I have recently pulled out the water operated gas valve to check the diaphram for holes/wear after i re-assembled unit the heater now turns on but will not go out after turning water of, this unit is old maybe 15-20yrs
  • 34 Answers
SOURCE: Junkers gas water heater automatic ignition not working
Yes that is going to be the contoll valve on that heater. You can probley fix it very easy with the right part. You will need to locate a plumbing supply over there in the UK. Give them the make and model number and tell them you need a unitroll gas valve for it.
Posted on Feb 08, 2009
  • 11 Answers
SOURCE: BOSCH AQUASTAR 2400ES NATURAL GAS TANKLESS HOT WATER HEATER
Q. FA - Gas leakage error, gas valve circuit not closing properly
A.
  1. Disconnect power supply cord and check wire connections on gas valve and the two connectors on the control board.
  2. Flow water out of a hot water tap above the minimum activation point of .8GPM. Measure voltage at the gas valve wire connector. The connector should measure 24VDC between the left pair of wires and 24VDC between the right pair of wires when the unit is operating. If voltage is not correct, contact Bosch Water Heating for further instruction.
  3. Gas valve may be defective, contact Bosch Water Heating for further instruction.
Q. EA - No flame ionization detected with water flow
A.
  1. Verify that all manual gas shut off valves are open.
  2. Verify gas type (See Fig. 2 in installation manual) corresponds with the type of gas supplied to the heater.
  3. Reset error code and open a water tap to cycle the heater in an effort to purge air from gas line (especially on new installations). Cycling hot water tap on and off multiple times may be necessary. If heater still faults with EA error code, have a licensed gas technician properly purge air out of the gas line leading to the water heater.
  4. Verify the three yellow wire connections to the set of electrodes (underside of the burner assembly) are secure.
  5. Verify gas pressure meets specifications outlined in chapter 3.8. See Bulletin TWH-G2-03.
  6. Verify venting meets specifications outlined in chapter 3.6 of the installation manual. Improper venting may cause premature failure of the flame sensor rod.
  7. Observe inside the viewing window of the heat exchanger when a hot water tap is opened. Sparking should be followed by a steady blue flame. If not, Call Bosch Water Heating with observations. Readings from above gas pressure test will be required.
Q. C1 - Fan rotation too low on startup
A.
  1. Disconnect power supply cord. Check wire connections on back side of fan and the two large wire connectors on the control unit. Removal of lower access panel on control unit is necessary to access connectors.
  2. Verify that supply voltage is 120VAC and is properly grounded.
  3. Verify that venting meets specifications outlined in chapter 3.6 of the installation manual. Long vent lengths, venting with more than three elbows, blocked vent or combination venting may cause this failure. Verify backdraft flapper inside flue gas collector is not stuck shut.
  4. Check gas pressure. See Bulletin TWH-G2-03. Low gas pressure may cause the fan to change its speed to meet desired temperature.
  5. Possible defective control unit. Call Bosch Water Heating for further instructions.
Posted on Mar 15, 2009
Bati99
  • 88 Answers
SOURCE: Lighting Instructions for a Bosch Junker Water Heater
go to this site, have your model number at hand.
http://www.boschhotwater.com/HelpfulResources/BrochuresManuals/
Posted on Apr 18, 2009
senor8
  • 73 Answers
SOURCE: Water Heater Won't Fire up
There are a few things you'll want to check:
1) make sure you have 120VAC at the outlet
2) measure voltage across the blue/white and black/white wires connected to the gfi (black box inside the unit on the bottom left or right hand side). You should read roughly 100 VAC on both sides. If you don't read voltage on the black/white wire pair, then you gfi is tripped. Look for moisture that might be shorting the gfi.
3) If the GFI checks out ok, you probably have debris clogging your flow sensor
Posted on Aug 15, 2009
  • 33 Answers
SOURCE: Bosch Aquastar 2400E LP Does Not Heat Water
Sounds like the water flow sensor and servo, may just need cleaning, get it checked out by a Bosch agent
Posted on Jan 17, 2010
Junkers wr11 has no spark and no power
Is it gas or electric? if it is gas and has a pilot, and the pilot is out. If you don't smell gas go through the start pilot proceedure. when the pilot is running it produces a small electric current sufficient to hold the main gas valve open; then the temperture sensor allows the unit to keep the water heated.
