Question about Dayton 3VU34 Heater
240v circuit wiring to run my new Dayton Heater (3Vu34A)
I was planning to run a new wire from my dryer plug (with a 40 amp breaker), that is not being used, to my garage that I will be heating.
Is the 40amp protection too high for the heater circuit?
What size wire should I run if its ok?
10-3? or is 12-3 good enough?
I could also run a new circuit from a new 30amp breaker, but the cost will be higher and I would like to avoid this if I can safely.
Thanks,
MattS
  • mrcc1234 Jan 29, 2009
    From my panel to the dryer plug which is 40amps is about 45ft. From the earlier post I am guessing its likely a 8-3 and its grounded. I have another 10ft to run to the new plug location. The heater has a 30amp, 240volt NEMA #6-30P plug type. The heater is rated at 240volt, 4000watt, 16.7amp. If I ran a new cable the total length would be about 50ft.
    Thanks, Matt
  • Joe Hogan May 11, 2010
    Tell me the distance from the new heater to the dryer plug, and the distance from the dryer plug to the electrical panel.
    also what size breaker do u now have for the dryer?
    And what size is the heater as far as watts. Is the heater 110 volts or 220 volts. get back
  • 10,865 Answers
Thanks for your quick reply. First of all let me cite the UL position on this issue:
Avoid using an extension cord with your air heater. If you must use an extension cord, it should have a rating 1.25 times the wattage rating of the heater. For example, you should use a cord rated at least 1,875 watts with a 1,500 watt heater.
That being said I strongly recommend that you spend the few extra dollars to install a double pole breaker and the proper size wire and outlet to make this a completely safe project. If you are going directly from a panel to the area of the heater I would use 10-3 with ground and do the job right.
In the long run I can assure you that you will feel real good about doing this job by the Underwriters Laboratory specification
Posted on Jan 29, 2009
  • 565 Answers
Yes, 40 amp circuit is to high for that unit. That unit requires a 20 Amp 240 volt, 3-wire circuit. Since the dryer circuit is abandoned, you can remove the current dryer circuit breaker and replace it with a 2 pole 20 amp circuit breaker. You can then remove the dryer outlet, run 20 amp circuit wire (#12) (probably in 1'2" conduit) from the dryer (now) junction box to the heater outlet in the garage. Make up your joints in the dryer j-box with large blue or gray wire nuts, put a blank cover on the box, and it's a done deal.
You don't need 12-3, 12-2 with ground is fine, however, you have to sleeve it with conduit from the ceiling down in both the laundry room and the garage.
  • 1 more comment
  • Bob
    Bob Jan 29, 2009
    Yes, a 30 amp circuit is correct, I didn't look close enough at the spec sheet, but if it came with a 30 amp plug, then a 30 amp circuit is needed. A #10 building wire or 10-2 romex will work.
  • Bob
    Bob Jan 29, 2009
    Of course, now you need 3/4" conduit if you use romex.
  • Bob
    Bob Jan 29, 2009
    Only one more concern. If the wire for the dryer is aluminum, then you'll need a special connector for the AL/CU joint.
  • 360 Answers
On the 40 amp breaker, you should be using 8-3 w/ground. 10-3 w/ground will work on the 30 amp breaker. 12-3 w/ground is used for 20 amp circuits. Your new heater should have the electrical requirements listed in the user/installation information.
I have a craftsmaster electric hot water heater 40 gallon 2 elements and I want to know if I need double circuit breaker for it because I have hooked it up and it isnt getting hot
most water heater of that size is rated 240v, therefore it needs 2-pole. is it 240v rated? make sure you have a properly sized circuit breaker & matching conductors (wires) with the kw rating of the water heater
Oct 05, 2015 | Water Water Heaters
1 question can Cutler Hammer breakers have the amperage feed through the breakers. To the breaker box and from the box grid to the load. Does it matter which way the amperage is fed through the breaker?...
There seem to be several questions mingled in with those 2 questions.
1) Amps can go either way
2) Breakers trip when heat exceeds certain level. Heat is caused by amps.
