Furnace continues to short cycle over and over and over...
Call for heat. Inducer starts. Than igniter glows. Than burner lights. Than blower comes on. Then after one minute. Burner goes off. Than blower shuts off. Inducer is still running. After 30 seconds igniter starts again. Total time is 3 to 4 minutes. Over and over and over..
  • Heating & Co... Master
  • 2,602 Answers
It could be two things flame sencor needs cleaning of conections not tight or the pressure switch is not working try jumping it out and see if it lights
Posted on Jan 15, 2013
  • 579 Answers
SOURCE: Dayton 3E227A Heating Cycle
The sensor for the thermostat is probably going bad or has bad connections. It is (or thinks it is) heating up fast and therefore shuts of the heater.
Posted on Dec 31, 2007
  • 17 Answers
SOURCE: weatherking furnace is starting and stopping
This just sounds like a couple of problems. First, your blower is designed to only turn on once the heat exchanger heats up, so the flame will be on for a minute or two before the blower starts. it sounds like your blower is cooling down the heat exchanger too fast and causing it to shut off so it can warm up again...check blower speed for heat, it should be the lowest speed (black wire). Blue=medium speed, red= high speed. second problem could be your flame sensor rod is calcified, you just need to locate this and clean it off with some fine sand paper.it is located in the flames near the burners. Also change your filters, for proper air flow through your heat exchanger.
Posted on Oct 28, 2009
  • 89 Answers
SOURCE: Coleman Presidential II Model 7656A Mobilehome Furnace blower p
have you changed t-stat? if so you need to increase the heat anticipator. if you have a fan limit switch, the setting may need adjusting. Thay will change with age
Posted on Nov 01, 2009
  • 26 Answers
SOURCE: goodman furnace, inducer blower comes on, but
In the burner compartment opposite of the ignitor is the flame sensor. seems to be dirty. one screw holds it in. Remove and clean with a wire brush.
Posted on Nov 21, 2009
heatman101
  • 43501 Answers
SOURCE: Burner ignites and goes out (Goodman Gas-fired furnace)
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Posted on Dec 24, 2009
My York furnace sometimes doesn't completely ignite
A noisy inducer probably is headed for replacement.
The igniter can produce a healthy glow and still be defective. Mine had to be replaced with a new, improved one.
The thermocouple could be defective even though it seems to open the gas valve when it should.
The heat sensor in the bonnet could be defective. That controls main blower operation.
The heat exchanger could be cracked.
Jan 10, 2014 | Heating & Cooling
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
Mar 05, 2010 | Goodman GMS90703BXA Heater
80% ducane furnace makes several attempts to ignite then shuts down. glow stick lights but no ignition to main burners. any ideas?
Check for 24 volts across the gas valve terminals!
Mar 04, 2010 | Heating & Cooling
Glow bar starts, gas valve opens, gas start burning in all four ports, glow bar turns off and gas valve closes. no flame roll-out is it the board bad?
Depending upon how long the burners stay on it could be a bad or dirty flame rod, read on.
Jan 16, 2010 | Goodman Heating & Cooling
Red light blinking continuosly meanig gas valve relay short how can I fix myself - furnance only blows cold air
You will need to check for 24 volts AC to the gas valve after the igniter starts sparking or glowing. If you have it but it does not open, bad gas valve and you will need to replace it. If you are not getting 24 volts after it starts glowing or sparking, you have a bad board.
Jan 16, 2010 | Heating & Cooling
I have an americanaire ultra sx 80 furnace that if it does start up the 1st time, the induction motor continue to run and it will not start
Jan 04, 2010 | Heating & Cooling
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
Nov 23, 2009 | Heating & Cooling
FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
HEIL 80% furnace T-STAT calls for heat, Inducer runs and nothing else happens, Ohm meter reads 4.9 on ignitor. MDL#NTGM100EHA2....Any help with this?
Nov 03, 2009 | Heating & Cooling
Heating & Cooling Logo
217 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen