I have a reznor V3 Tcore2 the pilot lights and the burner heats up but the air circulation fan doesnt kick on ?
5 Suggested Answers
Therinnaiguy
  • 1420 Answers
SOURCE: Laars boiler pilot light is blown out when burners shut off
Time for a cleaning and gas pressure test.
Posted on Dec 05, 2008
  • 26 Answers
SOURCE: Pilot goes out after heating cycle
Check regulator on the unit.
Check pilot unit on the heater
use soapy water to check for leaks if see bubbles turn off main gas supply valve.
always turn off gas supply before any checks or repairs are made
when all else failes call your local gas provider to check heater and gas supply
Posted on Dec 16, 2008
  • 80 Answers
SOURCE: my goodman gas furnace is not kicking on. the
If you are not getting any codes from the board, then the furnace is not getting a call for heat from the thermostat. A wire may have come off, the thermostat not properly wired, or a break in the stat wire. On a call for heat, you should have 24vac between W and C on the circuit board. This will let you know if you are getting a call for heat all the way back to the furnace.
Posted on Oct 07, 2009
billyvangogh
  • 108 Answers
SOURCE: pilot light goes out when burner kicks off
Sounds like the pilot is dirty....when dirty it gets smaller and lazy...tends to go out easy...try gently tapping it with a screwdriver...make the pilot bluer and bigger....when it's dirty it has yellow tips or yellow completely , the pilot should fully envelope the thermocouple as well
Posted on Nov 01, 2009
I have a reznor heater in my garage I have to keep lighting the pilot it wont stay lit.
i have an ole reznor in my garage been workiing for ten + years no problems , mine is gas , the pilot light does go out after it switches to main burner like ten seconds later , but does light back up when thermostat shuts main off ( i had to go look to make sure) not a real big flame maybe like an inch or so , has a spoon shaped air shield around it , maybe yoours is missing ?
Mar 02, 2015 | Heating & Cooling
Reznor Heater UEAS 260 not heating
Check your igniter. If the furnce does not light it will do that every time.
Dec 09, 2013 | Reznor 205895 CC2 Vertical Vent Kit for...
I have a Reznor heater that hangs from the ceiling. I can lite the pilot, turn the t-stat to call for heat, it fires up, and will run as long as it calls for heat. When it reaches the set point, and shuts...
Check pilot is not blocked may needed cleaning out it sounds like the pilot is lifting off when the burner is on and when it gets to temp it shuts of as pilot may not be there , also check thermocouple is tight , or flame sencor is clean ( if fitted )
Mar 09, 2013 | Heating & Cooling
Brivis Upflow/Downflow fan on continuously, no heat
depending on the year of the unit
if its between 1992-1999 it would be caused by the either the pilot not staying alight, or a faulty gas valve not opening,
These models start the fan on a time delay not tempreture so you will only get cold air circulating and when the thermostat is off the fan will stop.
(All models) if the fan is running regardless of the thermostat position an over heat sensor is faulty.
May 17, 2010 | Heating & Cooling
I HAVE A RUUD SILHOUETTE GAS FURNANCE. The pilot light keeps blowing out. When I light the pilot flame it seems to work perfectly at ignition. As the Manual instructs, I hold down the ignition switch for...
Short answer, yes. However you could have another problem. Replace the thermocouple that keeps the pilot lit. You can get a universal one at any good hardware or farm store. Make sure the new thermocouple is well into the pilot flame. If the blower knocks out the pilot flame again, I would be suspecting cross contamination from a crack in the heat exchanger. As the exchanger heats up, it may be causing a small crack to open and allows the blower to extinguish the flame. It may also be causing a leak of Carbon Monoxide into the heated room air. I would get it checked out very quickly.
Mar 07, 2010 | Ruud UBHC Air Conditioner
Just replaced idnitor and flame sensor on a bryant model 376c and its still not kicking on. blower kicks on fans kick on and then cycles off. no heat need help
Make sure all wires are connected and the gas is on. Follow the sequence of operation for this model and a few tips on what could be the issue.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 27, 2010 | Heating & Cooling
Gas heater won't ignite
I agree. Either the pilot flame is dirty and is not making good contact to heat up the bi metal strip on the pilot assembly, or the pilot assembly is defective. 90% of the time if you clean the pilot orfice and the pilot burner it will take care of the problem
Nov 16, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Pilot light goes out when burners kick on burnham
Get a toothbrush and clean the **** off the pilot, could be partially blocked. Change the safety thermocouple. Check the plenum for cracks. A cracked heat exchanger can cause this.
Nov 07, 2009 | Goodman GMS90703BXA Heater
I have a Ruud deluxe 80 plus heater. The unit is running, the pilot light is lit, still no heat.
repost with more specific . motor aka fan is running?stat is set to heat and max heat? how old? general progression is as follows. stat says its cold. signal is sent to gas valve to open. gas valve looks to see if pilot is lit via thermocouple. if pilot is lit then main valve opens and burner lights. shortly thereafter sufficient heat builds up to trip heat sensor that turns on fan and blows hot air into house.many times a tripped safty causes a default fan response. aka when you show up the fan is on 24 7 . that equals a failed safety and needs a pro tech to see why saftyfailed.
Oct 18, 2008 | Ruud Heating & Cooling
1986 Weathermaker SX 150 series, model S85X060-CC-1
There are 4 -steps for full run time to kick in a furnace.. step-1, inducer fan runs & prove thru the air tube which closes a switch and tell the circuit board to go to step-2, the igniter lights the pilot & prove its lit by heating the thermocouple, which tells the circuit board to go to step-3, opens the gas valve to dump gas in, which will light from the pilot light, and prove by a flame sensor metal stick on the last burner , which heats up and tell the circuit board Saying, ok , I've got flame.. step-4. when the box heats up, it closes a switch and turn on the main fan...! (Some gas-valves has a brain -or circuit board on top of them and are real sensetive to moisture..)
Sep 05, 2008 | Heating & Cooling
Heating & Cooling Logo
318 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen