58STA070---12112 furnace. Not working, three flashing lights means "reversed polarity" . Furnace has been running for 7 years with out a problem. Replaced igniter, and this did not work. ANy ideas
  • 80 Answers
SOURCE: furnace will not light. Igniter glows but no gas
Make sure that the switch on the gas valve is in the on position. If it is and the gas valves coming into the furnace are open, you probably have a bad gas valve.
Posted on Oct 04, 2009
gear001
  • 59 Answers
SOURCE: reverse polarity
Its a simple fix. Follow the cord that plugs into the wall into the furnace. Or if its hard wire, follow the romex wire that goes into your furnace. Inside the furnace, switch the white and black wires that connects to the power cord. www.fastacservice.com
Posted on Oct 18, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: my furnace tries three times then red light blinks once
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Your furnace has a diagnostic chart on the reverse of the lower panel incorporated in the wiring diagram. One blink tells you that it is a failure but wont tell you where to start looking.
Posted on Nov 28, 2009
heatman101
  • 43501 Answers
SOURCE: Coleman furnace -- fan runs, ingniter won't light,
The chances are that the furnace was running when the power went out. This will cause the high limit switch to cutout and needs to be manually reset.
You will find that switch in the blower compartment near the blower. Usually somewher near the highest point of the cabinet.
Push the little red button firmly till it clicks.
When the power goes out while the furnace is running the heat builds up because the blower shuts down immediately and causes this limit switch to cut out.
If you have a electric tester you can also follow the low voltage circuit till you find the open switch. Ther is usually a wiring schematic on the door cover of most furnaces.
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Posted on Dec 09, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: 3 flashing light....Aire-Flo furnace AF80MPA100B5A
That control board is several hundred dollars. If I may make a suggestion, take a jumper and when the inducer fan starts, jump out the pressure switch. If it starts, it's not the board but a bad switch, hose or blocked exhaust vent.
Posted on Jan 15, 2010
Bryant plus 80 furnace no fan/ operation , yellow constant flashing light code , power to furnace was rerouted during remodel and since then furnace stopped working. Any suggestions ?
You need to have/ know the "fault code" chart for that specific furnace. Count the number of flashes and refer to chart. Look on the inside of the furnace blower door or other panel. Also look up on internet and print it off. If the furnace was allowed to run during the remodel it voids the warranty automatically. Read the installation manual.
Try resetting the electronic board by turning the power off then back on.
Mar 29, 2017 | Bryant Heating & Cooling
Coleman furnace
Reverse polarity means the power wires coming to the furnace are connected backwards. The black wire should the hot ( 120 volt line) . The white wire should be the neutral. The green should be the ground. Check these connections and test them to make sure they are correct. You should get 120 volt reading between the black and white.120 volts between the black and green and 0 volts between the white and green. Hope this helps.
Jan 02, 2014 | Heating & Cooling
I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye
Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Nov 29, 2011 | Goodman Heating & Cooling
I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help
Oct 28, 2011 | Goodman Heating & Cooling
I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong
Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.
Oct 18, 2011 | Goodman GMS90703BXA Heater
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
Feb 03, 2011 | Goodman Heating & Cooling
Goodman 95 %furnace keeps saying low pressure is stuck. changed out low pressure switch and high pressure switch and still have same problem.
That thang might be sensing a lazy flame. In other words the flames took too long in the board's opinion to quit sensing the flame. Yall probably need to do pressure tap on the gas valve.
Here is a realistic look at goodman fault codes and what to check fer and I am assuming you are not a tech and don't know this already and am hoping it helps:
Now here is how it should all go down:
Bottom dollar: it all goes back to type of gas, the initial setup, the pressure tap. and how it is wired up to begin with.
This will give you an idea where to start I hope.
Dec 10, 2010 | Goodman GMS80903BNA Heater
My central heating is on lockout and the burner is with red light
A sampling of various codes on a furnace
Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Dec 02, 2010 | Heating & Cooling
Hi, I have a Janitrol GMPN060 natural
HI Check you air filter in clean , jump out the pressure switch see if it starts are the fan motors clean also check out the fan control hope this helps
Feb 12, 2010 | Heating & Cooling
Heater not working after new uniot installed
you might switch polarity on the plug going into the furnace. Reversing polarity consists of taking the 110 volt line going into your furnace and switching the two plug wires aroung leaving the green connected. This may help since some furnaces run with the electricity going into the furnace a certian direction. Good luck on you repairsDave
Dec 02, 2009 | Heating & Cooling
Heating & Cooling Logo
189 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen