SOURCE: The LED indicators on my Lutron Maestro
1) If this installation was working before, the Maestro has a small pull-out circuit breaker that lets you reset the device. This is called the FASS Front Accessible Service Switch, located at bottom of dimmer where it meets cover plate.
Open sample Lutron Maestro dimmer manual to see FASS illustration
http://www.lutron.com/TechnicalDocumentLibrary/0301106A.pdf
2) If this is new installation, then double-check your wiring and check that load matches dimmer capacity: 600 watt incandescent or halogen, which apparently excludes CFLs.
Some electronic devices have shortened lifespan on circuits that are not clean. Use circuit analyzer on nearby outlet that is on same breaker to see if line has interference.
3) Lutron has customer service numbers:
1.888.LUTRON1 (588.7661)
1-800-523-9466
Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, expert speaks with you over phone while you work on dimmer or any do-it-yourself project.
Fixya is always less expensive than a service call.
Posted on Feb 03, 2011
4 ways are on and can not get them off?
The 2003 Softail TSM/TSSM's turn signal feature provides for Automatic cancellation; Manual cancellation; Four-way flashing and Diagnostics mode.
Turn signals can only be activated or deactivated with the ignition key in the "IGN" position, not the "ACC" position.
If you press the left or right turn switch the signal will activate both the turn signal operation/illumination and the automatic cancellation function. If you press the button a second time the signal will cancel. Also if you have one signal on and you press the opposite signal switch button the first set signal will cancel and the second pressed side will operate. However if you do not press the signal switch button the second time the signal will remain on and will not cancel while you are approaching the turn but will only automatically cancel after the TSM/TSSM senses that the turn has been completed because when the signal switch button is depressed the TSM/TSSM starts to count to twenty after which it will cancel the signal function if speed is not reduced below 7 MPH but as long as the speed of the motorcycle is above 7 MPH or is stopped the signals will not cancel until speed is resumed to above 8 MPH at which time the 20 count will resume and the signal will cancel after the end of the 20 count. The signals will also cancel within two seconds after the bank angle sensor in the TSM/TSSM senses more than a 45 degree lean of a turn action after which the motorcycle returns to a normal upright riding position. As well the TSM/TSSN will calibrate itself after it senses that he motorcycle has been ridden for one quarter of a mile or four tenths of a kilometer at steady speeds in an upright position. ON
The TSM/TSSM also flashes the signal simultaneously as four way flashers whenever the ignition is set "ON" , the security system is not activated and both signal switch buttons are simultaneously depressed. If you have to leave the motorcycle where it is with the four signal lights flashing they will continue to flash for two hours if while they are flashing you turn off the ignition switch and activate/arm the security system but if you turn the ignition switch is turned on, disarm/deactivate the security system and depress both signal light switch buttons simultaneously the four lights will cease to flash before the two hour period is up.
An auto arming feature that is not always active on domestic motorcycles but is user selectable on these models but that is always active on HDI models Auto-arming requires that the four-way flashers be activated within 30 seconds of key OFF or after the vehicle has been disarmed. This allows a vehicle to be left in a secured state with the four lights flashing until they are turned off as described above.
If the four way flashers are not turned of before the security system is disarmed/deactivated then the TSSM will stop four way flashing for one second and then per flash the lights one time to signal that the system has been disarmed/deactivated and then after one more second the four way flashing will resume.
When there is a burned out light bulb on one side of the motorcycle, the remaining light on that side and the turn signal indicator light on that side will flash at double the normal rate after the fifth flash so if that happens check your signal light bulbs.
As the TSM/TSSM also diagnoses for signal wiring short circuits and opens AND for stuck signal light switches if there is a stuck turn signal light switch the automatic turn signal cancellation feature will not work and the signal will continue to flash AND if there is a stuck turn signal switch the four way flashers will only be activated if both of the turn signal switch buttons are held in for more than one second so if the four way flashers are on when a signal switch becomes stuck you may have to hold them in for a longer period of time to cancel them also.
Otherwise if you are having turn signal or four way flasher problems you should check for TSM/TSSM trouble codes.
