Question about Reddy Heater-30-55,000 BTU Variable

1 Answer

Handy Master Fumes so Bad your Eyes can"t take the smell

I have adjusted the air pump pressure anywhere from 2 psi to 3 psi range and it runs fine until I install the top sheet metal back on it then it puts out fumes so bad you can't stand it for it burns your eyes so bad. I have cleaned the fuel filter screen and nothing was in it. I took the rotar and blades out to relace them but they were like new so I blew everything out with compressed air a put it back together and does the same thing. I took the nozzle out blew it with compressed air and found nothing wrong ,it was perfectly clean, along with both fuel line and air hoses. Spark plug is gapped at .055 " where as a sticker on inside of heater reads range is .055" -.060".No mater where I adjust the air pressure ,it runs fine until I install the top sheet metal cover.Can anybody help me with this problem? Thanks..

Posted by on

1 Answer

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    Hot-Shot:

    An expert who has answered 20 questions.

    Corporal:

    An expert that hasĀ over 10 points.

    Mayor:

    An expert whose answer gotĀ voted for 2 times.

  • Expert
  • 92 Answers

It sounds like it's not getting enough air to fuel mix, check your lines.

Posted on Jan 22, 2009

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Starts then shuts off


REAL FACT is: If all individual components of the heater are at 100% but the air pump pressure is not on it's mark, then the heater WILL NOT continue to run!
Air Pump Pressure is directly related to fuel delivery. Read that statement again! It is the most important line of text on this website.
If the pump pressure is incorrect, then, the fuel delivery will be incorrect. As a result, the heater will not run to specs.
Instructions for setting the air pump pressure:
Air pump pressure is the pulse of the heater. Pump pressures range from 3 psi to 6 psi depending on heater BTU size (see chart below). A loss of ONLY 1 psi translates to a 30% to 17% loss of FUEL FLOW (starvation). You must know the specified required pressure and set the pressure accordingly.
Heaters with Hot Surface Ignitor technology are extremely critical to pump pressure. If the pressure is off by 1/2 psi, the heater may run for 5 seconds, then shut down because of IGNITION FAILURE. The only way to correct this problem is to set the pump pressure to DESA's recommended pressure specification.
  1. The FIRST STEP in diagnosing any heater problem should be checking the output of the air pump. Determine the air pressure required for the heater model that is being tuned. The air pump, in turn, is responsible for fuel delivery.
  2. If you do not know the required pressure look for a decal on the side (usually) of your heater. This decal will state the model number, serial number, fuel capacity, pump pressure, etc.
  3. If your plastic end cover looks like this......
m29609t.jpgM29609 has 2 threaded holes. The hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
or
If your plastic end cover looks like this......
m16545t.jpgM16545 has 2 threaded holes. The shorter projection with a hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
4. The other hole (longer projection) has a screw with a hole which adjusts a ball and spring relief valve assembly. Carefully adjust the screw until the gauge is reading the pressure level that is specified on the heater's label. If operating properly, the pump should produce more pressure than is required to operate the heater. The relief valve allows the excess air to escape before being sent to the nozzle.
5. Replace plug. Test for leak.
6. If you are unable to reach the desired pressure spray soapy water around the seal of the end cover- at the same time check the plastic cover for a crack. A cracked end cover will not allow the heater to perform properly and will not allow for an accurate reading. The pump must be set at the specified pressure in order to have adequate fuel delivery an adequate fuel atomization. Replace if needed.
7. If you set the pressure to specs and the heater does not perform properly or the cone does not glow a soft red, then check for other fuel delivery problems such as a clogged fuel filter, cracked rubber hose, clogged or worn nozzle, or a cracked nozzle adapter. Soapy water lightly sprayed in these areas will quickly identify the problem most of the time. Any air leak will create problems.

