Troubleshooting guide for goodman furnace model GUPI075-3 operating cycle
The exhaust blower starts, but the pilot igniter does not cycle
SOURCE: goodman ac/gas furnace unit mdl. # gmp075-4
i HAD THE SAME PROBLEM, TURNS OUT IT WAS THE FLAME SENSOR, CLEANED IT, AND ALL WAS GOOD
Posted on Dec 13, 2007
  • 4 Answers
SOURCE: Fix for coleman rv furnace
Check all limit switches and check power to gas control
Posted on Jan 06, 2009
machtcl1
  • 61 Answers
SOURCE: Goodman furnace GMPN080-4 Getting 4 RED blinks/Open Limit Swtch
You have a limit switch located in the furnace (a little bigger than a dime and located near the center of the front panel, sometimes the switch is mounted to a small fiberglass board) . There will be two wires going to it. They sometimes trip so often that they fail to automatically reset(due to dirty filters or undersized ductwork). You can SHUT OFF POWER TO THE FURNACE, then remove the two screws holding the switch in the furnace, pull the switch out of the furnace and tap on it and wipe it off.
The switch may work a few more times but should be replaced with the same size and type. You will see some rating printed on the switch somewhere. Write down all the numbers and get a replacemet from a furnace/AC supply house. If you have a meter and know how to use it you could check the switch for continuity.
Sometimes just a tap on the switch will get it going. There will also be a couple of rollout switches that could be tripped. They have little buttons on them to reset them. If they trip it may have other issues to be solved.
Hope this helps!
Matt
Posted on Feb 01, 2009
  • 189 Answers
SOURCE: Goodman Model GMNT100-4 Auto Power Down and Up until Temp.
Keep in mind all furnaces and circuit boards are not the same. Look on the back of the door to the blower compartment. You should find the list of diagnostic codes. Look up four blinks it should narrow down the problem. Although from the discription you gave it sounds lie the high limit control. When a high limit appears to be acting up it DOES NOT mean that the high limit needs replaced. The high limit just may be doing its job. This means that the furnace is overheating. Check your filters. Are all of your registers open? Is your blower set on the right speed? Is your blower going bad? Is the blower motor capacitor bad? Is your evaporator coil restricted? Just changing a high limit switch does not always solve the original problem!
Good luck....
Posted on Apr 03, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Hello I have a goodman gas furnace
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Posted on Oct 18, 2009
Furnace tries to light but misfires
Check the air filter.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 26, 2010 | Goodman Heating & Cooling
Thermostat calls and from time to time won't ignite
I would first look at any wire connections both at the furnace and the thermostat. Then I would replace the thermostat. Check the units control board when it does not start for an error code. There should be a small viewing port to look into the furnace cabinet to see the control board.
Feb 12, 2010 | Goodman Heating & Cooling
Goodman model gms8 will not light fan comes on then turns off
Jan 26, 2010 | Goodman GMS80453ANA Open Flame Mid-Size...
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
Jan 26, 2010 | Goodman Heating & Cooling
My gas goodman heater will not ignite.
It is probably not the glow coil, if this is a 80% regular
furnace, Make sure the induced draft blower is working. I once went to a house where I came across
this problem, the only difference is that it would acutually start and then shut off. I took the vent apart
at the furnace and found a bird that was preety cooked.
If this is a90% High Eff. furnace, make sure the pvc
vents are not plugged. To troubleshoot the intake
Vent. Remove the combustion plate and then turn
the unit on, if it runs you have a problem with the
intake vent.
You could temp. remove the exhaust vent and then turn on the power if it runs then your exhaust vent
is probably plugged. You could go outside and make sure the vents are free.
Make sure you have gas available, these are the most commom issues that could solve your problem
Jan 14, 2010 | Goodman GMS90703BXA Heater
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
The exhaust blower starts for about 15 seconds then shuts off. several minutes later, the same thing happens - over and over
goodman furnance the exhaust fan starts, igniter glows hot, all burners lite up & will burn for about a minute and shuts down . I think it senses the room blower does not start so it shuts down.
Oct 20, 2009 | Ruud UBHC Air Conditioner
Oct 18, 2009 | Goodman Heating & Cooling
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater
Ignition failure after three attempts then sits for an hour.
try cleaning the burners and or adjust the distance the igniter is from the actual burner .
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater
Heating & Cooling Logo
270 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Tim Whalen