Gmnt condensing gas furnace will not ignite and red ligh is on
5 Suggested Answers
  • 69 Answers
SOURCE: Furnace start buts shuts off
It sounds like you have an obstruction in the exhaust vent. Thats why when you bybass the pressure switch it runs ok. Steve
Posted on Dec 21, 2008
  • 80 Answers
SOURCE: furnace will not light. Igniter glows but no gas
Make sure that the switch on the gas valve is in the on position. If it is and the gas valves coming into the furnace are open, you probably have a bad gas valve.
Posted on Oct 04, 2009
  • 66 Answers
SOURCE: Goodman GMNT furnace - should I be able to get
Check the front of the unit and you should see 4 5/16 screws . I believe the outer 2 screws undo the top cover .Remove it first, and remove the inner 2 screws, and the lower door will come off. Good luck. Vern
Posted on Feb 21, 2010
  • 1033 Answers
SOURCE: Gas furnace with Honeywell smart valve code error
Hello, it sounds like your Furnace might be shutting off due to your high limit switch.A limit switch will open when the furnace overheats due to low airflow, . check air filter, clean blower wheel, and check to make sure the blower wheel is running at proper speed and not dragging sometimes cause by a weak capacitor. Anything that restricts airflow will cause a limit switch to open.
Posted on Mar 08, 2011
Why does the gas valve on my furnace fail to open after the igniter heats up?
gas valve should be getting 24vac from ignition module. if your getting proper power, then module is fine. check continuity of gas valve. valve maybe stuck closed
Dec 18, 2014 | Heating & Cooling
Arcoaire furnace ran out of propane and now wont ignite
Check along the gas supply line to the furnace and make sure there isn't a valve that is shut off. If you have a gas oven see if the ranges light and have gas. I'm assuming you've also turned on the gas supply at the furnace itself as well. Check that the furnace has electricity it won't be able to open the automatic valve let alone fire the igniter. My brand new furnace had a safety switch that went out 3 days after installation preventing it from lighting. You might contact Arcoaire about that. http://www.arcoaire.com/
Dec 23, 2013 | Ovens
Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...
Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
Oct 29, 2010 | Electric Circuit Breaker Kit for Furnace
My furnace tries three times then red light blinks once
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Your furnace has a diagnostic chart on the reverse of the lower panel incorporated in the wiring diagram. One blink tells you that it is a failure but wont tell you where to start looking.
Nov 27, 2009 | Goodman GMS90703BXA Heater
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
Nov 23, 2009 | Heating & Cooling
We have a dayton gas furnace model #3E463A. thought the control box was gone. got new one we furnace starts up the power goes on, fan starts no green pulsing light on control no ignition
When your furnace starts...the Ventor motor(exhaust fan) starts up....within a short time (seconds) the Pressure switch closes proving that the Fan is indeed running and the vent is not blocked...if this doesnt happen the furnace will not poweer the ignitor or fire at all....Check the vent pipe outside and look for obstructions or dirt on the screen inside the pipe...the condensate from the fuirnace may not be draining at all...due to plugged condensate drain lines...find this tube coming out of the furnace front...bottom of upper compartment usually , and pull it off the tap....if water starts coming out then your drain is plugged downstream of the furnace.
Oct 25, 2009 | Dayton Gas Furnace Heater
Goodman GMNT furnace goes into 'lock-out'.
The brain has to have constant verification of flame. If the burner ground is corroded then you will get the condition you prescribe.
Jan 08, 2009 | Heating & Cooling
I have a goodman GMNT gas furnace Propane it lights off I have a blue flame for about 3 seconds I hear a click on the circuit board and the flame goes out this is doing it constantly. could you please help...
Hi!!! If the flame turns on then off and on then you should change your flame sensor on the gas furnace..YEs flame sensor is shorted..The flame sensor is located by the valve burners it has one wire and is white..Good luck..
Jan 03, 2009 | Heating & Cooling
Dec 15, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen