Question about Goodman Heating & Cooling

2 Answers

Goodman heat pump trips sometimes no know cause.

Unit about one year old. The unit trips a 20 amp breaker every once in awhile. Cause unknown. Company noted 78 amps once when starting. Company who installed the unit place a hard start kit on th unit. The unit is mounted about 15 feet from inside unit. Inside unit down flow GR28K7-PFV-270.

Posted by on

  • the_maintena Jan 28, 2009

    The entire system is new. They wired new service 20 amp to the out side unit. The 20 amp trips infrequently no know cause. Will the hard start kit reduce the expect life of the compressor. I'm worried about the warranty. Would the manufacturer void the warranty 10 year if a hard start kit had been installed.

  • Mark Egan May 11, 2010

    Which circuit breaker trips? The one on the furnace, or the one for the outdoor unit?

    78 Amps on start is not unheard of. You can check that by looking for a value indicated in the LRA section of the compressor electrical label.


×

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    President:

    An expert whose answer got voted for 500 times.

  • Master
  • 1,214 Answers

20 AMP Circuit, huh? More on this below.

The tech probably didn't put a hard start kit on, but if he did, I hope he added the resistor to the start capacitor, or you could have a problem in the future. He probably put a soft start on it, a 2 wire device which looks like a capacitor. But only you will know for sure (or he.). As for warranty, manufacturers don't care about soft or hard start kits. In fact, they like 'em, because they extend the life of the compressor, which keeps them from having to pay for a new one.

I would be concerned with a 20 AMP circuit for anything higher than 2 tons. Take a look at the nameplate rating on the side of the condensor and tell me how many Running Load Amps (RLA) this unit is supposed to pull.
Also need to know your line voltage at the condensor, with the unit running.

Posted on Jan 28, 2009

  • Level 1:

    An expert who has achieved level 1.

    MVP:

    An expert that got 5 achievements.

    Governor:

    An expert whose answer got voted for 20 times.

    Scholar:

    An expert who has written 20 answers of more than 400 characters.

  • Contributor
  • 54 Answers

Short cycling of the compressor can be an inconsistent cause of a breaker overload. It happens when the compressor start winding is "jolted" into operation several times over a short period this can happen when there is a loose power or control wire connection that is broken from the vibration at start up of the compressor or by the occasional "jiggling" of the mercury in older analog thermostats. I suggest that all electrical connections are checked and that you use a newer model thermostat, if its not already that has a built in start delay circuit.

Hope this helps you if your still having trouble with this issue.

Posted on Jan 28, 2009

  • Wes Rackley Jan 29, 2009

    I would contact the manufacture, if it is actually needing the hard start capacitor to start every time then the equipment has not been installed correctly or it is defective and will shorten the life of the compressor. The hard start capacitor reduces the load on the start windings but does nothing for a high amperage draw on the run windings of the compressor. A high amperage draw can be caused by loose line voltage connections or wiring of to small a gauge to accommodate the current it is carrying to the compressor which causes undue strain on the windings not to mention it making your unit expensive to operate. In any case a hard start capacitor is a patch not a repair.

    Good luck.


×

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

2 Answers

Any ideas as to why the panel breaker for my Goodman CPE24-1AB heat pump would immediately trip when the air conditioner is turned on?


Without looking up the specifications for this heat pump, I cannot be certain, but I expect the operation to provide cooling may require more power than when heating. You probably can find the specifications online for this unit. As you probably know, power is measured in watts and is calculated by voltage times current. This also is likely to be 240 volts operation. If you take the specified power on cooling and divide by voltage (240), that will indicate the current in amperage that will be required to start it. Your circuit breaker is set for current and needs to be a higher current than is required. If that is the problem, you can buy circuit breakers at Home Depot or Lowes. You have to remove the front panel of your breaker box and snap out the circuit breaker. To be safe it would be good to turn off the main breaker switch before you open the front panel and remove the circuit breaker for the heat pump. Should your calculation of current required be less than the rating of the circuit breaker, that implies a malfunction of the heat pump in the cooling mode and would require a service call to the local representative of the heat pump manufacturer.

