Question about Honeywell Electronic Programmable Heat/Cool Thermostat - CT3300A100 Heater
I have a LP horizontal AIREFLOW furnace and it fires up pand runs fine for about 5 mins, then the burner shuts off and re lights over and over again before the stat has reached temp setting. I have replaced the pressure switch, the gas valve, the control board and it is still doing it. It has 2 inch PVC vent pipes for intake and exhaust. HELP!
    President:
  • 1,214 Answers
Assuming you have A/C on this system, I would look to see if the evaporator is plugged with dust from a failed filter.
That causes the exact symptoms that you describe, assuming the filter is clean and all supply and return vents are open as the system was designed to operate.
Let me know what you find or you rthoughts and I can give you instruction on how to clean. One indication it's the evap being plugged is buildup on the blower blades. That will need to be cleaned too.
Posted on Jan 28, 2009
Burner comes on for about 30 seconds then goes off. after a little while it lights again. then goes off again. this repeats 4 or 5 times then furnace shuts down completely. gas supply problem?
That's usually your flame sensor. If the board doesn't detect a flame after burner is running it will shut your gas valve down. You can usually fix this by cleaning the flame sensor with some extra fine steel wool.
Dec 26, 2016 | Heating & Cooling
Coleman evcon furnace
How old is your furnace? Does it have a circuit board that controls everything, or are there separate controls for each function?
Nov 19, 2013 | Heating & Cooling
I have a bosch aquastar aq 125fx probably 9 to 10 years old it heats fine but after about year 2 it stopped working when you fire it up shortly or immediately after firing it up before. in other words it...
You either have a weak spark from your ignitor which needs replacing, a bad elec connection to the ignitor, or it needs to be repositioned nearer the burner. Check connections and try repositioning it before you install a new on.
Apr 30, 2017 | Bosch & Tankless LP Hot Water Heater
I have a hanging Dayton in garage pilot lights fine furnace fires up runs 6or7 min. then burner and pilot go out
Does unit fan come on ??? Is flue clear as most units have a safety klixon if exhaust not venting properly.
Nov 24, 2012 | Dayton Gas Furnace Heater
Have a goodman lp gas furnace modelgmpn060-3 furnance starts up get main flame for about 5 seconds then shutsoff
i would start by checking the flame sensor ...if the unit is actually firing off just not staying lit sounds like a faulty or dirty flame sensor.... if you look inside at burner assembly there will be a metal rod ranging from 1 1/2 to 4 inches in length.... it ia in burner assembly and has (1) wire that connects to it and usually one 1/4 inch screw on it.... remove this and lightly /let me emphasize lightly sand it and clean it ...to much will actually damage it...re-install and see if it helps... this senses the flame and tells the control board to keep gas valve open most likely your culprit....good luck to you...
Feb 13, 2011 | Rinnai RHFE-431FAIII 16,700 BTU Direct...
RUUD Ultra 90 Plus Modulating up flow furnace UGFD_07EMCK 1.5 years old. Furnace doesn?t function properly from the very first day, often shuts down after initial burners firing. The 1st (right) burner...
Sounds like the cross over between the burners are to tight. I would take a common screwdriver and open the slot just a little. Only other thing I am worried about is the gas pressure on the burner side. Needs to be set as per installation manual.
Jan 05, 2010 | Heating & Cooling
LP Ruud furnace achiever 90+. Strange problem.
Sounds like two problems. Not enough combustion air or a defective high temperature limit switch. You enclosure may not be getting enough outside air to properly sustain combustion. If the unit has a rollout thermostat it may be defective and stopping everything.
Oct 10, 2009 | Heating & Cooling
Dometic RM 2800 Works great on AC but not on LP
Most likely cause is a blocked gas jet in the main burner its rare for the thermostat to be faulty but you cant dismiss it
Jul 27, 2009 | Dometic RM2652 Refrigerator
FURNACE CYCLING ON AND OFF ..
I would check furnace filter first. If that looks good i would check the thermostat. To check thermostat turn power off to furnace then take thermostat off the wall and connect wires labbled R & W together then turn power on and check furnace to see if it runs for more than a couple of minutes. If so install a new thermostat. If that doesn't work let me know and i can give you a couple more thing to try.
Jan 17, 2009 | Honeywell Programmable Thermostat Heater
Rudd furnace molel robd-150rbja worked good for 5 years now takes 24 hours to raise house temperature from 60 to 70 degrees burner fires properly then fan starts properly after about 5 mineuts of bott...
Get it looked at quick, before your exchangers crack, because the furnace not cooling them down after operation will lead to failure, and the replacement is not cheap, close to the cost of a new unit.