on it. So anything COULD be wrong.
Oct 05, 2008 | Coleman Powermate Premium Plus 6250W...
Generator plugs doesn't match cord
Hey steve. do you really need 240 volts for 120 v. circuits. the reason you have to have an adaptor plug is because on your 220 volt plug in , 2 of tthose prongs are hot and 1 is ground. for safety you need to get a plug adapter ( a regular 120 volt plug end ) run a ground from adapter to ground on 220 adapter. same with nuetral. you also need to ground your generator. there is usaully a ground lug on the bottom of the gen. Another way. if you dont really need 220 v. is to use both 120v. recepticals on gen. Run 2 chords to tranf. switch. and hard wire it in to switch. another way i did mine . when i lost power in this hurricane. i ran two # 10 chords from my 2 120v. recept on my gen to my breaker panel. when you do this you have to pull the service meter, if you dont when power comes back on it would backfeed through your gen.then i turn all my 220v. breakers i was able to run lights ,ciling fans, freezer, ice box,washing machine and gas dryer , tv's computors etc. . but to do this, you probably need someone that knows what they are doin.
Sep 18, 2008 | Coleman Powermate Premium Plus 6250W...
Coleman Powermate Powermate 5000W Generator Logo
215 people viewed this question
Top Coleman Electrical Supplies Experts
John Trevino
Craig Butler
Craig Butler
Phil Walker
Phil Walker
Are you a Coleman Electrical Supply Expert? Answer questions, earn points and help others