Feb 17, 2015 | Reddy R60A Utility Heater

1 Answer

Starts then shuts down


REAL FACT is: If all individual components of the heater are at 100% but the air pump pressure is not on it's mark, then the heater WILL NOT continue to run!
Air Pump Pressure is directly related to fuel delivery. Read that statement again! It is the most important line of text on this website.
If the pump pressure is incorrect, then, the fuel delivery will be incorrect. As a result, the heater will not run to specs.
Instructions for setting the air pump pressure:
Air pump pressure is the pulse of the heater. Pump pressures range from 3 psi to 6 psi depending on heater BTU size (see chart below). A loss of ONLY 1 psi translates to a 30% to 17% loss of FUEL FLOW (starvation). You must know the specified required pressure and set the pressure accordingly.
Heaters with Hot Surface Ignitor technology are extremely critical to pump pressure. If the pressure is off by 1/2 psi, the heater may run for 5 seconds, then shut down because of IGNITION FAILURE. The only way to correct this problem is to set the pump pressure to DESA's recommended pressure specification.
  1. The FIRST STEP in diagnosing any heater problem should be checking the output of the air pump. Determine the air pressure required for the heater model that is being tuned. The air pump, in turn, is responsible for fuel delivery.
  2. If you do not know the required pressure look for a decal on the side (usually) of your heater. This decal will state the model number, serial number, fuel capacity, pump pressure, etc.
  3. If your plastic end cover looks like this......
m29609t.jpgM29609 has 2 threaded holes. The hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
or
If your plastic end cover looks like this......
m16545t.jpgM16545 has 2 threaded holes. The shorter projection with a hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
4. The other hole (longer projection) has a screw with a hole which adjusts a ball and spring relief valve assembly. Carefully adjust the screw until the gauge is reading the pressure level that is specified on the heater's label. If operating properly, the pump should produce more pressure than is required to operate the heater. The relief valve allows the excess air to escape before being sent to the nozzle.
5. Replace plug. Test for leak.
6. If you are unable to reach the desired pressure spray soapy water around the seal of the end cover- at the same time check the plastic cover for a crack. A cracked end cover will not allow the heater to perform properly and will not allow for an accurate reading. The pump must be set at the specified pressure in order to have adequate fuel delivery an adequate fuel atomization. Replace if needed.
7. If you set the pressure to specs and the heater does not perform properly or the cone does not glow a soft red, then check for other fuel delivery problems such as a clogged fuel filter, cracked rubber hose, clogged or worn nozzle, or a cracked nozzle adapter. Soapy water lightly sprayed in these areas will quickly identify the problem most of the time. Any air leak will create problems.

Mar 02, 2014 | Reddy Heater-170,000 BTU Kerosene Deluxe

1 Answer

Runs when started but won't stay running.


REAL FACT is: If all individual components of the heater are at 100% but the air pump pressure is not on it's mark, then the heater WILL NOT continue to run!
Air Pump Pressure is directly related to fuel delivery. Read that statement again! It is the most important line of text on this website.
If the pump pressure is incorrect, then, the fuel delivery will be incorrect. As a result, the heater will not run to specs.
Instructions for setting the air pump pressure:
Air pump pressure is the pulse of the heater. Pump pressures range from 3 psi to 6 psi depending on heater BTU size (see chart below). A loss of ONLY 1 psi translates to a 30% to 17% loss of FUEL FLOW (starvation). You must know the specified required pressure and set the pressure accordingly.
Heaters with Hot Surface Ignitor technology are extremely critical to pump pressure. If the pressure is off by 1/2 psi, the heater may run for 5 seconds, then shut down because of IGNITION FAILURE. The only way to correct this problem is to set the pump pressure to DESA's recommended pressure specification.
  1. The FIRST STEP in diagnosing any heater problem should be checking the output of the air pump. Determine the air pressure required for the heater model that is being tuned. The air pump, in turn, is responsible for fuel delivery.
  2. If you do not know the required pressure look for a decal on the side (usually) of your heater. This decal will state the model number, serial number, fuel capacity, pump pressure, etc.
  3. If your plastic end cover looks like this......
m29609t.jpgM29609 has 2 threaded holes. The hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
or
If your plastic end cover looks like this......
m16545t.jpgM16545 has 2 threaded holes. The shorter projection with a hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
4. The other hole (longer projection) has a screw with a hole which adjusts a ball and spring relief valve assembly. Carefully adjust the screw until the gauge is reading the pressure level that is specified on the heater's label. If operating properly, the pump should produce more pressure than is required to operate the heater. The relief valve allows the excess air to escape before being sent to the nozzle.
5. Replace plug. Test for leak.
6. If you are unable to reach the desired pressure spray soapy water around the seal of the end cover- at the same time check the plastic cover for a crack. A cracked end cover will not allow the heater to perform properly and will not allow for an accurate reading. The pump must be set at the specified pressure in order to have adequate fuel delivery an adequate fuel atomization. Replace if needed.
7. If you set the pressure to specs and the heater does not perform properly or the cone does not glow a soft red, then check for other fuel delivery problems such as a clogged fuel filter, cracked rubber hose, clogged or worn nozzle, or a cracked nozzle adapter. Soapy water lightly sprayed in these areas will quickly identify the problem most of the time. Any air leak will create problems.

Feb 13, 2014 | Reddy HEATER R70DT 70,000-BTU PORTABLE...

1 Answer

Reddy heater 170T- terrible fumes-fuel pressure problem


Are you sure there is not water in the tank? Fuel pressure should almost never need adjusted.

