Question about Aprilaire 700 Humidifier
Aprilaire 700 Only works in test mode;
Installed an Aprilaire humidifier model 700 with a model 56 Humidistat Wiring is: correct, verified several times. Both Outside and inside sensors read okay. HH goes to Humidifier (24VAC when unit is plugged in) RC go to furnace W and 24 VAC common) and reads 24VAC when furnace is running, ODT go to outdoor sensor Plugged in the unit to 110 and both the Green and Red lights came on briefly then turned off. Dial set at 7 outside temp is 24F Humidifier only runs when in the test position with either outside or inside resistor and in auto or manual mode. Could the model 65 circuit board be bad? How to verify? Any assistance appreciated
  • Grumpywun Jan 15, 2013
    I read on a post to use a hair dryer and blow on the thermostat. I did this and the humidifier worked one (1) time but has failed to come on since. The water solenoid is good and energizes and denergises. When energized water does flow and exits the drain hose. I have used the manual mode with the internal resistior and the unit still does not operate on a continuous basis. Hunidity in the house does not seem adequate (do not have a means to measure) but the house still seems dry to me. Any additional help is appreciated.
  • Grumpywun Jan 18, 2013
    Problem Solved: Thanks to all who contributed. Solution: Unit was wired correctly, and ran after using hair dryer on thermostat board. Reason humidifier would not run is: I have a high efficiecy furace and it appears that it was inducing humidity into the air from the outside intake and the condensation humidified the air satisfying the set humidity level on the humidistate.
2 Suggested Answers
  • 232 Answers
SOURCE: Water only runs with humidistat in test/reset mode
you need to make sure your humidity level in the house isnt higher then what your humidifier will provide at any givin outdoor temp. this chart is in the owners manual. you cant remove the wires going to the ODS or it will give an error unless you have a resistor to put in its place. Anyway if the humidifier works in test mode according to AA it works so you may have higher humidity than you think, the highest your gonna get is 45% as the temp outside drops it will allow less humidity so it doesnt cause window condinsation (property damage) here is a copy of the chart. the #s on the left are the dial setting
TABLE 2 – % Relative Humidity Guide
Outdoor Temperature (°F)
-10°F 0°F 10°F 20°F 30°F 40°F
10% 10% 10% 15% 20% 25%
2 10% 10% 15% 20% 25% 30%
3 10% 15% 20% 25% 30% 35%
4 15% 20% 25% 30% 35% 40%
5 20% 25% 30% 35% 40% 45%
6 25% 30% 35% 40% 45% 45%
7 30% 35% 40% 45% 45% 45%
Posted on Nov 29, 2009
Aprilaire 760 keeps running
Is this a newly installed unit it sounds as if there's a wiring issue. Could you show a picture of the wiring terminals. If this is not a new install try turning of your furnace fan.
Nov 02, 2014 | Aprilaire 700 Humidifier
I have a aprilaire 700 I just installed on return plenum. Have a problem with the wiring, the instruction say to connect the R&C wires from humidistat to the same on furnace power strip. Is the C
Depending on the age of your furnace you may have an aux terminal for a humidifier. If not, you should use the white wire (heat) coming from the homes thermostat to power up the humidistat and ultimately bring on the humidifier. This way it will only run when in heating mode.
Nov 16, 2012 | Aprilaire 700 Humidifier
No "C" on furnace power strip for humidifier power "C"
Hello, since this humidifier has a transformer installed with it, you bring one wire from humidifier to Humidistat and then a wire from humidistat to Transformer. You will need a current sensing relay to turn the humidifier on and off with the Furnace cycle. I will attach a link for a wiring diagram for your Humidifier http://docs.electronicaircleaners.com/aprilaire_700a_installation.pdf
Nov 15, 2012 | Aprilaire 700 Humidifier
I have an Aprilaire 700 humidifier and it won't come on. It has been in the 20's and it worked fine. We then had a couple days in the mid 30's, and it stopped working. I put the humidistat to test and it...
Did you get the plug back together. And did you plug it back in. Also make sure the Humidistat is set right. Here is site that might help you. Hope this helps.
http://www.aprilairehumidifierparts.com/aprilaire_humidifier.php?model=700&gclid=CLy4zffHnKYCFVZc2godEC51nQ
Test the humidistat-- by taking one of the wires off one of the screws, and touching it to the other-
Does the unit come on?-- Then possibly the humidistat is bad.
Let us know what you find
Mack B
Jan 20, 2011 | Aprilaire 700 Humidifier
Loud clicking and banging, A700 doesn`t work
You have a faulty humidistat
Greg Sunsetmech
Dec 13, 2009 | Aprilaire 700 Humidifier
Aprilaire 560 will only click and flow water when turned to "test" does not work in any other settings?
Humidity must be hi enough in the house or Humidistat is not working. Do you any way to check humidity in the house?
If the Humidistat is set as Automatic, try to leave it as Manual.
Dec 03, 2009 | Aprilaire 700 Humidifier
Aprilaire 700 only works in test mode.
connect two wires at humidifier without any wirng connected if works problem is in wiring or humidistat
Oct 28, 2009 | Aprilaire 700 Humidifier
Aprilaire 700 Humidifier not working. Can it be repaired?
turn the humidistat back up, aand make sure if is still wired up.
Jan 18, 2009 | Aprilaire 700 Humidifier
Aprilaire 700 operating at wrong time
You want the humidifier to run in heat mode which is the r-w1 terminal on the stat.
Nov 17, 2008 | Aprilaire 700 Humidifier