I HAVE A DGAA070BDTB COLEMAN FURNACE, IT WILL LIGHT BUT FLAME DROPS OUT BEFORE IT REACHES TEMP ON STAT
Therinnaiguy
  • 1420 Answers
SOURCE: furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Posted on Nov 25, 2008
mrgrzz
  • 88 Answers
SOURCE: furnace blower not working how it should
first off buy yourself a honeywell stat, in my personal opinion lux stats are garbage, I have run into so many that are bad stats !!! but as far as your fan not shuting down, sounds to me like your fan center on your circuit board is bad and will not shut down the fan when needed, you will have to replace the circuit board, as the fan center is a part of the whole of the circuit board, hope that helps
Posted on Jan 20, 2009
farfield
  • 462 Answers
SOURCE: I have a Coleman furnace model number 7681-8171/b.
Short of being able to look at everything Its impossible to say exactly what the trouble is. Does the board have a blink code showing and a legend that says what this is? What fuel are you on NG or LP? What does the flame look like (if you can see it) IE a lot of yellow, Some orange and Blue...?. Did anyone else look at the system and the thermostat? Does it have AC or HP on it too?
The only 1 thing I may be able to offer is this. On your thermostat (if it is not electronic) there is a needle pointer that points to a number it should be around .4 to .7 if set to a lower number the thermostat will cut the unit off well before it completes a heat cycle.
Posted on Mar 11, 2009
  • 26 Answers
SOURCE: PROBLEM WITH COLEMAN DGAA070BDTB FURNACE KICKS ON
you have a bad ignitor or gas valve call your local heating repair company
Posted on Nov 02, 2009
keith91gmc
  • 52 Answers
SOURCE: New Trane XV95 furnace runs and stops nine
if it is a mechanical thermostat the heat ant. does that on cheaper digital tstats it is set by span and on better stats like honeywell model 5000,6000,8000 series you set the cycle rate. what kind and model number is tstat
Posted on Dec 19, 2009
I have a coleman furnace model 4066A656
Make sure your air filter is clean. Is the thermostat satisfied? or is the room temp. still below the thermostat setting? When ever you have to turn the power off and then back on to a furnace that usually indicates that the furnaces ignition control locked out. The first thing that I would try is cleaning the flame rod.
Mar 02, 2017 | Coleman Heating & Cooling
Pilot and burner light then gas shut off model 7900
How many degrees before it reaches desired temp, does it shut off? A thermostat is designed to shut the furnace off a couple/ few degrees before it reaches set temp. It has what is called a heat anticipater, which shuts the burner down, and lets the blower use the remaining heat from the heat exchanger to bring it up to desired temp making it more efficient. If it is more than a few degrees, replace the thermostat. You can jump out the red and white wires to confirm the faulty thermostat. If by doing this, the furnace never shuts down, until you separate the red and white wires. That confirms a faulty thermostat. Hope this helps someone.
Oct 06, 2014 | Coleman Propane Forced Air Heater...
The furnace will light up and the fan will blow but the flames cut out before my house reaches temp. i have the thermostat set at 70 and the house will not get above 55. i have tried turning the propane...
First, for those of you who might not know, "What is a flame sensor?" A flame sensor is a safety device. When your furnace's main burners ignite (light Up) the flame sensor picks up the heat from the furnace's main burning and says, "YES," and sends a signal back to the main furnace control board saying that it is OK to let the main burner stay on. Or if the main burners do not ignite, the flame sensor does not pick up the heat and says, "NO" to the main control board, Shut That Gas Valve and Main Burners Down! Thank God we have safety controls like the flame sensor. Most of the time, after turning your furnace's power off, you may clean the flame sensors with light sand cloth, emery cloth or steel wool. Reinstall the flame sensor and you are back in business! Over the years flame sensors can build up a light coating of burned-in dust and dirt. This insulates the flame sensor so that it doesn't sense the heat of the flame well enough, so by cleaning it you have almost restored it to its new condition. Seldom, but sometimes they do go out completely.
Dec 08, 2010 | Coleman Heating & Cooling
My honeywell t-stat reaches current temp setting and furnace kicks off...but within 1 minute the t-stat drops 1 degree and the freakin furnace kicks on! This can't be right as it has never happened with...
Your differential is set to close you can go into tstat and change differential setting. Your install manual for your thermostat will tell you how you can set 1.2.3 degrees differential
Dec 13, 2009 | Honeywell Electronic Programmable...
The furnace model# DGAA070BDTB will ignite then almost immediately go out it will the ignite again then go out then the blower motor will come on it will then try to ignite again with blower on til the...
Is the flame spreading all the way across the burners within 2 seconds? If not clean the flame tray. If it is and the flame still goes out, you have either a poor ground wire connection or the circuit board is bad. Keep your chin up and thanks for helping others.
Dec 11, 2009 | Coleman Heating & Cooling
My furnace will not restart after it reaches the desired temp, then drops below that temp. The on light flashes
If this is a gas furnace, the thermocouple is one likely point of failure. It could also be a clogged pilot light jet.
Nov 18, 2009 | Heating & Cooling
Wiring to bryant furnace/ac
your t-stat maybe now not talking to the furnace remove it temporarily to check
Apr 09, 2009 | Honeywell Electrical Supplies