Jan 08, 2014 | Reddy Heaters

1 Answer

My kerosene torpedo heater turns on but then it dies after five seconds


REAL FACT is: If all individual components of the heater are at 100% but the air pump pressure is not on it's mark, then the heater WILL NOT continue to run!
Air Pump Pressure is directly related to fuel delivery. Read that statement again! It is the most important line of text on this website.
If the pump pressure is incorrect, then, the fuel delivery will be incorrect. As a result, the heater will not run to specs.
Instructions for setting the air pump pressure:
Air pump pressure is the pulse of the heater. Pump pressures range from 3 psi to 6 psi depending on heater BTU size (see chart below). A loss of ONLY 1 psi translates to a 30% to 17% loss of FUEL FLOW (starvation). You must know the specified required pressure and set the pressure accordingly.
Heaters with Hot Surface Ignitor technology are extremely critical to pump pressure. If the pressure is off by 1/2 psi, the heater may run for 5 seconds, then shut down because of IGNITION FAILURE. The only way to correct this problem is to set the pump pressure to DESA's recommended pressure specification.
  1. The FIRST STEP in diagnosing any heater problem should be checking the output of the air pump. Determine the air pressure required for the heater model that is being tuned. The air pump, in turn, is responsible for fuel delivery.
  2. If you do not know the required pressure look for a decal on the side (usually) of your heater. This decal will state the model number, serial number, fuel capacity, pump pressure, etc.
  3. If your plastic end cover looks like this......
m29609t.jpgM29609 has 2 threaded holes. The hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
or
If your plastic end cover looks like this......
m16545t.jpgM16545 has 2 threaded holes. The shorter projection with a hole on the left has a square plug inserted. Remove the plug. Screw in the nipple end of the gauge into the threaded hole. Check for air leaks with soapy water.
4. The other hole (longer projection) has a screw with a hole which adjusts a ball and spring relief valve assembly. Carefully adjust the screw until the gauge is reading the pressure level that is specified on the heater's label. If operating properly, the pump should produce more pressure than is required to operate the heater. The relief valve allows the excess air to escape before being sent to the nozzle.
5. Replace plug. Test for leak.
6. If you are unable to reach the desired pressure spray soapy water around the seal of the end cover- at the same time check the plastic cover for a crack. A cracked end cover will not allow the heater to perform properly and will not allow for an accurate reading. The pump must be set at the specified pressure in order to have adequate fuel delivery an adequate fuel atomization. Replace if needed.
7. If you set the pressure to specs and the heater does not perform properly or the cone does not glow a soft red, then check for other fuel delivery problems such as a clogged fuel filter, cracked rubber hose, clogged or worn nozzle, or a cracked nozzle adapter. Soapy water lightly sprayed in these areas will quickly identify the problem most of the time. Any air leak will create problems.

Jan 08, 2012 | Reddy Heater-70,000 BTU Kerosene w/T'stat

1 Answer

Smoking shop up and fumes burning eyes,smells rich ,how do i adjust?


next to pressure gauge is usually a phillips or flat head adjust it to match same psi as nameplate rating

Dec 16, 2010 | Master Heaters B200BT

1 Answer

Master Reddy 30,000 btu heater put out nasty fumes.


Sounds like it's not getting enough air to fuel mix, check your air inlet line for breaks or just put a new one on for a couple bucks. any fuel line thats the right diameter will work, got mine from auto zone.

Jan 21, 2009 | Reddy R155D Utility Heater

1 Answer

I have just purchase a kerosene fan force (reddy) space heater ,we use it in a very drafty garage,but the strong smell of kerosene fumes are more then we can stand.we have tried scent additives but nothing...


Try running it outside where the oxygen level is 21%. Carbon Monoxide will kill you The smell might be the product if incomplete combustion CARBON MONOXIDE, or the fuel line pressure needs to be adjusted.

If you still get the smell the unit may defective. If you want to try adjusting the fuel line pressure, you will need a low pressure gauge 0-15 psi.remove a plug from the heater and set the pressure at the documented pressure, the other plug with the hole in it is the adjustment.

Dec 05, 2008 | Reddy Heater RLP100 Portable Forced Air...

1 Answer

Heavy smell


This is a fuel delivery problem. Look for:
  1. always start troubleshooting fuel problems on a Hot Surface Ignitor heater by checking the pump pressure!
  2. restricted fuel filter
  3. air leak
  4. restricted nozzle
Troubleshooting tips

Nov 17, 2008 | Reddy R60A Utility Heater

Not finding what you are looking for?
Reddy Heater-30-55,000 BTU Variable Logo

119 people viewed this question

Ask a Question

Usually answered in minutes!

Top Reddy Heaters Experts

Mack Baxter

Level 3 Expert

379 Answers

paulcarew

Level 3 Expert

1863 Answers

Superior Maintenance

Level 2 Expert

63 Answers

Are you a Reddy Heater Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...