York diamond 90
I have 4 codes flashing what is it
  • papi9295 Jan 22, 2009
    High Aux or Spill Limit Switch Open,that what is says,
  • Perry Putnam
    Perry Putnam May 11, 2010
    On the inside of the cover there should be a list saying what the fault codes mean. What is the system doing?
    Problem Solver:
  • 9 Answers
If you shut off the power and turn it back on does it start and run? if so, replace you air filter. Odds are the blower is dirty and if it is dirty the secondary heatexchanger is dirty and if you have a/c your a-coil will most likely be a bit dirty too. And it all starts with the ducts, there is only one place the dirt comes from. This causes bad air flow over time and could be causing your problem. But in order to do this have a hvac company come in and clean it. Find someone who does furnace and duct cleanings. I own a heating, cooling and duct cleaning business and see this all the time. a way to check the air flow is to take the return tempature and the plenum tempature. if the unit is running on high it prob should be around 70-75F diff. The sticker inside the furnace will tell you the proper temp rise.
Now if the rool out switch on the side of the burner box is tripped call a tech and have them check the heat exchanger. a burner tube is most likley gone, but this is very unlikely.
Let me know what you find...
Posted on Jan 22, 2009
2 Suggested Answers
  • 59 Answers
SOURCE: York, diamond 90 heating issues!
Look at the electrical schematic on the inside cover to the electrical compartment. It should have a list of fault codes. Locate the condesate drain lines (up to three) and remove them and inspect them for debris/blockage. Clean them and flush them with warm water and clorox solution. Make sure that your condensate line is not blocked and that you are getting drainage from the condensate line. The new high efficiency furnaces generate a great deal of condensate water from the burner and it needs to drain properly.
Posted on Jan 29, 2011
York diamond 90 furnace burners won't ignite ... igniter glows for a few seconds then clicks off, no burner ignition. Tried resetting the furnace by powering off and then setting thermostat to call for...
The thermocouple could be defective. If this is a high efficiency York furnace, the stack blower should start and run first. If it doesn't the blower controller may have failed.
Dec 06, 2013 | Heating & Cooling
York diamond 80 - continuous flashing red
Is there a chart on it somewhere that describes what each mode of flashing means? Most of them do. Inside the front cover,,,somewhere on the inside of the panel that covers the filter? I've never seen one of these without that diafram.
Oct 24, 2013 | Tools & Hardware - Others
Where is the pilot on the york diamond 90 furnace
there is no standing pilot on your 90% AFUE furnace this is a hot surface ignition
Mar 05, 2011 | Heating & Cooling
York, diamond 90 heating issues! Ruscopeland suggested to check out problem by noting fault code on the system... after it turned off it kept flashing 6 times. what does this mean? any answers?
Jan 28, 2011 | Heating & Cooling
York, diamond 90 heating issues, on & off
try cleaning the flame sensor with some steel wool if not could be pcb
May 23, 2010 | Heating & Cooling
York "high Aux or spill limit switch open"
how can I fix the spill limit switch, also how do I found it
Mar 05, 2010 | York Furnace Draft Inducer Blower Fasco #...
I have a york diamond 90 diagnostic 1 flash lock
open the top of your unit so that you can see into the burner box
what your looking for should be an orange wire that leeads up to a metal rod
that metal rod should be in the way of the flame when unit is on
this is your flame ground,,, or more commonly known as the flame sensor,,, take this out and goive it a good brush with some steel wool
and reassemble,,
this should clear up you problem
Nov 04, 2009 | Goodman GMS90703BXA Heater
Wiring Question York Diamond 90 Condensor Unit - New Capacitor
the wire diagram should tell you how. it all depends where wires lead to. be very carefull, capacitors can be dangerous. brown usaully go to fan black usaully goes to common red usaully goes to herm or compressor. it all depends where wires come from
Aug 27, 2009 | Heating & Cooling
York diamond 80 hvac blower and comp wont start on automatic
Need blower motor for York Diamond 80 Furnace I am in St Louis MO where can i get one
Jun 20, 2009 | York Furnace Draft Inducer Blower Fasco #...
York
I have an old York outside compressor/coil/fan unit, CDHF36-6A, that I need to replace as it is no longer repairable. What is the capacity of this unit and what Carrier unit would be a good replacement?