Oct 29, 2014 | Water Heaters
Tip
How to Change the Gas Valve and Thermostat on a Hot Water Heater
<p>If you are having<b> trouble with the temperatures</b> of your <b>gas hot water heater</b> fluctuating too much, or after <b>changing the thermocouple</b> of your gas <b>hot water heater</b> then you may need to change the complete <b>gas valve and thermostat assembly</b>. Also if you have changed the <b>thermocouple</b> and the pilot still will not stay lit, then the gas valve could be bad or the <b>ECO (Emergency Cutout)</b> may have activated and is open. This is a onetime device and cannot be replaced.<br /> <p><br /> <p>These instructions are for the older style <b>gas valve and thermostat combination</b>. These commonly have a large red knob that adjusts the temperature of the water. Also note that the burner tube nut for <b>natural gas</b> is right hand thread, but if you have <b>LP or propane gas</b> the burner tube nut is left hand thread.<br /> <p><br /> <p>The newer <b>gas valve thermostat combinations</b> that have come out recently are similar, but they have a well in the tank that the sensor slides into. The assembly is held fast with a set screw. With this type of <b>gas valve and thermostat unit </b>the tank does not need to be drained, but most of the rest of the change out is similar.<br /><br />To change a <b>gas hot water heater thermostat</b> you will need to first buy a new gas valve for your <b>hot water heater</b>. The <b>gas valve</b> and the <b>thermostat</b> are integrated into one unit.<br /><br />To <b>replace the thermostat on a gas hot water heater</b> you must follow these procedures....<br /><br />1. Turn off the incoming water and<b> drain the hot water heater</b>.<br /><br />2. Remove the <b>pilot tube</b>, the <b>burner gas tube</b> and the thermocouple from the gas valve. Turn off the <b>gas line</b> and remove from the gas valve.<br /><br />3. Get a <b>pump pliers</b> or a<b> wrench</b> in behind the gas valve and turn the whole assembly CCW to remove it from the tank.<br /><br />4. After applying pipe dope or tape to the new gas valve threads, turn the new gas valve into the tank by turning in a CW direction. Be careful not to damage the small wires to the <b>ECO</b>. They are the little red wires on the back. If you break them the assembly is irreparably damaged.<br /><br />5. Reinstall the gas line, thermocouple, burner tube, and the pilot tube to the gas valve.<br /><br />6. Fill tank with water. Make sure to open a <b>hot water faucet</b> and <b>purge all air from the tank.<br /><br /></b>7. <b>Check for leaks</b> where the gas line hooks up with soapy water.<br /><br />8. Relight pilot light and check operation.<br /><br />9. Set the new temperature setting to a medium setting and then adjust the temperature to your liking from there and adequate time for heating completely<br /> <p>
on Feb 25, 2011 | Water Heaters
How to light the pilot light in a bosch aquastar 125 fx ng tankless water heater
I have the same machine first they said replace the micro switch i did then rebuild the water valve did not enough gas presure had it checked revented the unit the unit is brandnew relubed the water valve idk
May 11, 2014 | Bosch AquaStar 125FXKIT-NG 125FX Natural...
Eratic hot water flow
Bosch 1600H NG??? I suppose. If so you need a digital manometer.
Take a static (off) reading then leave it hooked up and start flow. Watch pressure draw down and you should see the heater draw Water Column down below 5" as the pocket of NG in the pipe just before the unit draws down to minimal to keep heater lite. In that case problem in gas line size/gas line run length, Meter pressure.
If you have and maintain in operation 5" WC then is probably the water valve needs rebuilt along with a new diaphgram and also the water filter should be replaced too. This occurs esp after 2-3 year as Bosch specs rebuild at 3 yrs on the Maint Schedule. Also clean all the faucet aerators for good flow above 1.25 GPM Min at all faucets.
Under a single faucet flow (laundry sink) of 2.25 GPM the flame bed of the Unit should be 1"+ high and uniformly Blue.
I assume at this time you either have a Maint problem or you could be overflowing the heater's Winter capacity. This unit @ 70F rise only makes about 2.2 GPM. It's strictly a single use faucet heater at 117,000 BTU.
When you do the Maint look to see if there is corrosion between the GV pushrod and the water valve pushrod. Notice there is a huge mis- match in the 2 rods sizes.These units occasionally (more the 125B) corrode there and the GV will seize on and boil the heater dry and open a seam so you really want to maintain it to Bosch Specs and Schedule.
Note: This is a gas appliance & requires skill and knowledge to service. While Bosch may say you can DIY, I'd readily advise a Bosch approved Service Tech or Plumber do any rebuild. The Digital Manometer alone is a $100-150.00 item and it's the ONLY way to get accurate gas pressure readings.
Mar 14, 2014 | Bosch 1600H-NG Natural Gas AquaStar...
I have a bosch aqvastar 250 sx ng error code EC keeps appearing
Q. EC - Ionization failure during operation
A.
  1. Verify gas type (See Fig. 2 in installation manual) corresponds with the type of gas supplied to the heater.
  2. Verify the three yellow wire connections to the set of electrodes (underside of the burner assembly) are secure.
  3. Verify that venting meets specifications per chapter 3.6 of the installation manual. Improper venting may cause premature failure of the flame sensor rod.
  5. Check and adjust CO2 readings. See Bulletin TWH-G2-12.
  6. Gas valve or flame sensor may be damaged. Call Bosch Water Heating with observations and results of previous steps.
Mar 06, 2011 | Bosch & Tankless LP Hot Water Heater
Faulty Junkers water heater
first find out from your manual what the flashing red light means...that should narrow your search---could be a thermocouple shot,a rubber diphragm in the gas valve has weakened and not operated, or gas pressure into the appliance may suddenly be too low, or springs in gas valve may have worn out---very many possibilities
Mar 02, 2010 | Water Heaters
Bosch 125BNG burners not firing
the diaphram is the pushing force for the gas valve to open, if you have a split or worn diaphram it will ned to be replaced.
Feb 21, 2009 | Bosch AquaStar Indoor Natural Gas Tankless...
the A3 & E3 codes are for the back flow sensor on the heater. Could be disconnected or a bad sensor. Call bosch tech support and they will help you with this.
Dec 30, 2008 | Bosch AquaStar 2400ES-NG
Water Heaters Logo
78 people viewed this question
Top Water Heaters Experts
Donni Steen
Gil Shultz
Are you a Water Heater Expert? Answer questions, earn points and help others