Goodman heat pump trips sometimes no know cause.

Unit about one year old. The unit trips a 20 amp breaker every once in awhile. Cause unknown. Company noted 78 amps once when starting. Company who installed the unit place a hard start kit on th unit. The unit is mounted about 15 feet from inside unit. Inside unit down flow GR28K7-PFV-270.

Posted by on

  • the_maintena Jan 28, 2009

    The entire system is new. They wired new service 20 amp to the out side unit. The 20 amp trips infrequently no know cause. Will the hard start kit reduce the expect life of the compressor. I'm worried about the warranty. Would the manufacturer void the warranty 10 year if a hard start kit had been installed.

  • Mark Egan May 11, 2010

    Which circuit breaker trips? The one on the furnace, or the one for the outdoor unit?

    78 Amps on start is not unheard of. You can check that by looking for a value indicated in the LRA section of the compressor electrical label.


×

Ad

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    President:

    An expert whose answer got voted for 500 times.

  • Master
  • 1,214 Answers

20 AMP Circuit, huh? More on this below.

The tech probably didn't put a hard start kit on, but if he did, I hope he added the resistor to the start capacitor, or you could have a problem in the future. He probably put a soft start on it, a 2 wire device which looks like a capacitor. But only you will know for sure (or he.). As for warranty, manufacturers don't care about soft or hard start kits. In fact, they like 'em, because they extend the life of the compressor, which keeps them from having to pay for a new one.

I would be concerned with a 20 AMP circuit for anything higher than 2 tons. Take a look at the nameplate rating on the side of the condensor and tell me how many Running Load Amps (RLA) this unit is supposed to pull.
Also need to know your line voltage at the condensor, with the unit running.

Posted on Jan 28, 2009

Ad
  • Level 1:

    An expert who has achieved level 1.

    MVP:

    An expert that got 5 achievements.

    Governor:

    An expert whose answer got voted for 20 times.

    Scholar:

    An expert who has written 20 answers of more than 400 characters.

  • Contributor
  • 54 Answers

Short cycling of the compressor can be an inconsistent cause of a breaker overload. It happens when the compressor start winding is "jolted" into operation several times over a short period this can happen when there is a loose power or control wire connection that is broken from the vibration at start up of the compressor or by the occasional "jiggling" of the mercury in older analog thermostats. I suggest that all electrical connections are checked and that you use a newer model thermostat, if its not already that has a built in start delay circuit.

Hope this helps you if your still having trouble with this issue.

Posted on Jan 28, 2009

  • Wes Rackley Jan 29, 2009

    I would contact the manufacture, if it is actually needing the hard start capacitor to start every time then the equipment has not been installed correctly or it is defective and will shorten the life of the compressor. The hard start capacitor reduces the load on the start windings but does nothing for a high amperage draw on the run windings of the compressor. A high amperage draw can be caused by loose line voltage connections or wiring of to small a gauge to accommodate the current it is carrying to the compressor which causes undue strain on the windings not to mention it making your unit expensive to operate. In any case a hard start capacitor is a patch not a repair.

    Good luck.


×

Ad

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya Repairman can help you resolve that issue over the phone in a minute or two.
Best thing about this new service is that you are never placed on hold and get to talk to real repair professionals here in the US.
click here to Talk to a Repairman (only for users in the US for now) and get all the help you need.
Goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Trips breaker once in awhile.Not consistent. Replaced elements, contactors, wash motor. Still trips once in awhile.


check for a bad connection, if there is a bad connection it could draw more amperage then it should.

Jun 25, 2015 | Hobart C44a Commercial Dishwasher

1 Answer

Starting tripping circuit breaker


Good Afternoon Dennis - Often when this occurs, it is because there are too many appliances on the circuit or something may have a weak or poor breaker. Try plugging the unit in a different location or on its own circuit. If the issue continues, then it could also be possible that something shorted within the unit. So in this case, because it is a smaller appliance, repairs are often more costly than the actual unit replacement. You may want to check and see if your dehumidifier is still under warranty and if so, reach out to the manufacturer to determine the exact warranty coverage. Thanks for allowing me to help you.

Jul 28, 2013 | Frigidaire FAD504TDD Dehumidifier

1 Answer

We have a 1999 "Thermal


DO NOT install a 20 amp breaker, you can cause a fire. The breaker is rated for the WIRES, and unless you change out the wires, the 15 amp wires will overheat and can cause a fire.
Typically, A/C units need dedicated power, with nothing else on that circuit.
One step that you may try is a new 15 amp breaker. Once a breaker starts tripping, is starts tripping earlier....
You may wind up running a new circuit for the A/C, if you do, size it for the A/C.

Jul 18, 2011 | Heating & Cooling

1 Answer

Hi: I have a Carrier 38CMC42300 AC unit which will not turn on and the air handler is blowing hot air. The 40 amp breaker for the AC unit trips right away when reset. Could this be a condenser or motor...


Hi,
Your compressor or the start components are bad...
Here is a tip about troubleshooting your air conditioner...
There are many things that can cause your air conditioner not to cool...