May 16, 2014 | Goodman CLQ36AR49 Air Conditioner

1 Answer

Grunaire unit trips breaker immediately when we try to reset it.


very likely a defective compressor. while there are other things that could cause the tripping, 90% of time it will be the compressor. generally, it will not be cost effective to repair the system if it is.

Jan 27, 2013 | grunaire GSI091HXB / GSU091HXB 9,000 BTU...

1 Answer

We have a 1999 "Thermal


DO NOT install a 20 amp breaker, you can cause a fire. The breaker is rated for the WIRES, and unless you change out the wires, the 15 amp wires will overheat and can cause a fire.
Typically, A/C units need dedicated power, with nothing else on that circuit.
One step that you may try is a new 15 amp breaker. Once a breaker starts tripping, is starts tripping earlier....
You may wind up running a new circuit for the A/C, if you do, size it for the A/C.

Jul 18, 2011 | Heating & Cooling

1 Answer

I have a heat pump/air conditioner that keeps tripping the breaker when I reset the breaker it soundss like it is sizziling is the 30 amp to small for the unit it is a 13 seer cooling system


Why would you ask about a breaker size?

Has it not been properly installed for the unit
& there for years with no problem?

You must know ,that you would need to see
the wiring diagram for the A/C unit, to check on
the required breaker Amperage

You need to call a service tech to troubleshoot
what has failed on the unit & is tripping the breaker

Bad Compressor or Motor,maybe

Jun 29, 2011 | Whirlpool Heating & Cooling

1 Answer

Heat pump cutting off and knocks out power to house.


Wow!.
Wires buzz where, What are the hooked into? On he heat pump? At the breaker Box?

I would have electric company check incoming pole lines & transformer. Was there a bad electrical storm in your area?

You may also have a bad Main breaker box, Is it out in the weather? Terminals may be corroded.

Pulling power from other breakers means you have a dead line or low voltage/amps on that line, Or a dead short That much power you should see welding & melting of wires.

Good Luck! Be very Careful. MSG me back let me know if i can help more.

Mar 11, 2009 | Goodman CLQ36AR49 Air Conditioner

1 Answer

Goodman heat pump 5 ton power problem


Sound like the outside unit is going to ground or the unit is over amping. Take and shut off the power to the unit and check all of the electrical connection for tightness. Don't forget to check the disconnect wires too since you shut it off at the breaker box. If you have a meter check to see if it''s live before you work on it. If it's all tight then call back the person that did the previous repair and tell them that he obviously missed something and the you feel that it should be a warranty call.

Dec 20, 2008 | Goodman CLQ36AR49 Air Conditioner

3 Answers

Heat Pump/Furnace Trip Circuit Breaker


My system will run for a short period and then suddenly trips the circuit breaker in the main panel for the heat pump.

I have a Goodman - 3 ton system about 8 - 9 yrs old. I'm being told that I need to replace the heat pump/air conditioner compressor?

What do you think?

Oct 22, 2008 | Haier Energy Star ESA3183 Air Conditioner

1 Answer

AC breaker trips after 10 minutes


Whats the amp breaker? Is this for the inside unit or the outside condenser? If the inside and gas heat you have a bad fan motor, If its an electric furnace , the same, but if its the outside unit, the fan could be going bad, locking up and the compressor still runs and pulls high ampsand tripps breaker or the compressor is just pulling too many amps due to plugged coils with dirt , grass or weeds blocking airflow.(koolbreezes74401@yahoo.com)

Jun 08, 2008 | Goodman CLQ36AR49 Air Conditioner

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

445 people viewed this question

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

paulcarew

Level 3 Expert

2028 Answers

Brandon Berry
Brandon Berry

Level 2 Expert

407 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...