3) You want to add a subpanel in garage.
I do not know the code in your area for installing a subpanel.
Your plan will work by connecting 6 gauge wire to main breaker, and new 60 amp breaker will protect wires between main box and subpanel.
Remember, wires going into main breaker cannot be turned off without pulling meter.
Some areas require license to pull meter.
http://waterheatertimer.org/How-to-replace-circuit-breaker.html
4) To work around license and meter-pull, simply replace a 240V breaker in main panel with your new 60 amp breaker.
Then move breakers around to match new set-up.
New subpanel can accommodate two new 240V breakers and one new 120 Breaker
http://waterheatertimer.org/How-to-install-a-subpanel.html
5) 6 gauge wire is correct for 60 amp breaker.
6) I'm not sure what you mean by the box rails?
7) Do you need more amperage on main service?
This means adding a larger service panel with 150 Watt or 200 Watt main breaker.
Some areas require service upgrade when remodeling or adding circuits.
8) How to figure total amp draw at your house.
Add up total watts being used.
For example you have 1/2 Hp motor
754 watts per Hp
1/2 Hp = 377Watts
Volts x Amps = Watts
Amps = Watts divided by Volts.
377 Watts divided by 240Volts = 1.57 amps (plus a bit more amperage when motor starts)
40 watt light bulb divided by 120Volts = .33 amps
Double oven has label located inside door that shows upper and lower wattage.
Dishwasher, dryer, big screen TV, satellite receiver all have labels that show wattage.
Water heater has label that shows wattage of each element.
http://waterheatertimer.org/Figure-Volts-Amps-Watts-for-water-heater.html
http://waterheatertimer.org/See-inside-main-breaker-box.html
Add a comment for more help
Feb 18, 2011 | Cutler Hammer 100 Amp Main Breaker...
One of the breakers assigned to our Hot wtr htr has been tripping recently leading to loss of hot water. This has happened twice in the last month. After resetting the breaker things have worked fine,...
Breaker could be bad.
Let's do a quick check and save you money.
Open top cover on water heater and push in red reset button that might be tripped.
If reset is tripped, water heater should turn ON.
If reset will not reset, then replace upper thermostat:
http://waterheatertimer.org/How-to-replace-thermostat-on-electric-water-heater.html
If reset is not tripped out, then it is OK, so test two top wires on upper thermostat.
Use cheap multimeter from home center, and set dial to 240-250-277 VAC.
Test across top two screws on upper thermostat to see if you have 240Volts.
To do full troubleshoot on ordinary tank electric water heater takes 30 minutes and multimeter
http://waterheatertimer.org/How-to-troubleshoot-electric-problems-with-water-heater.html
If water heater is not receiving 240V, then the breaker is suspect, or a wire between breaker and water heater is loose.
See basic water heater circuit
http://waterheatertimer.org/240-v-water-heater-circuit.html
Now let's look at circuit breaker:
Mark suspect 240V breaker.
Identify all your breakers, and also mark another 240 Volt breaker that is same amperage as water heater 240V breaker.
Turn off main breaker.
Take front panel off breaker box.
The wires and lugs on main breaker are HOT, so stay away from that area.
Suspect breaker has 2 wires coming from breaker.
See if one or both wires are loose, and then tighten.
If wires are tight, then move these wires to the other 240V breaker that is rated for same amps as water heater.
Now turn on main breaker.
Put ear against water heater tank to hear bubbly fizzing sound.
This will identify if circuit breaker is bad, or if water heater needs a full troubleshoot.
It is not a good idea to run two 240V appliances on same 240V circuit breaker, so you may have to decide one or the other appliance until you can replace breaker.
Instructions to replace circuit breaker:
Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, fixya expert speaks with you over phone while you work on water heater circuit.
Jan 07, 2011 | Water Heaters
Need instructions on how to install a 750W Fahrenheat heater. Wire size, breaker size, etc.
To know what to tell you you need to know if it is 1 phase or 3 phase and what the voltage is that it will be running on...