Jul 11, 2014 | 2003 Harley Davidson FLSTF Fat boy
ERROR CODE 61
If you have Zanussi washing mashine
To enter diagnostics:
  1. Switch off the appliance
  2. Press and hold down START/PAUSE and any one of the option buttons simultaneously
  3. Holding down both buttons switch the appliance on by turning the programme selector one position to the right (clockwise)
  4. Continue to hold down the START/PAUSE and option buttons until the LED begins to flash (at least 2 seconds)
In the first selector position, the operation of the buttons and the relative Led's is checked; turning the selector knob clockwise activates the diagnostics cycle for the operation of the various components and displays any alarm conditions.
Apr 21, 2014 | Washing Machines
I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye
Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Nov 29, 2011 | Goodman Heating & Cooling
I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help
Oct 28, 2011 | Goodman Heating & Cooling
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
Feb 03, 2011 | Goodman Heating & Cooling
Code 991 continues to show.. will not clear... how do we clear that code???
to clear the 991 Takagi code, simultaneously press the bottom 2 grey buttons of the four just to the left of the flashing LED light. When the LED stops flashing, release and then press the reset button on the black panel about 8 inches above that
Jan 17, 2011 | RTO Takagi T-M1 Mobius Gas Tankless Water...
My central heating is on lockout and the burner is with red light
A sampling of various codes on a furnace
Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Dec 02, 2010 | Heating & Cooling
Philips 20PF4121 LCD tv no picture but flashing error codes
I had exactly the same problem When the TV was switched on all I could see was a flashing green light. After cheching the TV internals and not seeing a problem including the power supply unit which looked and checked normal. Here is what I did to get M TV working again.
Disconnect it from the power supply. Hold down all the buttons simultaneously i.e. the on/off, the volume, the programme, menu buttons, all of them simultaneously and Plug it into the power supply again.
Lo and behold My TV jumped back into life after an absence of about 4 weeks.
Try it yourself exactly as above.
Best of luck.
Irishfreethinker
Jul 09, 2009 | Philips 20PF5120 20 in. EDTV-Ready LCD...
Blinking panel lights
To Calibrate , start and warm engine to normal operating temp. with engine idling turn blower switch to high, turn mode switch to panel, open all outlets, move temp lever to full cold.
press and hold rear wash and rear wiper buttons simultaneously for 5 seconds (untill all leds illuminate.) all leds should light up for 5 seconds, rear wiper and intermittent rear wiper button leds will flash alternatly during calibration... after 60 seconds if only rear wiper button led is flashing, cal. is complete
Jun 18, 2009 | 1998 Plymouth Voyager
1999 f150 airbag light stays on after blinking upon start up!
Passenger Air Bag Deactivation (PAD) Switch
The passenger air bag deactivation (PAD) switch:
  • is located on the instrument panel to the right of the climate controls.
  • contains a light emitting diode (LED) that indicates when the PAD switch is activated (passenger air bag disabled).
  • allows the passenger air bag deployment circuit to be disabled using the ignition key.
  • should be used whenever a child safety seat is being used in the front passenger seating position.
Prove Out the System
Prove out the system means to turn the ignition switch from the OFF to the RUN position and visually monitor the air bag indicator with the air bag modules installed. The air bag indicator will light continuously for approximately six seconds and then turn off. If an air bag supplemental restraint system (SRS) fault is present, the air bag indicator will either:
  • fail to light.
  • remain lit continuously.
  • flash.
The flashing might not occur until approximately 30 seconds after the ignition switch has been turned from the OFF to the RUN position. This is the time required for the restraints control module (RCM) to complete the testing of the SRS. If the air bag indicator is inoperative and an SRS fault exists, a chime will sound in a pattern of five sets of five tone bursts. If this occurs, the air bag indicator will need to be repaired before diagnosis can continue.
Active Commands
This command allows the technician to verify operation of the air bag indicator, passenger air bag deactivation (PAD) lamp and chime. When the air bag output command is executed, the indicator, the PAD lamp, chime and the chime are activated simultaneously for approximately four seconds. All devices are deactivated automatically.
Jan 15, 2009 | 1999 Ford F150 Regular Cab
Maestro Lutron  Dimmer 600 Watts Ma-600-wh Logo
Top Maestro Electrical Supplies Experts
jdthefixer
ken skalski
Are you a Maestro Electrical Supply Expert? Answer questions, earn points and help others