Question about MGE Computers & Internet
GE LP33 UPS inverter failed to start
I have a GE LP33, 30KVA UPS. Here is the situation (problem), -Mains power goes off, generator failed to start, -UPS takes over the load for its backup time of 15 minutes, -power still not back, -UPS shuts down because its batteries are drained, -mains power is back, -UPS starts but inverter fails to start giving and alarm "inverter cannot be started. I was once able to clear this alarm and restart the inverter by completely shutting down the UPS; but this is not acceptable since it interrupts power to the load. Can anybody help figure out why this is happening? Is there any way to clear the alarm without completely shutting down the UPS? Your help is highly appreciated. Yared
    Problem Solver:
  • 16 Answers
Dear Yared,
Did you try to give the UPS some time to recharge the batteries?
Seems like the batteries have reached their cut-off voltage and are not supplying enough voltage to the inverter.
Normally the dc boos circuit of the UPS will supply voltage to the DC BUS so maybe the problem can be found in the dc boost circuit or BUS if recharging the batteries is not helping.
Let me know.
Best Regards,
Ron
Posted on Feb 02, 2013
  • Yared Abebe Feb 12, 2013
    Dear Ron, Thank you for the feedback. Yes, I have given the UPS enough time to recharge the batteries. I found that the battery charger fuse for the negative string of batteries blown. I have changed the fuse, however the batteries on the negative string side have lower voltages (12.1V) compared to the positive side (13.6V). I have decided to change the batteries; what do you think? Regards, Yared
I have a GE Lp33 30KVA ups. I just renew the batteries and the problem is when the main power goes off all the loads goes off as well.As if the ups is not giving any power.But when main is present everything stays on.I can read the load output current per phase and so on.This indicates the ups is working normally when main power in on. Any suggestion?
Posted on Feb 27, 2014
2 Suggested Answers
SOURCE: Problem with Compaq UPS T1000h
I had a problem like this one, check the voltage from the generator , if the output from the generator is to high (over 240 Volts european standard voltage), the voltage protection (VDR resistors ) will brake the fuse to protect your UPS.
and also check the frequency of the generator, it has to be very stabile around 50HZ (european standard frequency)
Posted on Sep 20, 2009
APC Smart VT 30KVA UPS cannot sustain power after power failure
ups units run a computer directly from mains power and from a battery when mains power is cut.
some run the computer through the battery at all times and so use the battery as a surge protection
points to check on your unit
is the by pass system being damaged in the surge protection section
is this requiring the batteries to provide power but not being charged at the same time
Is the power consumption exceeding the battery rating ( pc, printer, monitor , modem etc exceeding the out put of the ups
Apr 27, 2015 | American Power Conversion Corp...
Tip
UNINTERRUPTIBLE POWER SUPPLY
UPS – UNINTERRUPTIBLE POWER SUPPLY
Uninterruptible power supplies provide protection against mains power faults to computer equipment.
These faults include voltage spikes/interference, over voltage and under voltage, mains supply interruptions and surge protection etc.
These faults can cause computer and electronic equipment that are connected to an unprotected mains supply to malfunction and/or sometimes fail.
A common problem, when burning Cds, DVDs etc. any slight power interruptions to the burning process will halt the recording process and rendered the disc useless.
There two type of Uninterruptible Power Supplies
The lower powered and cheaper type UPS are switch-over types, when the mains supply fails, the UPS switches over to the batteries and inverter in milli-seconds which then supplies mains power to the computer and peripherals. A faulty inverter circuit and or flat batteries won’t deliver standby power when the mains supply fails.
NOTE : The mains waveform from these UPS is a pseudo sine wave (i.e. not a true sine wave).
The true UPS types are usually the higher KVA units (over 1500 VA) that supply continuous mains power. The mains power is connected to a charger which charges the batteries and then the inverter draws power from these batteries and converts it to true sine wave mains power to the computer equipment, therefore there is no switch over time lag when the mains supply fails.
on Dec 06, 2009 | Computers & Internet
Tip
UPS - Battery Fault
UNINTERRUPTABLE POWER SUPPLY
Batteries in the UPS typically last 3 to 5 years and it depends upon several factors. Including the number of times the unit must go on battery power and environmental conditions. There are usually several batteries in the UPS and while the battery voltage may show 13 volts, this may only be a float charge/voltage and a true indication of the battery voltage and condition requires the batteries to be tested under a load. If one battery is faulty in a set of batteries it will causes the whole battery system to fail and indicate a battery fault. A faulty charging circuit will not charge the batteries and will also cause a fault condition.
Lower powered and cheaper type UPS are switch over types, when the mains supply fails, the UPS switches over to the battery and inverter in milli-seconds which then supplies mains power to the computer and peripherals. A faulty inverter circuit and or flat batteries won’t deliver standby power when the mains supply fails.
NOTE the power waveform from these UPS is a pseudo sine wave (i.e. not a true sine wave).