Assuming that it is 240v 1 phase current you will need at least a 40 amp 2 pole breaker and #8 wire for a distance of upto about 100 ft. if longer then you need to go up to #6 wire....
7500 watts / 240v equals 31.25 amps... so a thirty to too small and you will need the 40....
Wire sizing needs to go larger as the run gets longer...
heatman101
Dec 13, 2010 | Fahrenheat Ceiling-Mount Industrial Heater...
My EH40 is not supplying power to the water heater. I hooked the power line in to posts 1 and 2 and I hooked the load out to posts 4 and 6. When I use my power checker it reads no power to posts 3,4,5,...
I have an EH 40 sitting in front of me right now.
http://waterheatertimer.org/How-to-wire-EH40-hot-water-heater-timer.html
The link above shows correct 240V water heater timer wiring for EH40
Link below shows an overview picture of EH 40 connected to 240V water heater
http://waterheatertimer.org/images/EH40-water-heater-circuit-5.jpg
EH40 has a 240V clock.
Terminals 1 and 2 send power to the 240V clock
Power to the clock terminals do not pass through timer to any other terminal
How to wire EH40 for 240V
240V line has 2 hot wires from breaker box.
Lets call these wires Hot1 and Hot2
These wire are interchangeable on 240V circuit
Hot1 connects to terminal 1 with a jumper to terminal 3 (or connect to 3 and jumper to 1)
Hot2 connects to terminal 2 with a jumper to terminal 5 (or connect to 5 and jumper to 2)
240V circuit has 2 wires going to the Load
Let's call these Load1 and Load2
These wires are interchangeable on 240V circuit
Load1 connects to terminal 4
Load2 connects to terminal 6
If the timer is still not working, go back to the breaker and test if it is delivering 240V to the circuit.
If breaker is bad on one leg, then the circuit can test with live power, but the 240V appliance will not work.
240V circuit requires both legs of 240V before circuit is complete.
Oct 24, 2010 | Intermatic EH40 - Electronic Water Heater...
Unit comes on and runs for 5 minutes, the circuit trips off
30 is the correct size breaker for this unit. It sounds like there is a grounding issue going on in the system. Or off of the Thermostat. Something is grounding out causing the switch to trip. Are you running #10 wire to breaker and the unit? If not you will need to increase your wire size
Jan 03, 2010 | Dayton D-F79 Electric Space Heater- the...
I have a whirlpool WED5300SQ0 dryer that is on a 30 amp circuit , it trips the breaker after about 15 min ,,,it has 10 gage wiring but it is an older house , the breakers look ancient..should i replace the...
If you don't have an AMP clamp to measure the amount of AC current draw. Then I would replace the breaker with a new 30amp. If the electrical panel is a sylvania or Zinco then that is most likely the problem! Those panels use the same breaker type and are terrible at having breakers going bad and tripping premature. If it is one of those type of breakers better dig deep in your wallet as those breakers run $1.25 to $1.50 per amp !
Nov 30, 2009 | Whirlpool WED5300S Electric Dryer
Have a dedicater 220v 20a circut break to a clothes dryer. The only work done but the electrician was a new main grounding wire and removed conduit and wiring in the basement. Now the breaker opens after 1...
Typically, a standard electric dryer is 30A 240V unless it is natural gas. If the wire is #10awg then you can put a 30A circuit breaker on it. If the wire is #12awg then you DO NOT want to put a larger circuit breaker on it or it over heat the wiring in the wall. If it was a short in the wiring the circuit breaker would trip immediately even with out the dryer plugged in. If it was a grounding problem the circuit breaker would not trip at all, it would just electrify the dryer chasis. It sounds like it is an over current problem, drawing more than 20 amps through the circuit breaker, or like the dryer has an internal problem that is causing the circuit breaker to trip.
Nov 21, 2009 | Gb Electrical 100 Amp GE Load Center
Dayton 3VU34 Heater Logo
997 people viewed this question
Top Dayton Heating & Cooling Experts
Paul Carew
Mack Baxter
Dan Webster
Dan Webster
Are you a Dayton Heating and Cooling Expert? Answer questions, earn points and help others