Air Conditioner Trouble - Review the Possibilities

heatman101

Sep 30, 2010 | Carrier 38CKC036 Air Conditioner

1 Answer

I have a SubZero 690, approx 11 years old. It has tripped the circuit breaker twice, approximately 5 month apart. No additional load on the 20 amp breaker at the time. Can you suggest if it is the unit,...


Good day,
5 months surely doesn't point to the machine. I would check the wiring and replace the breaker and retest.
Breakers can become weak from age. They are by definition a heat operated device. Due to just happenstance it is posssible for both compressors to try to start at exactly the same time.
That would push the demand fairly high.
As well, usually unknown, breakers are rated at 80% of their value for continious duty. I.E. 20 amp breaker can maintain a load of 16 amps under continious load.

One caveat. The condenser coils need to be cleaned on an annual basis. To vacuum them is a poor solution. They need to be blown out with compressed air or a quality shop vac. Ugly but extremely important on Sub Zero's.

Aug 19, 2010 | Sub-Zero 690 Side by Side Refrigerator

2 Answers

My goldstar window air conditioner was working fine one day and then the next day nothing works even just the fan part.i tried pushing thei guess they are circuit breakers on the plug part that goes into...


Hi, did the surge /protectors/breakers on the cord reset? If they tried to reset then cut off again, you have a short in a component. Check the breaker that supplies the units wall plug to see if it may be tripped. If it is, it will be in the mid position and turn it off hard, and right back on hard. Hopefully it will hold. Do this, if the breaker is tripped, reset it and if it trips again, go to the a/c and unplug it. Now, reset it and it will hold. If you have a part, motor, compressor, or what ever is shorted to ground, when you plug it in and turn it on it should trip the cord and maybe the breaker to. Check these things I have told you and see what happens. If the unit does start up and start to cool, it overloaded for some reason. A part getting ready to go out, drawing to many amps and tripping cord or breaker. You will need to try and service some of it if it is coming on. Go outside and take your garden hose and give the outdoor coil a good washing. It builds up dirt and will cause high head pressures in the unit which in turn will cause it to overload and shut off everything. Clean it well. Inside, make sure the filter is clean behind the cover on the front and the evaporator coil is also clean. Dirt is a killer of these units and should be serviced at least once a year before it gets hot out side. So, do these things, leave the cord unplugged when washing out side, and we can go from there. If it starts to work good after you clean and service it, that was your problem, but keep me posted on this. I need to no the out come. We can take other steps if needed. Please be kind when you rate me for my help, if you feel I was of help. I will be here to help you more if needed.
Sincerely,
Shastalaker7
A/C, Heating, & Refrigeration Contractor.

Jul 03, 2010 | Goldstar M1003R Air Conditioner

1 Answer

I keep reseting my 15 amp breaker daily. I even moved the unit.


No. The unit is only supposed to pull 9.1 amps. (wattage divided by voltage equals amps) Your unit has a short, or your breaker is bad. Turn on the unit, when it trips the breaker see if the breaker is hot, If so, thats an indication the breaker is bad.

Apr 11, 2010 | Danby DMW112 Microwave Oven

1 Answer

Why is my air handler fan motor tripping the 20


sounds like fan motor is going bad - replace

Jun 15, 2009 | Heating & Cooling

1 Answer

Rule H53sp-24 pool cover pump trips GFI breaker


GFI devices are prone to degrade over time. Also, when used outdoors there are additional moisture issues that may cause sufficient current leakage to trip the breaker.

I had a similar problem this Spring. I was using a 20 amp GFI "master" outlet that protected two additional outlets 'downstream' of it (wired to the 'load' terminals on the GFI outlet- I'd have the check the doc. to see what terminology was used here). The pump was plugged into one of the downstream outlets.

Replacing the GFI seemed to solve the problem. I did ante up $20 for an 'outdoor' model of the 20 amp GFI unit, several bucks more than the standard 'indoor' unit - have no ideal if that represented additional value or not.

Note also, that this is the third such pump I have used for my pool cover. The other two failed to come on at all after about a year's use. The mfg replaced them under warranty (I may have had to send back the old pump - I forget!).

Curtis

Mar 22, 2009 | Rule H53sp 24mgra Swimming Pool Cover Pump...

2 Answers

Electrical - Air Conditioning


Ben, you are on the right track. To upgrade the breaker, first look at the main house breaker panel and determine if allowing more current through main breaker will be taxing it too highly (will 20 more amps exceed my main breaker limit...what is the main breaker current trip at?) Then look at the wire size leading away from the 40 amp breaker to outside. If it is 6 gage copper or 4 gage copper-clad aluminum wire, you are ok to upgrade. Any smaller wire size could be unhealthy.

Sep 03, 2007 | Heating & Cooling

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

451 people viewed this question

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8220 Answers

Paul Carew

Level 3 Expert

3083 Answers

Tim Whalen

Level 3 Expert

3074 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...