The true UPS types are usually the higher KVA units (over 1500 VA) that supply continuous mains power. The mains power is connected to a charger which charges the batteries and the inverter draws power from these batteries and converts it to true sine wave mains power to the computer equipment, therefore there is no switch over time lag when the mains supply fails.
on Dec 02, 2009 | Computers & Internet
GE LP33 30KVA output power fails when main goes out
if INVERTER IS ON, WHEN MAINS GO OFF IF UPS FAILS AT THE SAME MOMENT YOU NEED TO REPLACE ALL BATTERY SET
Feb 27, 2014 | MGE Galaxy 3000 UPS System
In my home using 100AH battery for inverter , want to know wht happens if the baterry is not connected to inverter ? Is battery life decreases..? or WHAT ELSE WILL HAPPENS TO BATTERY ..? plz give an...
It depends upon the type of UPS.
A true UPS requires a battery to be connected to the inverter at all times. Mains power is used to charge the battery constantly and battery is required to continually supply power to the inverter which then converts the voltage to mains supply voltage.
A lower powered and cheaper type UPS areswitch-over types, when the mains supply fails, the UPS switches over to thebatteries and the inverter in milli-seconds which then supplies mains power to thecomputer and peripherals.
This type UPS may operate without a battery, but it depends upon the design of the UPS and the battery error detection system In most cases I doubt it can operate without a battery. You can try the UPS without a battery, make sure the battery terminals do not short against each other.
Dec 21, 2011 | Televison & Video
Can i have all the basic details of UPS system
UPS come in two types, lower powered cheaper types are usually switch over power.
These units senses a power outage and then switch over to the battery power to generate mains supply. The switch over occurs in milli-secs and does not affect the computer.
True UPS types constantly run off battery power to generate mains supply so there is no switch over time lag. These units are higher powered and higher costs units.
Both type of UPS have the same components.
Battery charger.
Batteries
Inverter that converts battery voltage to mains voltage
Electronic controls
Dec 16, 2010 | Emerson PowerSure Personal 500VA...
Hi I have a Tripplite 3636VR connect up with 3 X 200AH batteries in series. The inverter works fine when connected to city power, when the city power fails the inverter takes over noramlly, I then go and...
check the system but you may have to turn off the batteries
the inverter is charging the batteries but when mains power fails , the batteries will be discharging back through the inverter that is dc converted back to ac
if you power on a genset and the ac is not phased correctly, what you describe will happen--- inverter ac from the batteries against genset ac to the inverter-
If you had mains power on then it would dead stop the genset because of the out of phase situation
it all has to do with the 2 wave patterns for ac current from each unit being in harmony and not working against each other
Mar 19, 2017 | Tripp Lite PowerVerter APSINT3636VR UPS...
Dc bus faulty
Batteries in the UPS typically last 3 to 5 years and it depends upon several factors. including the number of times the unit must go on battery power and environmental conditions. There are usually several batteries in the UPS and while the battery voltage may show 13 volts, this may only be a float charge/voltage and a true indication of the battery voltage and condition requires the batteries to be tested under a load. There maybe one battery in a set of batteries that is faulty and causes the whole battery system to fail and indicate a battery fault.
These lower powered and cheaper KVA type UPS are switch over types, when the mains supply fail, the UPS switches over to the inverter in milli-seconds which then supplies mains power but the power waveform is a pseudo sine wave (ie not a true sinewave. A faulty inverter circuit won’t deliver power when the mains supply fails.
The true UPS types are usually the higher KVA units (over 1500 VA) that supplies uninterrupted mains power. The mains power is connected to a charger which charges the batteries and the inverter draws power from these batteries and converts it to true sine wave mains power therefore there is no switch over time lag from the mains to the battery.
Oct 22, 2009 | Powerware 9120 UPS System
Sir after changing the battery ups worked well one day and the next day onwards when i pressed the switch red and amber lights blinking and the upc trips with beep sound .kindly give the solution
Oct 16, 2009 | APC Computers & Internet
My ups is switching off itself immediately the mains goes off.the battery is okay with 13v.
Batteries in the UPS typically last 3 to 5 years and it depends upon several factors. including the number of times the unit must go on battery power and enviromental conditions. There are usually several batteries in the UPS and while the battery voltage may show 13 volts, this may only a float voltage and a true indication of the battery voltage needs the batteries to be tested under a load. there maybe one battery that is faulty and causing the whole battery system to fail.
These lower powered and cheaper KVA type UPS are switch over types (when the mains fail, the UPS switches over to the inverter in milli-seconds to supply mains power). It is a possibility the inverter circuit is faulty and when the mains power fails the inverter does not switch over.
The true UPS type are usually the higher KVA units (over 1500 KVA units) that converts mains power continuously via the inverter circuit. The mains power charges the batteries and the inverter drawing power from continuously from the batteries (therefore there is no switch over time lag from the mains to the battery.
Sep 25, 2009 | MGE Pulsar Ellipse 800 (89363) UPS System
Computers & Internet Logo
456 people viewed this question
Top MGE Computers & Internet Experts
Jax Planet
Jax Planet
Raj Patel
Are you a MGE Computer and Internet Expert? Answer questions, earn points and help others