Have a 1992 goodman/janitrol gas furnace. Fan will turn on... gas burners turn on for 6-10 seconds and shuts off for 15-20 seconds and repeats cycle.will not hit the desired set t-stat temperture.The
M# GUPS100-3
Therinnaiguy
  • 1420 Answers
SOURCE: Honeywell Gas Furnace
A Make and Model number of the furnace not the thermostat will help but I can walk you thru the operation of a typical furnace. It sounds to me that the burners are igniting properly but the flame sensor is not sensing the flame and shutting down the system. You will need to find the sensor and clean it and check the wire from it to the control board. Typically, the flame sensor is found at one side or the other of the burner box. It is a small probe that the flame hits. Depending upon your model it may have a small wire attached to it leading back to the control. Or it may be part of your auto-pilot assembly. ? At any rate, you will need to get to it and very delicately brush it off. Then inspect the flame channel. This is a trough area where the flame travels to ignite all burners. Over time, they tend to fill with rust and debris. Take a small screwdriver and run the blade down the trough. Inspect the wire that goes from the flame sensor to the control board. Make sure it is not frayed or broken or shorting out and that the connection at the board is good.
Beyond that, it's time for a technician to come.
Let us know the Make and Model of the furnace (found inside the furnace cabinet) and maybe we can help you further.
Posted on Nov 20, 2007
JetJedi221
  • 25 Answers
SOURCE: The furnace burners won't stay lit
Could be a couple things. First and easiest is to check your intake combustion air supply. If it is blocked by anything or just not enough flow, it will put out the flame. Next would be the flame sensor, usually a temperature probe near the flame front. If it's not reading an increase in temp within a pre-programmed time, it will kill the flame. It can be checked with a multimeter.
Posted on Jan 25, 2008
SOURCE: Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Posted on Jan 06, 2009
  • 2920 Answers
SOURCE: Furnace fires for 10 seconds then cuts off
have the thermocoupler checked
Posted on Jan 17, 2009
  • 69 Answers
SOURCE: Goodman furnace seems to be cycling too often.
dIf the burners are only staying on for about 5 seconds, you proably hav e a dirty flame sensor. Watch the burners light, the glow plug will light one end of the burners, in front of the last burner to light the will be a small thin rod, this rod must sense the flame or the gas will be shut down. Take a piece of steel wool and gently cleqan the rod.
Posted on Oct 11, 2009
What's wrong with my furnace?
The relay for the motor is stuck or the points inside the relay are arced closed. Replace the relay.
Apr 26, 2016 | Goodman Janitrol Amana Goodman Janitrol...
Goodman furnace a36-20 fan runs non stop
is green wire from thermostat or from outdoor. retrace and change as needed. If not Goodman has a tech support number you can call while looking at unit.
Jun 21, 2014 | Goodman Heating & Cooling
Goodman Dependable Janitrol Ninety-two furnace starts but shuts off before blower runs
it is reaching it's temperture limit berore fan cycles on. control issue
Oct 23, 2013 | Goodman Heating & Cooling
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
Thermostat calls for heat, purge motor turns on, 15 seconds later hot igniter turns on, then gas turns on and burners are lit. Problem is, they only stay lit for 5 seconds then shut off and cycle repeats...
,Hello, Make sure the flame sensor is clean near the burners, The flame sensor is a metal rod that is on the opposite side of the ignitor. To clean the flame sensor you will need some steel wool, turn off power to the furnace and remove the flame sensor and clean it with the steel wool. After cleaning reinstall it and turn power back on to furnace.
Mar 02, 2011 | Goodman Heating & Cooling
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Furnace will not keep the gas burning.
May be your flame sensor on the right hand side of the burner assembly. You will need a 1/4 inch nut driver to remove it and then take a brass brush and clean off the sensor
Dec 15, 2009 | Heating & Cooling
I have outside Goodman-Janitrol furnace and air unit and
two things to try first to get you pointed in the right direction. First disconnect the R or RH wire from the T-Stat. If the furnace turns off (Stops firing w/ fan to turn offabout 90 sec. later) then you more than likely have a bad Thermistat. If it continues to run Pull the R wire from the Furnace circuit board. put door back on furnace if it stops you have a short in the wire. Still Running? Most likely a bad curcuit board. Hope this helps.
Oct 12, 2009 | Goodman GMS90703BXA Heater
Goodman furnace seems to be cycling too often. Burner not staying on long enough to put warm air into system. Burner quits after a few seconds then repeats.
Oct 11, 2009 | Goodman GDS80904BNA Open Flame Heater
Goodman gas furnace
Sounds like it coud have been a flame sensor. the limit switch is usually near the top of the heat exchanger.
Nov 02, 2008 | Goodman Heating & Cooling